furnace is working but dont seem to be putting out alot of heat. the flame is blue but sems to be rolling in the sealed cmbustion chamber. could it be a bad air exchanger??
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
1/2/2018
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,528
Experience: Furnace, A/C and heat pump specialist.
Verified

Absolutely. Turn furnace off. Allow blower to stop. Then turn furnace back on and watch flame.If flame changes characteristic when blower comes on the heat exchanger is cracked or has a hole.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok I just did that. The flame came on and they were burning like the should be. Then after about 30 seconds the flame was all around each burner and even underneath them. This happened before the blower kicked in???
Customer reply replied 8 months ago
I have checked the intake & exhaust. No obstructions!
Customer reply replied 8 months ago
After the blower came on the flames are still kinda all around the burners. One burner has a little yellow in the flame!
Customer reply replied 8 months ago
You still here??
Customer reply replied 8 months ago
This furnace does have a sealed combustion chamber
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Heat exchanger is the culprit

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Household air should never blend with the combustion chamber.The fact that flames changes indicates we have household air entering the chamber

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Is it possible to get one & replace it??
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Not usually worth replacing.You can buy a furnace for the price of the exchanger

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,528
9,528 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnace keeps tripping that little breaker next to the
My furnace keeps tripping that little breaker next to the burners in between the 2 little prongs. Then my thermostat shuts off and then my blower keeps running blower cold air until I push the little … read more
airheatman
airheatman
HVAC Technician
6 years college
9,528 satisfied customers
I'm having an issue with my furnace. Weathermaker 9200 Model
Hi, I'm having an issue with my furnace. Weathermaker 9200 Model 58MXA080-12 What would cause a flame rollout switch to keep tripping? I've gotten error 33 twice tonight, each time I reset the flame r… read more
airheatman
airheatman
HVAC Technician
6 years college
9,528 satisfied customers
I'm ***** ***** , I have an older Carrier unit model
I have an older Carrier unit model 48GS###-##-#### ***** unit stoped working yesterday. On examination it was ddetermined that the iDM fan motor and fan stoped working. we replaced the fan and motor assembly also checked out the roll out switch that the fault code was showing. We reassembled the unit and restarted it. On turning on thr unit immidiatly fired on. The flame was nice and blue. t seemd to working properly. Within aa minute or so flame roll out occurs. The roll out switch immidiately shuts the unit down. What could be the causs for the flame roll out. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,528 satisfied customers
I have a Bryant plus 90 that was built in 1998. Last night
I have a Bryant plus 90 that was built in 1998. Last night I noticed that the blower motor was going and it seemed cold. Checked t-stat. Was at 67. Normally set for 72 degrees. Turned off power to fur… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
propane furnace smells like plastic thru ducts when
propane furnace smells like burnt plastic thru ducts when propane is being used smell is not in the actual room where furnace is located, only thru ducts when propane is being used and air is blowing … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Goodman GMNT 100-4b Natural Gas Furnace. The problem
I have a Goodman GMNT 100-4b Natural Gas Furnace. The problem is one of the burners has slight flame roll-out because the flame can not enter its tube of the heat exchanger.It is like there is no draf… read more
heatncoolrepair
heatncoolrepair
Former HVAC Service Technician
Vocational, Technical or Trade Scho
75 satisfied customers
I have a Model 600 sears wall furnace cira 1970(NNN) NNN-NNNN65000
I have a Model 600 sears wall furnace cira 1970(NNN) NNN-NNNN65000 input BTU,has worked great in my camp, last couple times I used it noticed the subsequent time it recycled I noticed fire what I call… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have an 80,000 btu rheem outdoor ac/ heat combo unit, model
I have an 80,000 btu rheem outdoor ac/ heat combo unit, model rrka-a024jk08e. when I turn on the thermostat, the blower starts working and the furnace seems to fire up, then after 5- 10 seconds it shu… read more
airheatman
airheatman
HVAC Technician
6 years college
9,528 satisfied customers
Hi, I have a Heil 7000 propane furnace that was installed in
Hi, I have a Heil 7000 propane furnace that was installed in 1993. The blower runs constantly even when the thermostat is off. It also will not ignight unless the roll out switch reset switch is held … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Tempstar DC 90 furnace. The limit switch on the side
I have a Tempstar DC 90 furnace. The limit switch on the side of the combustion chamber trips frequently. I reset it, the furnace fires, but within an hour it trips again. I thought it was the switch … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am working on a 90% heil gas furnace converted to lp. I have
I am working on a 90% heil gas furnace converted to lp. I have rollout on one of the burners but the flame is not affected by the blower motor running. The flame rises to the top of the combustion cha… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Thermo Pride furnace. When the thermostate calls for
I have a Thermo Pride furnace. When the thermostate calls for heat, only the exhaust fan goes on. Once in a while the furnace works okay. Woke up to 55 degrees in house. when I press the Roll out swit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my trane xe80 has been burning roll out sencers all day,
my trane xe80 has been burning roll out sencers all day, have the chemine clean but after a few minites the burner is out and the senser is bour out please help?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I HAVE A 13 TO 15 YEAR OLD RHEEM HEATING AN AIR CENTRAL UNIT
I HAVE A 13 TO 15 YEAR OLD RHEEM HEATING AN AIR CENTRAL UNIT THE HEAT STOP WORKING I START SMELLING A BURNING SMELL, AFTER CHECKING THE FURNACE OUT UNDER THE HOUSE THE CONTROLBOARD WAS BURNED A LITTLE… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, I just moved into a foreclosed house and have a Payne
Hello, I just moved into a foreclosed house and have a Payne furnace that's about 10 years old. I had gas put in the propane tank outside and the technician ran a check on the furnace and was running … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Rheem RGDJ 10EBRJR furnace, it appears to be working
I have a Rheem RGDJ 10EBRJR furnace, it appears to be working properly, comes on when heat is called for, bright blue flames in chamber, fan is on and moving air. The air at the registers is coll, not… read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
Carrier high-efficiency condensing furnace model 58SXA060-GG
Carrier high-efficiency condensing furnace model 58SXA060-GG: The fuse-link in the pilot flame sensing circuit has blown twice. The main burner goes on and off several times during first minute of ope… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
I had a unit that appeared to have a bad roll out switch.
I had a unit that appeared to have a bad roll out switch. I changed it, it ran for 1 day and is out again. How can I check to see how much air the inducer motor should be moving?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x