I have an American Standard Freedom 80 gas furnace. The

Customer Question
Hello, I have an...

Hello, I have an American Standard Freedom 80 gas furnace. The flame sensor appears to be off – I replaced it last year. Now, the unit runs normally (both in heating mode and waiting mode), however, the gas will shut off after about 15 minutes. The blower continues to run. Thinking I need to swap out the sensor again

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filters are good. I kicked up the thermostat to 85, stopping prior to reaching 70.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

No, that is it

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 15 minutes by:
1/3/2018
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified

Usually if flame sensor it will shut off in a matter of seconds sounds more like a limit switch or pressure switch issue.Can you look inside the burner compartment on label on side panel and get me the model on your furnace? Then look in blower compartment and see if there is an error light blinking that will guide us in determining what is failing with the furnace.)Not if no peep hole and you have to remove blower panel to see control board, it will be necessary to hold door switch in to have power to board)

Ask Your Own HVAC Question
Customer reply replied 6 months ago
American Standard Freedom 80, Model = AUD080R936A1
SN = J40506970
category = ISituation: All four burners light properly, immediately, using the hot surface pilot once an ignition signal is received from the thermostat. Run time varies between 15 minutes to hours, no consistent failure time. When the system shuts off, all four burners stop at once. The lower unit flashes an error code 2 - System Lockout (retries or Recycles exceeded) after three ignition attempts. At each ignition attempt, the hot surface pilot glows, however, gas is not coming out of the jets. I cleaned the flame sensor and tested the limit switch with a volt meter while the blower was running (no gas/heat present). No voltage read when attached to limit switch leads. Filter is brand new. Blower volume at the vents appears normal.
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

I am thinking board is failing. If a limit or anything was opening we should get a different error before the actual lockout.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
AMERICAN STANDARD FURNACE FREEDOM 80 SOMETIMES IT LITES AND
AMERICAN STANDARD FURNACE FREEDOM 80 SOMETIMES IT LITES AND OTHER TIMES IT DOESNT AND THE FAN KEEPS BLOWING COLD AIR I SHUT IT OFF AND RESET IT THE IGNITER GLOWS AND THE GAS VLVE CLICKS BUT NO FIRE UN… read more
airheatman
airheatman
HVAC Technician
9,213 satisfied customers
American Standard freedom 80, trying to troubleshoot the
Hi, American Standard freedom 80, trying to troubleshoot the blower. The high limit switch shuts the sustem … read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
I have an American standard Freedom 90 furnace. Over the
I have an American standard Freedom 90 furnace. Over the last day or so it has quit running it is trying to start up and the green light is blinking but then it stops trying to start and the red light… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a American a standard freedom 80 reflecting a high
I have a American a standard freedom 80 reflecting a high open device limit. Clean filter. Burners glowing. Don't hear Blower kick in. Is the limit stopping motor or is blower likely shot? Saw info ab… read more
Expert
Expert
Greetings. American standard freedom 80, just replaced filter,
Greetings. American standard freedom 80, just replaced filter, single red light blinking, no heat. Ideas?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Have a American Standard Freedom 80 2 stage furnace-5 years
Have a American Standard Freedom 80 2 stage furnace-5 years old. The furnace will ignite and get up to temperature, then shut off. However, after awhile the furnace starts to make loud clicking sounds… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Hi - I have an American Standard Freedom 78 gas furnace. The
Hi - I have an American Standard Freedom 78 gas furnace. The furnace starts up and you can hear the click to call for heat and the inducer motor is running. Burners do not come on and the blower does … read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
I have a 1997 American standard freedom 90. Lost gas while
I have a 1997 American standard freedom 90. Lost gas while operating. I read the manual and it indicated to shut of an off and on before 30 seconds due to a lock out. The ignitght lights, however, no … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a American Standard Freedom 80 furnace installed 8 years
I have a American Standard Freedom 80 furnace installed 8 years ago and sometimes it doesn't kick in to heat the house. I have had to go down shut the main power off...give it a minute and turn it bac… read more
airheatman
airheatman
HVAC Technician
9,213 satisfied customers
I have an American Standard Freedom 80 thats about 25 years
I have an American Standard Freedom 80 that's about 25 years old. We purchased our house recently and I just changed the filter. It looked like it hadn't been changed in ages. After changing the filte… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have an American Standard, Freedom 80 furnace built in 7/95.
I have an American Standard, Freedom 80 furnace built in 7/95. I recently cleaned the flame sensor and that fixed my ignition problem but now when the gas turns off the blower will not shut off. If I … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have an American Standard Freedom 90 gas Furnace. Ignitor
I have an American Standard Freedom 90 gas Furnace. Ignitor starts up (flames up) then shuts down when the main blower starts up. Code flashes 9 times , it says check ignitor. The ignitor seems to fla… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
American Standard Freedom 95 Single Stage Furnace problem.
American Standard Freedom 95 Single Stage Furnace problem. Red light is on, on the bottom of the unit. Something is kicking on but no blower to be had. The gas is on. I open the unit and I don't see a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have an American Standard Freedom 90 I cant find a model
I have an American Standard Freedom 90 I can't find a model number are serial number. It is 11 years old. The burner lights but Blower does not come on. I can jumper the blower and it works. Can the f… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
My American Standard furnace wont fire up. The control unit
My American Standard furnace won't fire up. The control unit LED stays on constantly and according to the labeling, it means the control is bad and needs replaced. It will cost 300 to do that. Could i… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a American Standard Freedom 80 furnace, that has a
I have a American Standard "Freedom 80" furnace, that has a White-Rodgers control unit, model No. 50A50-473. The furnace "short cycles" during the heating cycle. The burners will light for appr. 30 se… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I have a Freedom 90 American Standard propane gas furnace.
I have a Freedom 90 American Standard propane gas furnace. Lately, it fires up and then within seconds it will shut down after igniting. It will retry and sometimes ignite and run and other times it w… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
We have a American Standard Freedom 80 gas furance about 5
We have a American Standard Freedom 80 gas furance about 5 years old. This morming it would not go on. How can I check the pilot and/or restart or relite the pilot?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x