Customer Question
It is blinking 3...

It is blinking 3 times, it says the limit switch is open

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Last night it was cold in the house, I didn't think to look. I changed the filter today and it looks like maybe the pilit is out?

Contractor's Assistant: Do you plan on doing the work yourself?

The unit is only a couple years old

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

I turned it up last night to 78 then 80. It stayed cool all night.

Contractor's Assistant: Anything else we should know to help you best?

The filter did need changed I'm sad to say I fell down on that this time.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
1/5/2018
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,175
Experience: Furnace, A/C and heat pump specialist.
Verified

The flash code is an open high temp limit error.
There may be
several limits on the furnace.Blow describes locations:
PRI***** *****MIT
The pri***** *****mit control is located on the partition panel and monitors
heat exchanger compartment temperatures. It is a normally closed
(electrically), automatic reset, temperature-activated sensor.
The limit guards against the overheating as a result of insufficient
conditioned air passing over the heat exchanger.
AUXILIARY LIMIT
The auxiliary limit control(s) are located on or near the circulator
blower and monitors heat exchanger compartment temperatures.
They are a normally-closed (electrically), manual-reset, temperature
activated sensors. These limits guard against overheating as a
result of insufficient conditioned air passing over the heat exchanger.
VENT DRAFGAURD
These would be located on the draft hood if you have one on your furnace.
ROLLOUT LIMIT
The rollout limit controls are mounted on the burner/manifold assembly
and monitor the burner flame. They are normally-closed
(electrically), manual-reset, temperature-activated sensors. These
limits guard against burner flames not being properly drawn into the
heat exchanger.
Lets start with the most simple and easy. Look near burners for limits with a little button in center.It will push in to reset.If none are tripped we will go from here. Let me know if you have a multi meter for troubleshooting.
http://i.imgur.com/CGkB9sa.jpg

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I don't have one. I don't see any buttons near the burners.
Customer reply replied 6 months ago
There is a red button right below
Customer reply replied 6 months ago
It has 2 red wires coming off of it
Customer reply replied 6 months ago
I pushed it but it's still blinking
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Follow the red wires and see if they go to more limits.There should be at least 2 or 3 more in the circuit before wire goes back to board.

If no buttons on limits try bypassing one at a time until we determine which is open.

https://i.imgur.com/WqmGzzO.png

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Ok there it another one on the top left but again nothing happened
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

What is model on furnace? There may be one tucked away on blower housing that is often overlooked.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I see model EZ-1625
Customer reply replied 6 months ago
Or would that just be the base
Customer reply replied 6 months ago
AbA 100 NI4R
Ser###-##-####
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Looks like furnace is made by an independent company Texas furnace, not much info available for me to pull a manual. Do you have a muti meter to troubleshoot to see if there is an open in the limit circuit?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I do not
Customer reply replied 6 months ago
Where is the limit circuit?
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

OK if furnace is saying we have an open limit we have to either trace that red wire from where it leaves board through limits until it comes back to board.That is considered the "limit circuit". If no limit is open the board is failing.

Can you attach a picture with both furnace panels remove standing back about a foot from furnace?

I was hunting a manual online but nothing available.Also if you can locate wiring diagram and sent a picture of it.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
There is a diagram on the cover panel would you like a picture of it also?
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

THat would be great

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I was looking at that, does the "w" mean white
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

W is the heat circuit from thermostat.When you call for heat, 24 volts comes from W at thermostat, through these limits, through the pressure switch and if all are "closed" continues to gas valve and energizes valve.

The error code is saying one of those limits is not closed.

TRy unplugging each and bypass it like this

https://i.imgur.com/WqmGzzO.png

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I'm going to ask a dumb question here, but what do I use to put in there ?
Customer reply replied 6 months ago
I mean will a paper clip or something like that carry the current?
Customer reply replied 6 months ago
Ok I did that with the two that plugged into the red push buttons did you also want me to do it with the one in the middle? The one that is one on a gray wire and one one red wire?
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Absolute. Or if you have a car fuse you can use it.

https://i.imgur.com/Aqd9O0f.png

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Yes fo the one in middle too

Ask Your Own HVAC Question
Customer reply replied 6 months ago
We still have the blinking light
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

OK if all limits are closed make sure connections are good to board and if so It looks like board is giving false code.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
that means what?
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

POints to a bad board , but hate to tell you to buy aboard without being there with a meter and putting my eyes on everything.I would probably get a local tech to verify before buying board as it could be something I can't see.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
really I'm no closer than I was an hour ago?
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

You have proved the limits are closed and the board is saying they are open

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have a Comfortmaker furnace Model G9MXE0801716A installed
We have a Comfortmaker furnace Model G9MXE0801716A installed new in May 2015. The furnace keeps shutting off intermittently (mostly during the night when the temperature drops) with Error codes 4 and … read more
airheatman
airheatman
HVAC Technician
9,175 satisfied customers
We have a honeywell furnace and air conditioning unit, we
we have a honeywell furnace and air conditioning unit, we just moved into the house and theres no manual. how do you switch the air conditioning to the heat? its just blinking and says filter, which I… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a furnace Model G9T10014UPC13B. controller is a
I have a Coleman furnace Model G9T10014UPC13B. controller is a White Rodgers 50A50-241. Furnace seems to run constantly and barely keeps house comfortable although it's not that cold out. Elect bill l… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My Goodman furnace will not reach the set thermastat temp for
My Goodman furnace will not reach the set thermastat temp for the last two days. My thermostat is set at 72 degF, yesterday it got as high as 70degF, last night down to 69degF, and this morning down t… read more
type2technician
type2technician
253 satisfied customers
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine for about 3~4 cycles then I get a green flashing light. Reset switch and runs fine for another 3~4 cycles. Help… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Trane xb80 furnace throwing 'open high limit device ' code.
Trane xb80 furnace throwing 'open high limit device ' code. Need assistance due to cold weather this evening!… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have an american standard freedom 95 comfort r unit. I have
I have an american standard freedom 95 comfort r unit. I have the thermostat set to 73 and its 78 in the house. The cooling comes on till it gets to 77 then stops and the thermostat says "wait". When … read more
Expert
Expert
I have a trane xe80 with a rodgers 50a50-471. The unit will
I have a trane xe80 with a white rodgers 50a50-471. The unit will work initially and then the gas will cut off and will not relight. Blower continues to blow and does not stop even when heat call is c… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a Carrier Model 58STA/STX. It stopped working in the
I have a Carrier Model 58STA/STX. It stopped working in the middle of last night. Just checked LED, got the code 33. The blower is running and there is cold air coming out of registers. What do I need… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
The inside fan is running, the outside fan is running, the
The inside fan is running, the outside fan is running, the pipes are room temperature. The outside unit seems to be quieter than it had been previously and I notice the lights dim when the A/C is enga… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Hi I have an American Standard Freedom 80 Single Stage. (I
Hi I have an American Standard Freedom 80 Single Stage. (I think split system as it controls both the heat and air conditioning) My father changed the air filter last night and poured bleach down the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem 80 Plus (central HVAC), which has been in service
I have a Rheem 80 Plus (central HVAC), which has been in service for over 20 years. Had a service contract for a long time, and I recently canceled it. It has been acting up where it is not keeping a … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Ruud achiever Super quiet 80 which runs the heat upstairs...
I have a Ruud achiever Super quiet 80 which runs the heat upstairs... thermostat tells it to turn on but all we're getting is cold air blown thru the up stairs. Basically it won't ignite. I installed … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have an amana 80 sse furnace. It had been working fine until
I have an amana 80 sse furnace. It had been working fine until today. Now, the blower is working, but no heat...The indicator light is blinking 4 times. I changed all filters, shut the system off, the… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
my furnace isnt working right it was just blowing cold air
my furnace isnt working right it was just blowing cold air last night when i turned it off waited 5mins and turned it on it would work for a little bit but then the warm air turned cold again today th… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
nordyne M1MA 070A AW series furnace. Keeps blowing luke warm
nordyne M1MA 070A AW series furnace. Keeps blowing luke warm air and HSI continuously lights, because flame keeps going out. Sometimes locks out due to failed ignition (4 blinking red lights). HSI rep… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
We have a Trane air conditioner with an intermittent problem.
We have a Trane air conditioner with an intermittent problem. Every couple of days, it randomly starts to blow tepid air and then stays on all the time because it can't reach it's setpoint of 78-80 de… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am looking for some information on just what might be causing
I am looking for some information on just what might be causing this code to show up on my furnace. I have a armstrong air ultra v tech 80 furnace. it keeps throwing a code 4 ( open limit switch or li… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x