I have a tempstar gas furnace. Its a 92% 80,000 btu furnace.

Customer Question
The flames come on for...
I have a tempstar gas furnace. Its a 92% 80,000 btu furnace. The flames come on for about 3-5 minutes and then they go out. The light blinks 4 times indicating an open limit. The blower stays on cools down the main limit then it fires again, over and over again. The filter is good, more then enough return air and all the supplies are open. I did jump out the 2 smaller limits, both of them proved to be good. So I got a main limt from the supply house and still the same thing. After awhile and a dozen head scratches I disconnected the wires from the main limit and attached them to the original one and let it hang outside the furnace the flames stayed on for every bit of ten minutes. Now what?
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
1/5/2018
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the furnace should have stayed indefinitely with the main limit hanging loose, look for an auxiliary limit switch, those are sometimes mounted on the main blower and jumper that if you find it.

AND for a brief test ONLY, jumper that limit switch that you removed from the furnace... if it still goes out after 10 or 15 minutes then its a bad printed circuit board most likely not the limit switch.

.

We can go from there without any time limits

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have two furnaces each 20 years old both are not working
I have two miller furnaces each 20 years old both are not working all of a sudden … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have good an furnance and stays lit for about 5 minutes and
Have good an furnance and stays lit for about 5 minutes and goes out replaced limited switch work great yesterday but this morning it's doing the same thing I over ride limit switch and it runs fine b… read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
See your discussion below on your websit - I have the exact
See your discussion below on your websit - I have the exact same problem - The igniter lights the burners - they go for about 8 seconds then on again over and over - then the Limiter opens - turns off… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier Weathermaker SX Model 58SX080-BC-1. For the
I have a Carrier Weathermaker SX Model 58SX080-BC-1. For the last couple days the furnace has not been able to heat the house above 59 degrees. I've checked the filter and the blower motor and they're… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a Bryant 340MAV furnace. I get a 33 code about every
I have a Bryant 340MAV furnace. I get a 33 code about every 5 to 10 furnace cycles. It doesn't do it all the time. According to my manual, that is a flame rollout switch problem. I changed the rollout… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Trane XE 80 and the burners wont stay lit. They cycle
I have a Trane XE 80 and the burners wont stay lit. They cycle up, 4 blinks when thermostat calls for heat. They burn for a minute or less then go out, after so many attempts two flashing lights indic… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My furnace is temporaly hot wired [red and wire tied] my
my furnace is temporaly hot wired [red and white wire tied] my funace runs for about 4 minutes [flame] then the fan runs till cool then cycle begins again… read more
V12Tech
V12Tech
252 satisfied customers
I have a williamson 5 in 1 furnance dating back to 1980 or
I have a Williamson 5 in 1 furnace dating back to 1980 or so we've lived in a two story house for 26 years but haven't use the 2nd floor much until now,not getting very much heat or air upstairs we ha… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Comfortmaker Furnace model GNJ075N12A1 burner wont stay lit.
Comfortmaker Furnace model GNJ075N12A1 burner won't stay lit. Checked all connections and just replaced the igniter and thermostat. Everything kicks on, even the burner once in awhile, but doesn't sta… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a Tempstar model N9MP2075B12B1. During call for heat
I have a Tempstar model N9MP2075B12B1. During call for heat (fan in Auto), the burners will ignite and the blower moter comes on. After about a minute or so of what seems like normal operation, the fl… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Trane XL80 gas furnace in the home that the wife and
I have a Trane XL80 gas furnace in the home that the wife and I purchased earlier this year. We didn't move in until April, so this is our first real heating season. Here's what we run into... ...I no… read more
johnincolorado
johnincolorado
8 satisfied customers
Help !! Trane XB 90. Burners light , small blower runs bt
Help !! Trane XB 90. Burners light , small blower runs bt as soon as it heats up the instant the big fan starts the burners go out ! Any suggestions, no codes just constant flash… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Carrier 58sta/stx 6 years old. found code 33. starts up fine.
Carrier 58sta/stx 6 years old. found code 33. starts up fine. inducer and flame kick off and blow runs for 2-3 minutes and then it starts rigth back up. had stupid tech come out and he cleaned the fla… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a model Rheem model RGLD-08EE-GR and the blower motor
I have a model Rheem model RGLD-08EE-GR and the blower motor will not shut off. The furnance does not try to light. It doesn' call for gas. What should I check?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Bryant Gas Furnace and is cycling and according to
I have a Bryant Gas Furnace and is cycling and according to the control board it is Limit or Flame rollout switch is open. I checked the blower motor it is fine I checked filter and motor capacitor ev… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a friend who asked me to check his furnace a Ultimate
I have a friend who asked me to check his furnace a Ultimate 2 by ICG, 2 small warm air rubber hoses were burned on top left which connect to a diaphram with a cutout switch,which i replaced, and also… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I just installed a new 95% 45K Goodman furnace and 1.5 ton
I just installed a new 95% 45K Goodman furnace and 1.5 ton central air. Air worked just fine this summer. Turned on furnace, everything seems to work. It heats, fan works, etc., but before it gets up … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have an Intertherm furnace model M3RL 080 ABW, no heat but
I have an Intertherm furnace model M3RL 080 ABW, no heat but the blower stays on. Red light on circuit board is steady flashing (one flash) on and off. Do I need to reset a switch, and if so where is … read more
HVAC DOCTOR
HVAC DOCTOR
President
Vocational, Technical or Trade Scho
74 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x