My furnace short cycles the heat, yes i checked the settings…

Customer Question
My furnace short cycles...

My furnace short cycles the heat

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes i checked the settings on the thermostat, the filters are new and i also just cleaned the blower motor which was extremely dirty

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Yes its an old trane xe60 im thinking its the limit control but not sure

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
1. changed thermostat with new one
2.replaced filters
3. blower motor was extremely dirty and clogged, took out and thoroughly cleaned, reinstalled
4. I see the limit control dial go up to the limit and shuts off the gas. Then it cools back down and turns on again and keeps short cycling.
5. Fan does not shut off weather it is on auto or fan on the thermostat
Answered in 25 minutes by:
1/4/2018
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,402
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. tell me in seconds how short the cycles are please,

.

If you are handy and have a multi meter

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Hi Phil. The cycles are about a 60 secs to maybe 90 secs apart. I do have a multimeter. Unfortunately the unit is so old the wiring diagram has deterioated off both the inside door and on blower. Would model number help ? It's a Trane XE60
Customer reply replied 4 months ago
It may be easier for us to try the live phone call but I will have to wait until tomorrow
Customer reply replied 4 months ago
Which is better for you?
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

click here please.

so far it sounds like a dirty flame sensor rod, clean it down to bare bright and shinny stainless steel.

We can go from there in the morning with a phone call if you wish, its optional.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
i would like to discuss via phone tomorrow because I dont think my model has a flame sensor rod but you are the expert and Im not. I will be back online and available tomorrow evening.
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

All furnaces built since about 1990 have flame sensor rods. if they have a printed circuit board mounted on the blower, or an inducer fan they have a flame sensor rod.

CLick here please

Ask Your Own HVAC Question
Customer reply replied 4 months ago
This is the original furnace and my home was built in 1988
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

The first printed circuit boards were used in furnaces in 1984, full adoption was complete by 1990 .. if yours has a printed circuit board it will be mounted on the main blower inside the furnace... look for it

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok i took pictures of the diagram but it is way too old to see anything
Customer reply replied 4 months ago
I can still upload it
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

Hello, set the limit control to its maximum temperature then measure the temperature of the air deep inside one of the warm air vents at the peak just before the furnace shuts off, then use the same thermometer to measure the room temperature. If the room is 70F the air coming from the registers should be between 120F and 170F... if its cooler than that replace the high temperature limit control.

.

Its an old furnace, it could have some leaks in its heat exchanger, buy two carbon monoxide detectors and put one in the living room and one in your bed room.

.

We can go from there without any time limits

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I dont have a thermometer, I thought we could start by testing with a multimeter?
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,402
9,402 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,402 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I CANT FIND THE RESET RED BUTTON ON MY AMANA AIR COMMAND
I CAN'T FIND THE RESET RED BUTTON ON MY AMANA AIR COMMAND 80 SSE II… read more
tadowhere
tadowhere
Maintenance Supervisor
Vocational, Technical or Trade Scho
90 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Where's my furnace reset button? Furnace fan not working.
Where's the reset button on my furnace?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
How to clean heat exchanger coils, filters have been clean
filters have been clean recently and I am getting an airflow alarm on the thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,808 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
278 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
9,402 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
my rheem classic 90 gas heater keeps shutting down after about
my rheem classic 90 gas heater keeps shutting down after about 5. min any sugestions… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Bryant Plus 90i furnace (355mav). Got a LED code 33.
I have a Bryant Plus 90i furnace (355mav). Got a LED code 33. (Limit Switch Fault) -Indicates the limit, rollout switch or ausiliary limit switch is open or the unit is operating in high hear only mod… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a RPJ Heat Exchanger Comfortmaker hone furnace. The
I have a RPJ Heat Exchanger Comfortmaker hone furnace. The furnace will not go on. Checking the furnace moude I see a red light blinking once, that is saying system lock out. What does that mean, and … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Furnace pressure switch open with inducer on. Help!
Furnace diagnostics indicate "pressure switch open with inducer on." What could be the problem? I recently had my natural gas turned on after being off for a few months. Furnace (Nordyne model KG6RC-0… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
1985 Rheem Imperial 80 plus gas furnace mod # RGDC 07EC1GS
1985 Rheem Imperial 80 plus gas furnace mod # XXXXX 07EC1GS starts and runs correctly for 20-30 minutes and then the main burner shuts down. The inducer motor,pilot flame and main blower continue to o… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
The furnace knob to turn to "on" and "pilot" wont depress
The furnace knob to turn to "on" and "pilot" won't depress.… read more
Phil
Phil
Mechanical Engineer
9,402 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x