The electrician was here this morning and had more

Customer Question
questions. Is the connection to...
The electrician was here this morning and had more questions. Is the connection to the generator panel to be 220V. Where exactly the new connection will be - yellow&black (see attached photo). With this new connection will I need to use only the option of "heat pump only" on my control thermostat so that the heat coils doesn't goes on when the generator is supplying the power? Presently I am on "System in control".
Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
1/4/2018
HVAC Technician: Daniel Plourde, HVAC Technician replied 7 months ago
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 464
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified

hi i am dan i can help you with this. can you describe your situation a little better as what exactly you are trying to do with the system?

Ask Your Own HVAC Question
Customer reply replied 7 months ago

Answer and reply from your service on Dec. 27, 2017
I just install a new electrical panel to be able to use a generator in case of electrical power supply failure. In the part of the panel for the generator use I have the geothermal heat pump unit Model 50YDS049NCD301 - Serial 4308V65160 but is not working because the coil and fan are on the main panel with the electric heater as one large packages with a need of too much amperage to connect to my generator package. My question is it possible to have a separate connection of the coil + fan (model FE4A FE5A) and the heater installed on top.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The heat pump is not working if the coil, fan and heater breaker is off

Contractor's Assistant: Do you plan on doing the work yourself?

No I used an electrician for the new panel and will use the same to make the corrections. I am not home now and only be back in one week but I like to correct the situation soon after my return.

Contractor's Assistant: Anything else we should know to help you best?

Need a way to separate the connection for the coil and fan from the heater which need too much power for my generator.27 December 2017 12:52
27 December 2017 01:03
airheatman
HVAC Technician
Absolutely you can run a seperate power supply directly from the electrical panel to the heat kit only.27 December 2017 01:08
airheatman
HVAC Technician
You will connect the circuit that will be supplied to generator to the yellow and black factory wires in the air handler and connect the higher amp breaker directly to the heat kit.My goal is to provide you with excellent service. If you are satisfied, please rate me. If you have follow-up questions on this same topic, use the reply box below. To start a new conversation with me on a new topic, request me again.

HVAC Technician: Daniel Plourde, HVAC Technician replied 7 months ago

OK THANK YOU FOR THAT, JUST TO CONFIRM YOU WANT TO BE ABLE TO RUN JUST THE FAN AND ELECTRIC HEAT IN THE AIR HANDLER WHEN USING THE GENERATOR CORRECT?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I want to run the coil for the heat pump and the fan on one breaker associated with the generator. Panel seperate from the electric heat coil.
HVAC Technician: Daniel Plourde, HVAC Technician replied 7 months ago

OK UNFORTUNATELY YOU CAN NOT RUN THE HEAT PUMP UNIT AND THE FAN IN THE AIR HANDLER FROM ONE CIRCUIT BREAKER. THE MAIN REASON BEING ELECTRICAL CODES WILL NOT ALLOW IT AS THEY ARE 2 SEPARATE APPLIANCES AND REQUIRE THEIR OWN CIRCUIT BREAKER, ALSO THE CIRCUIT BOARD IN THE AIR HANDLER NEEDS TO BE POWERED TO RUN THE CONTROLS ON THE SYSTEM WHICH MEANS THE WHOLE AIR HANDLER NEEDS TO BE POWERED WHICH WILL INCLUDE THE ELECTRIC HEAT. THE WAY TO DO WHAT YOU ARE TRYING TO DO IS DURING GENERATOR POWER YOU RUN THE SYSTEM IN HEAT PUMP ONLY MODE AND THE ELECTRIC HEAT won't COME ON. THE HEAT PUMP UNIT FAN AND CIRCULATORS WILL RUN. FOR AN ADDED LEVEL OF SECURITY TO PREVENT THE ELECTRIC HEAT FROM RUNNING YOU CAN HAVE YOUR ELECTRICIAN INSTALL A TOGGLE SWITCH ON THE AIR HANDLER THAT DISABLES THE ELECTRIC HEAT. OR YOU CAN USE JUST THE FAN AND ELECTRIC HEAT AND DISABLE THE HEAT PUMP AS LONG AS THE ELECTRIC HEAT BY ITSELF IS NOT TOO MUCH FOR THE GENERATOR.

Ask Your Own HVAC Question
HVAC Technician: Daniel Plourde, HVAC Technician replied 7 months ago

OK IF YOU RUN JUST THE ELECTRIC HEATER ON A SEPERATE BREAKER THEN YOU WILL HAVE TO DISCONNECT THE BLACK AND YELLOW WIRE GOING TO THE ELECTRIC HEATERS AND CONNECT THE POWER FROM THE NEW BREAKER TO THOSE 2 WIRES.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Where do we connect the cable for the electric heat coil now? What happen when the main power is back? Will the fan work with the electric heat coil also.
HVAC Technician: Daniel Plourde, HVAC Technician replied 7 months ago

RIGHT NOW THE POWER FOR THE ELECTRIC HEAT IS CONNECTED TO THE SAME POWER SUPPLY FOR THE CONTROLS AND FAN. YOU WANT TO RUN THE ELECTRIC HEAT ON A SEPARATE POWER SOURCE SO WE FIRST NEED TO ISOLATE IT. WE ONLY NEED TO ISOLATE THE HIGH VOLTAGE CIRCUIT OF THE ELECTRIC HEAT. THE LOW VOLTAGE CIRCUIT MUST STAY CONNECTED. ONCE THE BLACK AND YELLOW WIRES ARE DISCONNECTED FROM THE MAIN POWER THEY WILL NEED TO BE CONNECTED TO THE WIRES COMING FROM THE BREAKER THAT IS NOT FOR THE GENERATOR. WHEN THE MAIN POWER IS OON EVERYTHING WILL WORK NORMALLY. BASICALLY, IT IS JUST THE ELECTRIC HEATERS THAT DONT GET POWER WHEN IN GENERATOR MODE.

Ask Your Own HVAC Question
HVAC Technician: Daniel Plourde, HVAC Technician replied 7 months ago

IF YOU HAVE ANY MORE QUESTIONS ABOUT THIS PLEASE LET ME KNOW OR IF THIS HAS HELPED YOU I WOULD APPRECIATE IT IF YOU COULD RATE ME ON MY SERVICE BY SELECTING ONE OF THE 5 STARS ON YOUR PAGE SO WE MAY CLOSE THIS QUESTION.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I ask my electrician to share your answers with more experience electrician to understand fully the direction you want us to follow and obtain the result expected. This will need a few days before I know if I have more questions and rate you. If we need your help could we communicate by Skype or Facetime. If yes I need your Skype address or Facetime#.
Thanks
HVAC Technician: Daniel Plourde, HVAC Technician replied 7 months ago

I AM CURRENTLY NOT AVAILABLE FOR FACETIME SUPPORT BUT WILL BE MORE THAN HAPPY TO HELP YOU IN Q&A FORMAT.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Daniel Plourde Your Own Question
Daniel Plourde
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 464
464 Satisfied Customers
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings

Daniel Plourde is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have model AH16X20BA air handler. We know the heat pump
We have coleman model AH16X20BA air handler. We know the heat pump is bad and just want EM heat to come on. Thermostat batteries are good . Power to the heat strips but no fan operation or heat.HELP? … read more
Bill
Bill
Service Mgr
114 satisfied customers
I have a lennox heat pump with12.5 eer i bought about 25
i have a lennox heat pump with12.5 eer i bought about 25 years ago. i live in south Texas and use heat every other year. the AC works good, last month it was cold. i turned on heat pump, worked overni… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I need a thermostat wiring diagram for a tran xe900 heat
I need a thermostat wiring diagram for a tran xe900 heat pump w/aux heat … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I just install a new electrical panel to be able to use a
I just install a new electrical panel to be able to use a generator in case of electrical power supply failure. In the part of the panel for the generator use I have the geothermal heat pump unit Mode… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We are having issues setting up or new Nest Thermostat. The
We are having issues setting up or new Nest Thermostat. The wires our system has is: Rh, W, C, G, Y/Y2 & O/B When we hooked it up to new thermostat it said we couldn't have an O/B wire without Y1 but … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a cold flow heat pump.trying to change thermostat out
I have a cold flow heat pump.trying to change thermostat out that requires a c wire. not sure where to connect the new C wire on to the Coldflo. unit can you help me. I can send pics of unit wiring.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We are going from a Rheem Q674L-1504 thermastat to a
We are going from a Rheem Q674L-1504 thermastat to a Honeywell Th5220D. White, yellow, green, red, blue, black, brown. Each go to W2, y, g, r, b, l, - where does brown go?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm having trouble with my circulation fan in the furnace.
Hey I'm having trouble with my circulation fan in the furnace. Keeps going on and off. I have a nest thermostat that gets its power from the wires connected to the furnace and it seems that's not gett… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing a Robertshaw 9520 with a Honeywell RTHL3550.
I am replacing a Robertshaw 9520 with a Honeywell RTHL3550. We are pretty sure we have all the wires in the correct spots but the compressor is not coming on. The fan comes on and runs fine. This is a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hi I have also have a EB23B electric furnace. My problem is
hi I have also have a EB23B electric furnace. My problem is I have heat sometimes. I have replace one element and sequencer. My thermostat heat light cycles. It will occasionally put out some heat. th… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I am trying to replace my mercury thermostat in my condo. I
I am trying to replace my mercury thermostat in my condo. I have a First Co HBC-HW Fan Coil unit with a 24/120V transformer. I purchased a modern Honeywell 7 day programmable thermostat. Is this therm… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Replacing white rogers 180-261 with new white rogers 1F80-0261 Zoned
Replacing white rogers 180-261 with new white rogers 1F80-0261 Zoned system in Townehouse with Robertshaw Slimzone 2701-001 Zone Control System Have following existing wires White Red Blue Green Orang… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
I live in an apartment building that is more than 50 years
I live in an apartment building that is more than 50 years old and wish to replace a White-Rodgers thermostat, model number unknown, connected to a water baseboard radiated heat system. The wiring has… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Trane XL1200 heat pump troubleshooting. Fuse blows when in defrost.
I have a trane xl1200 heat pump. Worked great in the summer for the a/c kept the house nice and cool. Then winter came I turned the therm to heat setting. It kept the house pretty warm in september di… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have 7 wires from the HVAC system and I am trying to install
I have 7 wires from the HVAC system and I am trying to install a programable thermostat with only 4 to 5 options. The old one had a port for each wire. For the new one I assume the Red wire goes to Rh… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing a York T874R1046 7 wire 2-Stage Heat w/ Heat
I am replacing a York T874R1046 7 wire 2-Stage Heat w/ Heat Pump Thermostat with a Lux TX9100E. Need to match the wires.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Rheem horizontal gas furnace in my attic attached
I have a Rheem horizontal gas furnace in my attic attached to a Rheem RCFA-HM3617AC. When thermostat calls for heat the IDM turns on a few seconds later, but only runs for approximately 5 seconds unti… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
HI there im installing a Honeywell Visionpro TH8000 series
HI there im installing a Honeywell Visionpro TH8000 series to replace my old thermostat. The old one has wires connected to - Green goes to G, Black goes to C terminal, Red goes to R terminal, Orange … read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x