My furnace short cycles the heat, yes i checked the settings…

Customer Question
My furnace short cycles...

My furnace short cycles the heat

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes i checked the settings on the thermostat, the filters are new and i also just cleaned the blower motor which was extremely dirty

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Yes its an old trane xe60 im thinking its the limit control but not sure

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 7 months ago
1. changed thermostat with new one
2.replaced filters
3. blower motor was extremely dirty and clogged, took out and thoroughly cleaned, reinstalled
4. I see the limit control dial go up to the limit and shuts off the gas. Then it cools back down and turns on again and keeps short cycling.
5. Fan does not shut off weather it is on auto or fan on the thermostat
Answered in 25 minutes by:
1/4/2018
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,817
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. tell me in seconds how short the cycles are please,

.

If you are handy and have a multi meter

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Hi Phil. The cycles are about a 60 secs to maybe 90 secs apart. I do have a multimeter. Unfortunately the unit is so old the wiring diagram has deterioated off both the inside door and on blower. Would model number help ? It's a Trane XE60
Customer reply replied 7 months ago
It may be easier for us to try the live phone call but I will have to wait until tomorrow
Customer reply replied 7 months ago
Which is better for you?
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

click here please.

so far it sounds like a dirty flame sensor rod, clean it down to bare bright and shinny stainless steel.

We can go from there in the morning with a phone call if you wish, its optional.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
i would like to discuss via phone tomorrow because I dont think my model has a flame sensor rod but you are the expert and Im not. I will be back online and available tomorrow evening.
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

All furnaces built since about 1990 have flame sensor rods. if they have a printed circuit board mounted on the blower, or an inducer fan they have a flame sensor rod.

CLick here please

Ask Your Own HVAC Question
Customer reply replied 7 months ago
This is the original furnace and my home was built in 1988
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

The first printed circuit boards were used in furnaces in 1984, full adoption was complete by 1990 .. if yours has a printed circuit board it will be mounted on the main blower inside the furnace... look for it

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok i took pictures of the diagram but it is way too old to see anything
Customer reply replied 7 months ago
I can still upload it
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Hello, set the limit control to its maximum temperature then measure the temperature of the air deep inside one of the warm air vents at the peak just before the furnace shuts off, then use the same thermometer to measure the room temperature. If the room is 70F the air coming from the registers should be between 120F and 170F... if its cooler than that replace the high temperature limit control.

.

Its an old furnace, it could have some leaks in its heat exchanger, buy two carbon monoxide detectors and put one in the living room and one in your bed room.

.

We can go from there without any time limits

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I dont have a thermometer, I thought we could start by testing with a multimeter?
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,817
9,817 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,817 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Blower on furnace works if put in ON position but not in
Blower on furnace works if put in ON position but not in AUTO position. Gas comes on but shuts off when blower does not come on in after a few … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Im having an issue in which my furnace fan will not
Im having an issue in which my furnace fan will not start/run when the thermostat fan setting is on AUTO with HEAT ONLY. The fan works just fine when set to AUTO with the AC but not with the heat. The… read more
Jason Whatley
Jason Whatley
60 satisfied customers
regan. I have a problem with my xr90 trane furnace. I am
Hi regan. I have a problem with my xr90 trane furnace. I am getting the four flash open limit device code. The filter is new. The furnace will kick on and fire for about 20 seconds but then shuts off.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Trane xb80 furnace throwing 'open high limit device ' code.
Trane xb80 furnace throwing 'open high limit device ' code. Need assistance due to cold weather this evening!… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Rheem gas furnace that cycles and starts runs for 5-10 minutes
Rheem gas furnace that cycles and starts runs for 5-10 minutes main blower shuts off small vent blower restarts and main blower restarts what is wrong… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My blower motor will not run in the AUTO position. I replaced
My blower motor will not run in the AUTO position. I replaced the blower motor last year and the fan relay and still no dice. My furnace is 30 years old and I need one more season from it… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why is SV9502H2522 using a ST9120U1011 unit short cycling
I have SV9502H2522 using ST9120U1011 unit "short cycling" in odd way. Inducer comes on, normal ignition. Blower cuts off mid-cycle, with stat calling. Gas valve closes, blower comes back on. Reignites… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
TraneXE80 furnace control board flashes #4 code. Furnace goes
TraneXE80 furnace control board flashes #4 code. Furnace goes through all operations, fires up, runs for 2 1/2 minutes, gas valve and burner shut off, unit continues running and eventually blowing col… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HVAC Question Trane Model XE 70 with a White Rogers Model
HVAC Question: Trane Model XE 70 with a White Rogers Model 50E47-060 Ignition Control Board. Opened front panel and found board with a continuous blinking red light. Unplugged power and plugged back i… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
OIL FURNACE STARTS,RUNS AS NORMAL,FAN COMES ON ,RUNS A SHORT
OIL FURNACE STARTS,RUNS AS NORMAL,FAN COMES ON ,RUNS A SHORT TIME AND LOSES ALL POWER TO THE FURNACE.FAN DOES NOT WORK ON AUTO OR MANUAL. CIRCUIT BREAKER IN ON POSITION… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a problem with a Lennox G50UH(X) Series No heat. 1st
I have a problem with a Lennox G50UH(X) Series No heat. 1st small blower motor to flue starts up for short period. Then main blower motor starts. No flame no heat. I checked the flue and chimmeny are … read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
carrier furnace... just replaced control board. gas will ignite
carrier furnace... just replaced control board. gas will ignite blower will come on for about a minute then blower shuts off but flames remain lit. please help… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a coleman-evcon furnance. just recently when the house
I have a coleman-evcon furnance. just recently when the house reaches the desired temp, the furnance kicks off like is is supposed to. But it will not automatically re-ignite when it drops below the t… read more
BARRY
BARRY
owner
Associate Degree
56 satisfied customers
I have a Trane XB 90 Gas furnace. I have cleaned all the drainage
I have a Trane XB 90 Gas furnace. I have cleaned all the drainage hoses, replaced the filter and have installed a new thermostat. The furnace starts its cycle as the fan blows. It starts and stops sev… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi, my Trane TDE060A936K2 Gas Furnace will provide heat for
Hi, my Trane TDE060A936K2 Gas Furnace will provide heat for a few minutes and then gives me 4 flashes on the diagnotic panel which means it has a "open high limit device". I see that the limit switch … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Air Ease brand forced air upflow furnace. It started
I have a Air Ease brand forced air upflow furnace. It started short cycling on and of, when the burner is running, and even after the burner has shut off. I replace the Limit switch with a Honeywell L… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Trane Gas XE60. My pilot lights, but the furnace doesnt fire.
Trane Gas XE60. My pilot lights, but the furnace doesn't fire. None of the breakers are tripped. The fan blows when turned on. Any suggestions?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Tappan gas furnace model GUF105D30E5 blower fan wont turn
Tappan gas furnace model GUF105D30E5 blower fan won't turn off not even when temperature setting has been achieved. Thermostat fan setting is on auto. Any place I can find users manual, schematics?… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x