Customer Question
My furnace will not...

My furnace will not fire the fan kicks on the igniter comes on I’m getting 24 volts to my gas valve but it won’t open it’s new

Contractor's Assistant: Did you check the furnace's filters?

There all brand new

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

It’s a rgph-07eauer

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
1/5/2018
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Are there any error codes flashing on the board on the furnace?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
No two green lights
Customer reply replied 7 months ago
The gas valve is getting 24 volts but it won’t open
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

If the gas valve gets 24 volts but does not open you have a bad gas valve on the unit you will need to replace the valve for that issue. Just make sure the gas is on of course to the unit, but other than that it would be a burned out gas valve coil on the unit. This should be the valve for your unit does yours look like this one...CLICK HERE

I hope that I have earned a 5 star rating. We are on the honor system here for payment and will receive nothing unless a rating is given. Please remember to use the RATING LINK ON YOUR PAGE by selecting a star at the top or bottom of the screen before you leave today. If you need anything else, just let me know. You can continue asking follow-up questions at no additional charge after rating my service if you still need assistance.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I replaced it yesterday it fired ran great and now it’s not opening
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Did you test the coil on the valve is it reading open?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
How do you test the coil
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Just ohm out where the two wires go to tha gas valve coil. The 24 volt supply is across the coil. See if it is reading an open circuit

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It’s getting 25 to the gas valve when the unit calls for it
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

I would say it is just a defective new valve there is just nothing else it could be.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
There’s no sensor or safety to keep it from opening
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

No not if you get 24 volts to it that would not be the issue. I would test gas valve to see if the coil is open how many wires do you have to the valve?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Two
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

OK pull the wires off set your meter to ohms(do you have a decent auto ranging meter) if so just check across the two what ohm reading do you get?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
13.05
Customer reply replied 7 months ago
I have a cheap Gardner bender digital meter
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

OK the coil should be good,are you testing the valve for power with the wires on or off the valve?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
On
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Are you sure the gas supply to the unit is good? Also do you feel the coil clunk if you have your hand on it when it energizes?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I just did it with no wires connected getting 12.99 I just pulled the gas flex loose and I’m getting good flow
Customer reply replied 7 months ago
No I was able to hear it open yesterday now nothing
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

If you have them connected do you get about 27 volts AC?

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,747
18,747 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have problem with my furnace start. It's clean. It's a
It's a goodman furnace. Installed last year. Furnace works and when temperature goes down to settings then sometimes it doesn't kick on… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace won't light. Blower and ignition starts but no
My furnace won't light. Blower and ignition starts but no gas. Gas valve is open. No flashing light … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My burners won't turn on. I replaced gas valve and furnace
My burners won't turn on. I replaced gas valve and furnace control board. It worked for 3 days and now goes into lock out after 3 tries.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Nordyne furnace in my manufacture home that will not
i have a Nordyne furnace in my manufacture home that will not fire. It has a standing pilot that stays lite and i got 24 volts at the gas valve that has a slight buzzing noise until i pull one of the … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Xb80 furnace no ignition with 2 blink error code, main fan
Xb80 furnace no ignition with 2 blink error code , main fan runs but no heat. you can put a call from the t-stat for heat and the induction fan turns on and runs, pressure switch closes as soon as the… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
having trouble firing my american standard silver series furnace;
having trouble firing my american standard silver series furnace; replaced gas valve and air switch. Igniter comes on but no gas flow into manifold. there is 24 volts measured at the gas valve termina… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,747 satisfied customers
I have a Bryant 398AAV. It was on Propane, but last spring
I have a Bryant 398AAV. It was on Propane, but last spring we converted to Natural Gas and installed a new gas valve and changed the orifice size. We tested it that day and it worked. The tenant has n… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Nordyne TE Series 95+ furnace. Over the weekend I
I have a Nordyne TE Series 95+ furnace. Over the weekend I noticed the furnace making a clicking noise right at the moment the burners were supposed to kick in. For example, turn up the thermostat in … read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a Rheem Criterion II, when I select heat I the small
I have a Rheem Criterion II, when I select heat I the small fan kicks in, both lights come on, the igniter fires up, the burners never light up then the igniter cuts off. The igniter then cycles again… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
When I turn on the main power switch on my Rheem RGPH-07EAUER
When I turn on the main power switch on my Rheem RGPH-07EAUER the bloer motor kicks on regardless of thermostat setting and no fire/heat.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a rheem criterion II rgph-07eauer. the pilot light
I have a rheem criterion II rgph-07eauer. the pilot light isn't igniting. I tried to turn gas valve to off for 5 minutes and then back to on. turned back on electricity to unit, but still no ignition … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
my gas furnace is not heating. the blower fan comes on and
my gas furnace is not heating. the blower fan comes on and the igniter also comes on. it does not seem like the gas is going through the burner but the gas is on… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
re trane xr 90 diagnostic led flashes fast indicating normal
re: trane xr 90 diagnostic led flashes fast indicating normal call for heat but furnace wont fire clicking sounds heard while furnace tries to cycle on any suggestions? thanks tim in alaska… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a hqco furnace model number NUGK075DG06, Last weekend
I have a hqco furnace model number NUGK075DG06, Last weekend tried to turn on heat for first time and furnace wouldn"t work, The inducer fan would run, but the furnace would not fire up. My intermitte… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Need help troubleshooting a new installation of a Goodman
: Need help troubleshooting a new installation of a Goodman 70K btu 95% horizontal : efficiency two stage gas furnace (Model GMH951155dxac). Brand new. : Replaced old furnace with new. Unit ran fine f… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a rheem criterion 2, its three years old,it as working
I have a rheem criterion 2, its three years old,it as working fine till this morning.the igniter comes on,the fan is blowing,but no ignition of the gas.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE A LENNOX HVAC SYSTEM MODEL#CH33-44/48B-2F SERIES G40UH(X)GAS
I HAVE A LENNOX HVAC SYSTEM MODEL#CH33-44/48B-2F SERIES G40UH(X)GAS FURNACE. I PERFORMED AN OHM TEST GAS VALVE AND IT WAS 2.03Mohms. WHEN THE SURELIGHT CIRCUIT BOARD POWERS UP VALVE WITH 28.24V IT KIC… read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
MY GOODMAN FURNACE DOES NOT LIGHT FIRE IN FIREBOX. VENT BLOWER
MY GOODMAN FURNACE DOES NOT LIGHT FIRE IN FIREBOX. VENT BLOWER MOTOR WORKS, IGNITER GLOWS, BUT AFTER 30 SECONDS, SYSTEM SHUTS DOWN. STATUS LIGHT REMAINS STEADY, NO BLINKING.JUST NOT FIRING UP. CAN GAS… read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x