I am having trouble, my heater fires and runs great then the…

Customer Question
I am having trouble...

I am having trouble , my heater fires and runs great then the flame slowly gets smaller and smaller until unit shuts down . If i hit reset it fires up perfect , good flame but then the flame slowly gets smaller and goes out . I serviced it recently . new air filter , new nozzle , cleaned all screens , new oil filter , new electrodes and the usual heat exchanger cleaning along with the chimminy

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 16 minutes by:
1/5/2018
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,850
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Sounds like a bad fuel pump. Do you have a pressure gauge that can read up to 150 psi? If you do you'll have to reduce it to an 1/8" nipple so you can screw it int a pressure tap on the pump

Ask Your Own HVAC Question
Customer reply replied 8 months ago
this is a waste oil heater Reznor
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an oil burner question, One week, Yes, Please connect
Please connect me with someone who deals with oil burner questions… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a gun oil furnace and it keeps shutting down I bleed
I have a miller gun oil furnace and it keeps shutting down I bleed it and usually there is air in the line that I bleed out and it runs ok … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a vintage 1980's Weil McClain boiler and my oil pump
I have a vintage 1980's Weil McClain boiler and my oil pump continues to run without a flame. I had to replace my combustion chamber due to oil saturation. I also replaced the electric eye. I checked … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
Billy, it looks as though I have an ignition problem with the
Billy, it looks as though I have an ignition problem with the Beckett furnace. I've tried the :15 reset as well as the :30 sec hard reset. Both attempts end up in the "flashing green light" turning of… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
have Williamson furnace 1965 turns on. runs for about a minute
have Williamson furnace 1965 turns on. runs for about a minute then shuts off. never fires. no flame.… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I own a Dettson HME 20 with a Beckett AFG-F/ burner. The red
I own a Dettson HME 20 with a Beckett AFG-F/ burner. The red lith is flashing after few cycle on the oil mode and automaticly transfert to electric. I did reajust the burner electrodes, change the oil… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
I have a burnham oil fired boiler it will fire and run and
I have a burnham oil fired boiler it will fire and run and shut off if you wait a couple of seconds and push the reset button it will start and run for a few mins then shut off again… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am having trouble with a Lennox oil burner. It has a Beckett
I am having trouble with a Lennox oil burner. It has a Beckett AFII 85 burner. It has been working intermittently for the past couple of days. Due to the holiday my availability of parts is very limit… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a Becket Honeywell (7184B 1032). Was having some problems
I have a Becket Honeywell (7184B 1032). Was having some problems like I see posted in browsing through places like this: started with boiler shutting down and my thinking that low oil was the cause - … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a utica starfire 3 steam oil fired cast iron boiler
I have a utica starfire 3 steam oil fired cast iron boiler and "tankless" hot water heater. Before the boiler fires up, it is making a ticking sound for an extended period. The boiler would then fire … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
trouble shooting beckett burner on Lennox oil fired furnace.
trouble shooting beckett burner on Lennox oil fired furnace. found reset button tripped, unit tried to fire but locked out immediately. checked out control, determined I needed to replace the control … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very hard smokey starts,very shakey running and un called for cycling of motor). Replaced pump last year (leaking). Tech did not use beckett r… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a Bock 32E water heater with an older Beckett burner.
I have a Bock 32E water heater with an older Beckett burner. I recently ran out of fuel and of course, it cut out. I purchased oil the next day and bled the line. It tried to fire but cut out several … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a oil furnance it will run 3 to 4 times then it shuts
I have a oil furnance it will run 3 to 4 times then it shuts off.. I bought nozzle/checkvalue/eletros/but hot in the tank the test said no water the trasformer has good spark/the flame looks great .I … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a a-c/heater style number rnuo84af...sometimes it starts
I have a a-c/heater style number rnuo84af...sometimes it starts making a loud shaking noise then smoke comes out...do I need it cleaned or did the heat bowl burst?… read more
Joseph
Joseph
HVAC Contractor
Vocational, Technical or Trade Scho
87 satisfied customers
Hi, my riello 40 f3 oil burner is failing to ignite.Sometimes
Hi, my riello 40 f3 oil burner is failing to ignite.Sometimes after I hit the reset button it will work all day,then overnite it wont come on untill I press the reset button once again.its two years o… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Hot Water boiler heated by a Carlin 100 CRD burner
I have a Hot Water boiler heated by a Carlin 100 CRD burner (oil) The stack switch is shuting down the burner. Reseting the stack switch restarts the burner but I get only a smokey output in the flue … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
from homeowner -- My boiler stopped working over night. I
from homeowner -- My boiler stopped working over night. I was thinking it was a frozen fuel line. I opened the bleader, hit reset, dirty fuel came out after a bit of sputtering. If fired at first, but… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x