HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

Are you? I recently just worked on a furnace (goodman) The…

Customer Question
Hey how are you...

Hey how are you? I recently just worked on a furnace (goodman) The furnace will fire up to the point flame and fans come on. After about 15 minutes it cuts off .

Contractor's Assistant: Did you check the furnace's filters?

The light on unit blinks 4 times inddicating Open limit switch according to literture on cover plate. My question is what could be the problem. sensor that pick up flames

Contractor's Assistant: Do you plan on doing the work yourself?

Model GMT090-5 serial #(###) ###-####

Contractor's Assistant: Anything else we should know to help you best?

Thats pretty much it

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
1/3/2018
HVAC Technician: airheatman, HVAC Technician replied 7 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
Experience: Furnace, A/C and heat pump specialist.
Verified

It is not the flame sensor if it runs for 15 minutes.Either filter is dirty, ac coil on top is dirty, limit is weak .

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a furnace Model G9T10014UPC13B. controller is a
I have a Coleman furnace Model G9T10014UPC13B. controller is a White Rodgers 50A50-241. Furnace seems to run constantly and barely keeps house comfortable although it's not that cold out. Elect bill l… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
ok originally my goodman furnace model # ***** Gas
ok originally my goodman furnace model # ***** Gas Fired kept tripping off on the roll out switch top left side only. so when I removed the top cover it would stay running. I get 6 flashes stating blo… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
Hi Can you help with a Goodman Gas furnace? Wont stay
Hi Can you help with a Goodman Gas furnace? Won't stay lit and have clean the sensor and changed the limit l200f-30. 4 flashing red blinks… read more
type2technician
type2technician
253 satisfied customers
I have a code 33 and 13 going back and forth on my furnace.
I have a code 33 and 13 going back and forth on my furnace. I found leaves in the intake and the rollout flame switch won't reset, what resets it?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a goodman gms9/gcs9 gas fired warm furnace. I have three
I have a goodman gms9/gcs9 gas fired warm furnace. I have three zones and when the one zone is on the light blinks four times and the fire lights up and then goes out repeatedly. What is the problem ?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My furnace shuts down when it very cold for long periods of
My furnace shuts down when it very cold for long periods of time -- and clearly there is also correlation to windy days as well (I didn't believe it at first -- but there is. I'm renting the place, fi… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
Getting 4 blinks with original 50A55-288 control board. Checked
Getting 4 blinks with original 50A55-288 control board. Checked wiring by shorting and with meter. Wiring is fine and none of the switches have tripped. Do I need a new board?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Reference RA80+: I am getting a single flashing LED per unit
Reference RA80+: I am getting a single flashing LED per unit of time indicating an open limit on the over temperatue switch of the flame roll out switch. I am stuck on how to fix it; and don't you kno… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman furnace model GMT090-4a. The furnace operates
I have a Goodman furnace model GMT090-4a. The furnace operates but sometimes the gas turns on and the ignitor ignites the gas for a few seconds then it stops. This happens 3 or four times then it shut… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a goodman model gds81155cna, the first time it went
I have a goodman model gds81155cna, the first time it went out I cleaned the flame detector, it worked ok, next it flashed 4 times, limit open, replaced both limits, still had a problem, replaced gas … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i have a goodman gmt070-3 funance tries to start 3 times then
i have a goodman gmt070-3 funance tries to start 3 times then shuts off. i have replaced the flame sensor and the monitor light blinks once. options are gas flow gas pressure gas valve flame sensor i … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a goodman GMPN080-4 Rev B Furnace. It will start up
I have a goodman GMPN080-4 Rev B Furnace. It will start up & run for approximately 15 minutes and then it shuts off. The light on the circuit board blinks once. I took out the flame sensor & lightly s… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a goodman gmt070-3b. the furnace burners turn off after
I have a goodman gmt070-3b. the furnace burners turn off after about 4 minutes, then the furnace sorta reboots. The red light blinks four times and furnace burner lights again after the proper start u… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
goodman GMT090-4A furnace flame shutting down after 3 min or
goodman GMT090-4A furnace flame shutting down after 3 min or so then starts all over again not heating the house over 69 degrees… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Coleman Evcon comes on for about 3-5 minutes and then goes
My Coleman Evcon comes on for about 3-5 minutes and then goes right back off, can trip thermostat and comes back on and does same, am freezing… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a rheem 90+ furnace that i installed eight years
I have a rheem "90+ " furnace that i installed eight years ago! I ran out of LP gas this week in the middle of the night! The burners went out but the blower never cut off! when I tried to cut off the… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why is my furnace running but no heat is coming from it?
My heater is running, but no heat is coming out, just cold air. It is not igniting, the the fan will not turn off, even when you turn the thermostat off. I had to use my emergency switch on the wall t… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
blinking light 1.indicates flame sensor .replaced flame sensor
blinking light 1.indicates flame sensor .replaced flame sensor still furnace will light and shut off.cycles 3 times and same code .furnace is a gmt090-3 checked all wire connections all seem ok . plea… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.