I have a Pensotti blue line boiler. Recently it stopped

Customer Question
I have a Pensotti...

I have a Pensotti blue line boiler. Recently it stopped working. Troubleshooting the problem I found a open between terminals 6 and 7 on the terminal block in the oval control box located top front of the boiler. The wiring diagram shows LS1 and LS2. One of these switches is not operating right. Where are these switches located ( the wiring goes though a cable into the covered boiler area) and were can I get replacements?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

3 days. I placed a jumper across terminals 6 and 7 to get the boiler operating under manual control to keep the house from freezing.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 58 minutes by:
1/2/2018
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, LS1 and LS2 are safety limit switches. You have to follow the wires to locate them. These are most likely just tripped and not bad,, they will have red reset button on them if thats the case.

.

I am 77 years old with 58 years in the boiler business, Pensotti is not a common brand. Be patient and I will see if I can find a manual on it. Do you have a model number to go with that brand name

click here for the manual I have so far, tell me if this is it or not please

.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago

Click here for the manual, see diagram on page 19, figure 8 and jumper terminals 6 and 7 as a brief test only, to see if either of those are tripped

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I jumpered terminals 6 and 7 to get it running. The manual you referenced is the manual I have. After I left the jumper on for 4 hours to get the boiler temp back up to 190 degrees the switches closed. The boiler temperature was down around 40 degrees before I finished troubleshooting and put the jumper on. The boiler now started working properly but I wanted to replace the switches to stop it from happening again. With this cold temp the house nearly froze up before I got to the problem. I hate to have it happen again when we may be out.
Customer reply replied 8 months ago
The model number is *****
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago

Hello. high limit thermostat source click here please, but do call them on the phone to confirm for you boiler or not, thats a UK source

I will see if parts are available in the US for you as well

.

Click here for Pensotti dealers in the US and Canada... they are a bit sparce, it will take a while calling these people to source that part

.

Its time to rate my work for the day, locate the "finish and rate your expert" link near the top of the page, that also gets me paid. We can go from there tomorrow with whatever help you might need.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
9,880 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,880 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a teledyne laars mini therm 2 jvs 160 model boiler. I
I have a teledyne laars mini therm 2 jvs 160 model boiler. I have a boiler start up issue. First it will only start up when I kill the main power and turn the power back on. Then all for heat happens,… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am trying to connect a RTH9580WF to the air handler in my
I am trying to connect a RTH9580WF to the air handler in my Condo. I have the wire diagram for the current stat. Can I send you the diagram and you tell me the correct connections?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
After nearly having my home destroyed by inept plumbers and
Good afternoon, After nearly having my home destroyed by inept plumbers and bad hydrostat controls and a second set of controls and chinese gauges that are also being sent back to the retailer I am re… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Will a Honeywell RTH7600, RET97 Series be used to replace a
will a Honeywell RTH7600, RET97 Series be used to replace a old two mercury switch t'stat The older t'stat controls heat and air condition using a "heat pump" there is a 6 wire cable connecting the "t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi Rick my name is XXXXX XXXXX you have helped many people
Hi Rick my name is XXXXX XXXXX you have helped many people and hope you can help me---I have a Slant Fin Galaxy Boiler Model GG-100 HEP with a Honeywell L8148E Aquastat and a D896 vent Damper with a S… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a teledyne-laars residential gas-fired mini-therm jv
I have a teledyne-laars residential gas-fired mini-therm jv hydronic boiler, model JVS100NDI, rated at 72,200 BTU/hr. I press the red reset button, and the furnace fires up. The furnace operates as ex… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I still seem to have a problem with our Munchkin T50M high
I still seem to have a problem with our Munchkin T50M high energy boiler system. It's a "Vision 1" system by Heat Transfer Products, Inc. of East Freetown MA. An error code sometime appears showing "P… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
Laars Minitherm JVS no burner and can't measure voltage
I have a Laars Minitherm JVS. I have a pilot but no burner when the t-stats call for heat. It appears, the cut off circuit (flame roll-out, blocked vent, hi-limit) has continuity but I am not able to … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
warmflow oil combi 90 he,fitted new control box ,new motor,condensate
warmflow oil combi 90 he,fitted new control box ,new motor,condensate ok,light wont go off on controlbox after pressing. still wont fire .any ideas.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,880 satisfied customers
I HAVE A WORCESTER COMBI BOILER THAT AS WIRED IN A DANFOSS
I HAVE A WORCESTER COMBI BOILER THAT AS WIRED IN A DANFOSS TS 751-SI TIME UNIT ON MY CENTRAL HEATING SYSTEM, TH TIMER UNIT HAS STOPPED WORKING. I HAVE ORDERED ANOTHER UNIT BUT CAN I BYPASS THE TIMER U… read more
SparePartspro
SparePartspro
Business Owner
Vocational, Technical or Trade Scho
26 satisfied customers
I have a Lennox (1992 ish) G20Q3E-75-4 whisper heat furnace
I have a Lennox (1992 ish) G20Q3E-75-4 whisper heat furnace The fan motor was successfully replaced last year and 2 years ago the ignitor was replaced. There were no problems until I turned the furnac… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
How do I replace an old Lennox (Honeywell) round dial w/mercury
How do I replace an old Lennox (Honeywell) round dial w/mercury switch thermostat to a Honeywell Series 2000 Commercial digital thermostat?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am experiencing problems wireing a Honeywell Pro TH3000 /
I am experiencing problems wireing a Honeywell Pro TH3000 / TH321OD1004 it is a 2H/1C heat pump system. I am using a 18/22 low voltage 6 wire cable. White yellow green red brown blue I am using a jump… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Baxi Solo 3 PFL installed in my home. The pump runs
I have a Baxi Solo 3 PFL installed in my home. The pump 'runs' continually, even when the controller (Siemens RWB9) is in the 'off' mode. The terminal block in the bottom of the boiler casing, has 7-N… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
installed 110v motorized honeywell zone valve replacing older
installed 110v motorized honeywell zone valve replacing older non motorized unit that was not working honeywell 845a had hot lead (4) on panel supplying 110 volts to parker soldenoid which i used that… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
GWA gas-fired boiler not firing. I have a lit pilot and have
GWA gas-fired boiler not firing. I have a lit pilot and have checked all connections. I believe there is no fault (open connection) to the thermostat but I am not sure how I can tell if the thermostat… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
How to wire Beckett oil burner to weil mclain wgo series 3
How to wire Beckett oil burner to weil mclain wgo series 3 boiler and zone valves? have 2 wires going to boiler, do you use jumper from boiler panel to burner? seems that this might activate burner ea… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
hi, i have a glow worm space saver 50 mk 2 boiler pilot light
hi, i have a glow worm space saver 50 mk 2 boiler pilot light is on but is not firing up have changed thermo couple but still the same thermostats are clicking on and off any suggestions?… read more
alex hewitt
alex hewitt
Vocational, Technical or Trade Scho
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x