I my heating elements aren't coming on in my furnace. I checked the breakers in side of the furnace and one has current going to it and the other one doesn't. I thought the breaker was bad but I switched them and the breaker is good. There is no power going to the breaker.
Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 20 minutes by:
1/4/2018
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago
Steve Peck
Steve Peck, Over 24 years experience Just Ask, quick HVAC repair!
Category: HVAC
Satisfied Customers: 16
Experience: Owner at Steve Peck Heat And Air
Verified

Hello, Im Steve How can I help.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
My furnace blower will come on but no heat. I checked the breakers and one breaker has power and the other doesn't. I thought the breaker was bad but when I switched it there is still not power coming to it.I was wonder if the disconnect outside controls the heat also or just the a/c?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

It shouldn't

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

The power for both breakers should come from the breaker box.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
one breaker has power and the other one shows zero when I check it with a voltage meter.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Do you have something that looks like 4 breakers in furnace in a 2 and 2 pattern?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

If you would like you can attach a picture of the breaker setup.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
they are double pole breakers but just one switch. one is 60 and the other is 30
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Perfect thanks, ***** ***** is evidently the one that has power, correct?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Okay, the way they are setup is the 60 powers the fan and first set of elements and the 30 is for the other element.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

So we have a problem with the first 2 mainly and the other will stage on after the other two have ran for awhile.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Kind of a secondary problem we can get to in a minute.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

So are you ready to jump in this thing?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I am
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Good deal I'm here for you. You do have a electric meter?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I do
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

I would like to work on getting the first 2 stages of heat first then we will look at the other power problem, Sound good?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
sounds good
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

If you test (with power on and unit calling for heat) the 2 working breakers to each other what is the voltage?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it's not separate breakers, it looks like a double pole but it only has one switch
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes the place where the wires connect should be 2 seperate sets.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
245
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Perfect now test from one of those points to one end of the element.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Then the other.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Is it 0 on both? or 240 on the other?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the other is 245. I went from the red to both elements and it was 0. I went from the black to one element and it was 245 and the other one 0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Okay good, Now one end has wire connect from element to limit switch (small disk with 2 wires) test black to both sides of limit.Please

Ask Your Own HVAC Question
Customer reply replied 1 month ago
244 on all sides of the top one and 0 on all sides of the bottom one
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Does your meter have a clamp on AMP

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it has one
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

if you clamp around the wire to element and set meter to ac amp what do you get?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

The next test is the stack of switches, on the bottom do it read 24V from one side to other...very bottom probably has wire soldered to it.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm not sure if I'm doing this right but I am getting 1
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

The other test should look like this.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

And yes around 1 is what I expected.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I just replaced the sequencer because it wasn't turning off
Customer reply replied 1 month ago
When I first replaced the sequencer it worked fine for about and hour and then it stopped heating
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Okay has It worked since, the quit?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Okay

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm waiting for it to come back on so I can check the sequencer. I had cut it off and it has a 5 minute delay when turning it back on
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

On the other side on element the wire comes from element to single switch, what is the voltage red and black test?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Sequencer on left side? this is probley on right, between elemt ends.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
on the sequencer where do I put the leads
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Very bottom where one side has wire welded on to other side same place.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm getting 0
Customer reply replied 1 month ago
ok, should I be getting 0?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

We should be getting 24v to allow fan to run.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
maybe I'm not checking it right cause the fan is running
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

can you attach a pic. for the controls there where you are working so I can describe better?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Basicly the inside of the furnace.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Thanks Let me look a second.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Alright in the pic of the seq. the bottom I can see has black wires on one side I cant see the wire color on the other but yours are not connected together like the pic I sent.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

That is actually a heater that causes the thermal disks to close points.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it was connected but when I pushed the wires on it came off. The old one wasn't welded
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Thermal disks stacked on top on heater causing delay in starting each element.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

We should have 24v across the bottom or heater .

Ask Your Own HVAC Question
Customer reply replied 1 month ago
from one side to the other or do I test side by side
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Across on one switch.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Common or ground on 1 side and 24v on other. the other switch should be the same.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

we can do a phone conversation if that is easier?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

All of these tests are with furnace running

Ask Your Own HVAC Question
Customer reply replied 1 month ago
on the top one when I check the middle it has 246 but the bottom 0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Okay 240 is across the top?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the sequencers are side by side but installed one is on the top and the other on the bottom. When I tested the top one in the middle I got 246
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

So lets back up, the thermostat wires that come to the furnace. We should have 24v from case or ground to red wire, white and green.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
from white to ground I have 121
green to ground 93
red to ground 122
Customer reply replied 1 month ago
which wires are the thermostat wires
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

OK so lets test to common wire instead of ground, probably a black or blue wire that comes out by the others.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Again to R,W and G.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
where are these wires connected to cause I think I'm testing the wrong wires
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Should go to small (normally) brown wire to thermostat and outside to a/c unit.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
they have wire nuts on them, do I take them off and check?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes if you cant get up inside very well, the only risk is the common wire. Don't let it touch the others...

WAIT these might have 110v if it is wired wrong so be very careful.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
can I check at the thermostat?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

If the comon or C wire is there.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

But again if its wired wrong could be 120V.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
The system has to be running? When the thermostat front is removed the unit turns off
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Thats ok for this test. we should only see 24v from C to R with tstast face off.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm getting 27 from C to R
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

AWESOME!

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Put tstst back togather and go back to heater.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

WHen your ready trace the white wire from wire nut to the first connection and where it goes.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the white wire from thermostat?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes where does it go in furnace?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
on the bottom of the the top sequencer. There is another white wire coming from a plug but the other end has a wire nut on it but it's not connected to anything. There is a red wire the same way.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

that is where we should have a black or common wire going

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

on the opposite side of the switch.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
when you say switch are you referring to the sequencer?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes a 24v and a common will cause the heater to work on the bottom of the seq.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
there is a black on the other side and a black and white on the other side
Customer reply replied 1 month ago
all of the other wires on the sequencer is black except for on the bottom one there is a blue wire
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

ok so the tstat wire goes to one side, it is 24V when a call for heat so on the other side should be something going to common.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
there is a red single wire and a white single wire that comes from a connector but the other end isn't connected to anything. It has a wire nut on it.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Can you tell what they are connected to on other end?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok the two with wire nuts are just extras that are for different voltage if needed, 120v,208v,240v.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

What color does it hook to on transformer, thing with extra wires.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
what color does what hook to?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

The opposite side of seq. from where W hooked.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
there is not a wire coming from the transformer to the sequencer
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

humm. Ok where does the wire opposite of W on seq. go?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
There's a black and white wire on the other side of sequencer and it is hooked to a yellow wire coming from the transformer
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok blue and Yellow are hot and common on transformer.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

So back to testing from white thermostat side to yellow transformer side do we get 24v?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
that is the transformer but I have 0 when I test the the white and black and white wire
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Can you tell where blue wire from transformer goes to??

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it's in a wire nut to a red wire that goes to a connector
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok I'm kinda jumping around , sorry but what does the red wire from thermostat go to?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it's hooked to a connector and the red wire coming from the other side of the connector is connected to the blue wire from the transformer with a wire nut
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Get me a second.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok so im seeing yellow from transformer to Black and white to sequencer the blue from transformer to red on thermostat then should come back on white with call for heat and back to other side of sequencer. does that sound correct?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
why wouldn't there be power coming to the 30 amp breaker
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

I'm going to laugh and appolage if we go to thermostat and turn the fan switch from on or run to auto, then switch the heat/cool to heat.

I'm thinking we have a thermostat problem now.

But 30 amp is different.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
The thermostat is on auto and it is on heat
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

We can test the 30amp on the "IN" side of breaker each side to ground the to each other.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Whew,

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I did that but I get 0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok thats from breaker box to there, we will need to test in breaker box to confirm it is leaving there and should go straight to heater 30 amp.

That's why we tested to ground with each leg to see if one is hot and not the other.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Back to main heat we can test from black/white on contactor to wire nut at Red to thermostat, I'm confident we do'nt have 120v now. The wirenut can be removed at furnace to redwire.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

The 30 amp should only run a single element that will come on after the first 2 have ran awhile.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
is it normal to not have any voltage showing there?
Customer reply replied 1 month ago
check from black and white wire to red wire that is connected to thermostat red wire?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Are you referring to 30 amp? if so then no It should have voltage at breaker all the time but sequencer will close allowing heat element.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes please, then to white coming from thermostat.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok. does the furnace need to be running?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Should read 24v to red and also 24v. to white from thermostat.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes we need power through thermostat

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Thank you for sticking with it, your the boss!

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Most of my tech's would have given up by now, I'm impressed.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
red 119
white 122thanks
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok lets test sequencer black/white to case, please.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
122
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Now red then white thermostat wires to case or ground.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
is there another red?
Customer reply replied 1 month ago
white 122
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

We are testing Red at wire nut to case this time not to black /white.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
120
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

WOW, this makes no sense that at furnace we have 120v going to thermostat but at the thermostat we have 27V.??

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

It is sounding a lot like your house has a grounding problem that is allowing high voltage to flow back to anypoint.

Give me a second to think again, thanks.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
should the system have been running while I checked these?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes, but we should never see 120 volt AC at thermostat on this system.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the system wasn't running
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok lets test red the white thermostat to case with system running please.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Wire nuts off and wires still connected.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
okay
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

In the HVAC business we call this bull dogging in on a problem...We just won't quit. Thanks

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Thank you
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

I think we have something in common, we don't like to give up or let a problem beat us.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
yeah. I got the same thing except on the red I got 94
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Turn off the 30 amp breaker and test one of them to confirm that the problem is not on that side.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm still getting the same thing
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok turn off both the 30 and 60, then unplug the top element just the wire on the opposite side of sequencer.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it's unplug
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

With it clear from any metal or people/pets to short out on. and don't get close. turn on the 60 amp and let it run to see if the system will run and heat now.

BE VERY CAREFUL AND IF YOUR NOT COMFORTABLE DON'T DO IT.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Are you still with me?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the furnace just came on
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

I think we have an element with the wire broken laying against the case causing the voltage everywhere.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
do I need to put the front on the furnace in order for it to blow out the vents correctly
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

It can take up to 90 seconds for other element to kick in

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

no it all stays in vents

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

It is just sucking from room not from return vent

Ask Your Own HVAC Question
Customer reply replied 1 month ago
okay.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

do you think you have heat anywhere yet?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Can you tell me what the brand of furnace is?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
not yet
Customer reply replied 1 month ago
Intertherm
Customer reply replied 1 month ago
still no heat, been about 2 minutes
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok lets kill both breakers again

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I only had the 60 on, was the 30 supposed to be on also?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

After that, with both off pull the other end of that element wire off.

you were fine during the test.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

we are going to do a continuity test on the element.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok, the top element has 2 black wires on one side and 2 red wires on the other side. The first time I disconnected the top black wire. Now do I disconnect the top red wire?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Correct, will your meter test continuity?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I think so, how do I do that?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago
Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok, I've looked at it.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Set meter to OHMS or upside down horseshoe touch leads together should read close to 0.

That picture is what is inside that you can't see

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok,,
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

if the leads are apart it read blank or says a word. on ohms setting.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it has a 1
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Once you get set to OHMs and understand what closed or together reading is test across the two plugs of the element.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the closed reading is 0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

What does it say when they are apart not touching anything

Ask Your Own HVAC Question
Customer reply replied 1 month ago
1
Customer reply replied 1 month ago
when I test the element it doesn't change
Customer reply replied 1 month ago
Is this supposed to be checked with power or no power?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

if you hold the test pins in each hand what does the reading say, the continuity of your body?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

No power

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it keeps going between 12 and 13
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok, but when the pins touch nothing it reads 1?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Also test element, 1 side to the case of furnace, or ground.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
when I test the 2nd from the top and the bottom I get 12
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

ok that is with no wires connected correct?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Or is that to the case?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I get 12 with wires connected. When I test the top with no wires connected it stays at one when I test them together and when I test them to the case. When I check all elements with the case it stays at 1
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

So 12 tells us closed or making connection and 1 is not shorted or connected. If element 1 reads 12 across terminals with no wires connected and 1 from each terminal to case, it is good.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the top one is reading 1 all of the time
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Put wires back on and repeat test on next element, remove it's wires , test terminals to each other then to case.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok so element 1 is open or in other words broken.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

I am hoping to find the element that is shorted to case.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
okay.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

If you would give me the readings.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Give me a few I had another situation I had to take care of
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

No problem.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm back
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Good deal

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Alright did you get to test each element? Or are we back on it now?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the top one is reading 1 all of the time.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok broken wire on element but not touching case.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Put wires on it and remove wires from #2 and test.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
oh ok. I got 12 on the second one
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Great and 1 when tested to case?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Same thing replace #2 wires and remove and test #3

Ask Your Own HVAC Question
Customer reply replied 1 month ago
12 and 1 when tested to the case
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok now, as I remember the wire from each end of element only goes a short distance and plugs into a switch on each end.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

replace wires on #3.

Then on #1 remove wires from switch end of wire to element. We are taking it out of the system.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
done
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Now lets power up both breakers and start unit.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok, waiting for it to turn on
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

After unit starts running lets test power to elements 2 and 3 with unit running.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I got 11
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Be sure to set your meter back to AC volts, and with wires on and system running test for 240v on each end of both 2 and 3.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Also on AC volt test each end to case, please.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm getting 0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

0 to case also?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
when I test 2 to case I get 122 for both but together 0
when I test 3 to case and together I get 0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Test 30 amp breaker to case, please

Ask Your Own HVAC Question
Customer reply replied 1 month ago
0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

With system running can you test across sequencer black/white to other side where white from thermostat is connected.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I have to wait for it to come back on again. I keep turning it off because it's making it cool in the house.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok, when the blower kicks on we "should " have 24v across the heater at the bottom of the big sequencer.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm getting 0 when I test them together and 121 when I test each to the case
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

these are the wires on the switch closest to the heater. Below the wires that go to elements.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
what do you mean by big sequencer, they are both the same
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

The one that has the wires that go to element 1 and 2, has more stuff on it.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
that's the one I tested
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Well I think you have done it, I just can't figure how you have 120V in the places you do.

On last thing.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

You can turn off breakers and take red and white thermostat wires loose at wire nuts. Then Put the 2 wires coming from furnace together with wire nut.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
put the two wires that I take toose together?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

yes the bigger wires that come from furnace not the smaller wires from thermostat. should be red and white also.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
o k
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

we are leaving the to thermostat wires out of connection.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

We are bypassing thermostat wire in wall

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Then turn breakers on.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Red sends power to thermostat and white is the return to energize heat.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Is fan running?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
not yet
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

can you heat or smell anything different?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
no
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

If you could test across bottom of sequencer again please.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
26
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

nice.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

If you could test from 60 amp breaker red wire to sequencer where elements connect please.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
218
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

On both middle and top?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Still no fan?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
no fan and now I'm getting 0 everywhere
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

how about at 60 amp breaker?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the same
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

240v or 0?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
the breaker itself is 240
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

ok lets put the thermostat wires back to original place with wire nuts.

Oh you can turn off both breakers.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok done
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

I think the only thing I can do at this point is to turn it over to someone else, You have me on this one.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok well thanks for your time
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

I strongly suspect it will take an electrician to find the no power to 30 amp and I suspect the other issue might be related. I'm guessing a grounding issue still.

So sorry.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I would like to be reconnected to my previous technician
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

This is Steve, am I the one you were looking for?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I found out why the 30 amp breaker didn't have power. There was another breaker in the the breaker box that went to it. So now I have power going to all of the elements but no power to the left side of the first one. The elements still aren't coming on. I just wanted to run that by you because that was one of the problems yesterday.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Ok the power to elements should be across terminals, 240v correct?

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

That is across elements not on the sequencer.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
does it have to be running?
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Yes, power to unit and calling for heat or it should not have 240 across element.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'm getting 0 when I check across elements but I'm getting 120 when I check to case except the top left I'm getting 0
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

The sequencer should get 24v power from thermostat, then heat up enough to let power pass through to element.

Ask Your Own HVAC Question
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Is top left the closest to sequencer?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
is that checking across sequencer?
Customer reply replied 1 month ago
I'll probably have to get back with you later because I have to get ready to go somewhere
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Me too. thanks!

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Thanks.
HVAC Technician: Steve Peck, Over 24 years experience Just Ask, quick HVAC repair! replied 1 month ago

Later,

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Is there anything that could have been shorted out?
Customer reply replied 1 month ago
I was looking back over the furnace and I notice that the new sequencer is not numbered the same way as the old one. I think the wires might have gotten screwed up
Customer reply replied 1 month ago
I was checking to see if you would still be able to help me with this project?
Was this answer helpful?
Ask Steve Peck Your Own Question
Steve Peck
Steve Peck
Steve Peck, Over 24 years experience Just Ask, quick HVAC repair!
Category: HVAC
Satisfied Customers: 16
16 Satisfied Customers
Experience: Owner at Steve Peck Heat And Air

Steve Peck is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rheem furnace blower runs on low but will not run on high
rheem furnace blower runs on low but will not run on high furnace goes off on high heat limit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My Rudd furnace blower vibrates the entire house. Research
My Rudd furnace blower vibrates the entire house. Research indicates a motor/fan set screw may need tightening, but I can't see one. Where is it found? Can it be adjusted without removing the motor?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Concord 90 furnace blower runs wont stay lit. I blew out
concord 90 furnace blower runs wont stay lit JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: yes JA: Anything else we should know to help y… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My 59SC2b furnace blower running time and blow cold air
My 59SC2b furnace blower running long time and blow cold air after heating cycle. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace blower stopped suddenly. I live in about 2,000sq
My furnace blower stopped suddenly. I live in about 2,000sq feet single family home. I called an HVAC technician. They arrived and installed a new motor. However, after they left I run the furnace and… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have an older luxaire commerical furnace blower motor runs
have an older luxaire commerical furnace blower motor runs all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My furnace blower wiil not start. Hopefully. Furnace tries
my furnace blower wiil not start JA: Did you check the furnace's filters? Customer: no JA: Do you plan on doing the work yourself? Customer: hopefully JA: Anything else we should know to help you best… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My evcon furnace blower fan cycles every day at 8:20 with no
My coleman evcon furnace blower fan cycles every day at 8:20 with no demand and no exhaust fan operation. It just co es on runs for 2 minutes then shuts down, and there was no previous heat dema d … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Nordyne furnace blower starts immediately when I turn on
My Nordyne furnace blower starts immediately when I turn on the switch. The LED light on the control board flashes 5 times. There is no flame. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My '92 Carrier model 58ssc furnace blower motor has finally
Hi! My '92 Carrier model 58ssc furnace blower motor has finally quit. I wonder what I can replace it with … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a question about a furnace blower that is not
We have a question about a Bryant furnace blower that is not working. The model number is ***** We have noticed a blinking light error that has two short and four long blinks. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a loud noise coming from furnace blower motor. Do i
I have a loud noise coming from furnace blower motor. Do i need to oil up the motor? Its a lennox g40uh (x) … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I'm replacing a furnace blower motor and assumed it would be
I'm replacing a furnace blower motor and assumed it would be plug and play. Old motor had 5 wires; white, brown, black, red and blue. The brown and white went to the cap, with another white wire comin… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
432 satisfied customers
My furnace blower won't shut off. Have confirmed it's not
My furnace blower won't shut off. Have confirmed it's not the thermostat (by disconnecting same). Could the fan relay cause this? … read more
derekh1966
derekh1966
0 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x