The furnace isn't kicking in. We have a code of 3 flashing…

Customer Question
The furnace isn't kicking...

The furnace isn't kicking in. We have a code of 3 flashing green lights. My niece and nephew put snow into the white pvc pipes yesterday. I thought they had cleared them back out, but I went out and shop vac'd any remaining snow. I turned the thermastat off and back on as well as a switch inside the furnace cover. Still nothing.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Larger problem

Contractor's Assistant: Do you plan on doing the work yourself?

Hopefully

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
1/5/2018
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,402
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

What's the brand and model of your unit?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Keeprite Model N9MSE0601410A1
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

You've confirmed that you have a draft issue. The question is do you have a bad switch or a weak fan ( is the draft fan running?) or a blocked exhaust vent. You can check the vent for blockages and also the vac tubing connected to the switch. Be sure the tubing is not kinked, deteriorated or doesn't have water in it. You can also poke a paper clip into the port where the tubing connects but not into the switch connection. If all that checks out. Turn the power off to the unit wait a couple minutes then turn it back on. After the fan starts remove one of the leads from the pressure switch and connect it to the other lead. If the sequence continues then you may have a faulty pressure switch or possibly a weak fan. The next thing we would do is put a manometer on the exhaust to check the actual draft pressure but you aren't likely to have a manometer and they are expensive. Replacing the switch is one other option since it's less money than a manometer (or a new draft fan) and it is a likely culprit.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Trane XE90 that will not kick on automatically, the
I have a Trane XE90 that will not kick on automatically, the exhaust fan kicks on but does not start. If I in plug the clear hose from the CDV and PO2 the furnace will start. The red light flashes 3 t… read more
hvacdave84
hvacdave84
53 satisfied customers
Phil I have a newer comfortmaker it'High eff.My problem
Hi Phil I have a newer comfortmaker it'High eff.My problem is.Call for heat no heat the digo.flashes 3 times.so I kill the furnace and wait 2 min click it on blower motor bunnung then the exh comes on… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My furnace seems to be stopping intermittently. The red
My furnace seems to be stopping intermittently. The red light is solid but green flashes … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Came to this site searching for "American Standard Freedom
Customer: my name is Tim. Came to this site searching for "American Standard Freedom 90 3 flash code" … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My name is***** have a Rheem Classic 90 Plus natural
My name is***** have a Rheem Classic 90 Plus natural gas furnace. It has three lights on the control board. 2 green and one orange. One green is for power, the second says ready also green and the ora… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My G26q3-50-1 furnace is turning on but there is no pilot light.
My G26q3-50-1 furnace is turning on but there is no pilot light. We turned the thermostate low and let it sit for 15 minutes then tried again. Can you suggest something else?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 31 code on my Bryant plus 90. The furnace will sometimes
I have a 31 code on my Bryant plus 90. The furnace will sometimes run for about a minute or two then turn off. Then it won't turn on again. The small motor will run but no Ignition,the fan will keep r… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem Classic 90 kicks in with 2 green lights and a gold light---it
Rheem Classic 90 kicks in with 2 green lights and a gold light---it then shuts down and has one green light flashing---there was snow in the pipe outside and I cleared that out. I took the door off an… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have a trane xr90. The red light is flashing and the unit
I have a trane xr90. The red light is flashing and the unit kicks on but only for a short interval. There is no heat. I did some checking about the unit and I checked the hoses to the pressure switch … read more
type2technician
type2technician
253 satisfied customers
I have an Intertherm 904037 furnace that will not ignite the
I have an Intertherm 904037 furnace that will not ignite the burner. The little fan on the front kicks on but notheing else happens. It is flashing a code 2 "pressure switch open with inducer on. We j… read more
heatncoolrepair
heatncoolrepair
Former HVAC Service Technician
Vocational, Technical or Trade Scho
75 satisfied customers
I have a nordyne Gas furnace It is newer model and the flame
I have a nordyne Gas furnace It is newer model and the flame is not comming on. The red status light inside the compartment is solid red but when you turn on the heat and the little fan comes on, afte… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE A A93UH FURNACE AND IT WILL NOT CONTINUE TO RUN i HAVE
I HAVE A A93UH FURNACE AND IT WILL NOT CONTINUE TO RUN i HAVE A FLASHING LIGHT THAT FLASHES 3 TIMES… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Carrier WeatherMaker 9200 furnace. The flashing
We have a Carrier WeatherMaker 9200 furnace. The flashing error code is 34. The blower was running but there was no heat. When I pulled off the sheet metal cover with the small window in it, the furna… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have two Bryant Model 340 MAV furnaces and both are generating
I have two Bryant Model 340 MAV furnaces and both are generating #34 fault codes. I've tried the restart procedures for both to no avail. Any suggestions?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Can you please tell me the problem with my furnace (Ruud Achiever
Can you please tell me the problem with my furnace (Ruud Achiever 90 Plus) if it is blinking twice and the blower motor comes on but will not ignite, then shuts down. We are in the middle of a blizzar… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a 90% Rheam furnace with no pilot (some sort of internal
I have a 90% Rheam furnace with no pilot (some sort of internal ignition switch) that's only a couple of years old. I can hear the blower kicking in and then after about 30 seconds, it kicks back off.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Our Trane XR-90 furnace is flashing 3 - pressure error. Of
Our Trane XR-90 furnace is flashing 3 - pressure error. Of course it is Friday night and it is snowing... Is this something we can fix on our own?… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I am getting 6+3 flashes from the diagnostic LED---label inside
I am getting 6+3 flashes from the diagnostic LED---label inside cover reads "soft lockout-pressure switch opened during run" what can I do, please???… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x