Hi need support with vitogas 050. System stoped working. 8 apartment unit. I think pilot is off. Don't know how to restart.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Every apartment has own thermostat. 8 units. Did not check units filters.

Contractor's Assistant: Do you plan on doing the work yourself?

Looks like pilot is off

Contractor's Assistant: Anything else we should know to help you best?

Need to spark pilot but don't know how

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 minutes by:
1/4/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the manual on that unit is out of print.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside one of the burner or blower access panels, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a carrier infinity model 58CVA090 that seems to be
hi! i have a carrier infinity model 58CVA090 that seems to be only blowing cold air, wondering if pilot light out since i just changed filters and my thermostat reset how can i tell if my pilot light … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
My furnace unit is blowing cold air. I tuned off the unit
My furnace unit is blowing cold air. I tuned off the unit and checked all connections and restarted unit. The pilot light turned on and the unit ignited, it only stayed on for a few minutes and then t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a standing pilot unit heater (75000 btu) I replaced
I replaced the pilot/thermocouple assembly this year. the unit lights just fine, but once it goes through a cycle and the main gas valve shuts off, the pilot also goes out. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
I have a new ductless system. One unit turns on the vent at
I have a new ductless system. One unit turns on the vent at the bottom opens and then it closes and turns off. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
I have a raypak propane pool heater and it says main
i have a raypak propane pool heater and it says main ignition failure … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a Viessman Atola, and it has stopped making heat.
I have a Viessman Atola, and it has stopped making heat. This happened about 2 months ago, and I fixed it but I cannot remember exactly how. When i remove the front panel, there is a black clicker but… read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
I've got a Carrier 17C natural gas furnace. We just replaced
I've got a Carrier 17C natural gas furnace. We just replaced the blower motor, and now the furnace won't heat the building. The inducer motor comes on, pilot fires, but no main burner. It fired up cor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a rheem criterion gas furnace tht won't heat. The
I have a rheem criterion gas furnace tht won't heat. The light is on and it tries a few times to sustain the 3 jets and then cuts out. Is there something I can do, to get it working? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Lennox G20Q5/6E runs fine until a warm day or thermostat
My Lennox G20Q5/6E runs fine until a warm day or thermostat change causes the furnace to be off for over an hour. It will not restart on its own. If I heat the pilot sensor with a flame it will restar… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Seems as though our fireplace is on lockdown or something.
Seems as though our fireplace is on lockdown or something. Green light blinks every 2 seconds. The only solution in the brochure is to shut off the master switch, which I have done a million times. Fi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello I have a Viessman Vitogas 050 Atola ECD series gas burner,
Hello I have a Viessman Vitogas 050 Atola ECD series gas burner, made in 2004. No problems except the pilot light has gone out. not clear how to restart it. any suggestions? should I leave this to a p… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I Have a hvac system at a vacation house in the desert,sears
I Have a hvac system at a vacation house in the desert,sears modelNNN-NN-NNNN the heater takes several trys to come on, I have opened up and cleaned everything and notice the auto ingniter allways wor… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Heelo, We have a Viessmann Vitogas 050 furnace for our hot
Hello, We have a Viessmann Vitogas 050 furnace for our hot water and forced hot air (fuled with propane). A technician was in today checking it in preparation for the winter and said it acted as expec… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Have a Rite boiler built in 1970 with fire eye boiler control
Have a Rite boiler built in 1970 with fire eye boiler control that controls the boiler first stage uses flame rectification and second stage is controlled by baso unit with thermocouple. I dont think … read more
Problem solver
Problem solver
Hvac technician
Vocational, Technical or Trade Scho
33 satisfied customers
I have power and gas to my trane xe 78. It wont come. It has
I have power and gas to my trane xe 78. It won't come. It has a red light flashing in the view window on the access panel. I have followed the shut down and restart and got nothing.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
We have a forced-air electrical heating unit for our house
We have a forced-air electrical heating unit for our house but all of sudden, it's cold, the air coming through the vents is cold, even when we turn up the thermostat.IT's a Tempstar furnace. When I t… read more
ComfortZone
ComfortZone
Associate Degree
515 satisfied customers
I have a Heil DC90 unit that seems the ignition module or smart
I have a Heil DC90 unit that seems the ignition module or smart valve is not working No pilot light Turned power off everywhere and then turned back on. No clicking, does not seem like I have gas flow… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
My 1988 Payne mid-efficiency furnace continues to have the
My 1988 Payne mid-efficiency furnace continues to have the gas cycle off. It starts okay but the gas keeps cycling off and on (or low and high) until the furnace eventually shuts down. Evrything works… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.