Sure. I have a Goodman gas-fired furnace installed around…

Customer Question
Sure. I have a...

Sure. I have a Goodman gas-fired furnace installed around 2005. Not working. When last checked, there were three red flashes indicating pressure switch circuit not closed. Changed thermostat batteries and reset to factory defaults. Shut off/turned on power at the breaker box and turned off the gas furnace emergency switch. Couldn't find any other reset buttons. Now nothing. No heat and no blower.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostat is a Rite Temp 8050. Screen indicated "filter". Filter has been changed. Thermostat reset with batteries. No messages.

Contractor's Assistant: Do you plan on doing the work yourself?

No idea. At this point there are no HVAC techs available in the area given the cold snap in Boston.

Contractor's Assistant: Anything else we should know to help you best?

Don't know what questions to ask or how this works. Just came across this as I tried troubleshooting.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 6 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Answered in 10 minutes by:
1/2/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,702
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the pressure switch is a 4" round disc type thing, with two wires attached and one or two 1/4" black rubber hoses attached... the hoses fill with condensate and the pressure switch stops working. also the nipples where the hoses connect get clogged with dirt.

.

To access the pressure switch remove the front panel of the furnace where the gas valve and burners are.

.

Remove hoses, cut off any split ends, and poke a paper clip wire in the nozzles about 1/2" to clean out the tiny orifice inside. That will solve the problem in 90% of cases.

.

We can go from there without any time limits.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Any images of this 4" disc for reference?
Customer reply replied 6 months ago
Any images of this 4" disc for reference? And is there anything else to troubleshoot or are we settling on the pressure switch thing only?
Customer reply replied 6 months ago
What tools do I need to have handy? And would it make sense to see a picture of the furnace set-up?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

You may need a multi meter and screw driver set.

.

click here for pressure switch photo's

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I don't own a multi-meter. Would it make more sense for me to get one before proceeding with a call or any next steps?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

You do not need a multi meter to service the pressure switch, but a meter is never a bad idea, you can get a good enough one for $30 or so.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
The pics were helpful. But the only thing that I see is about 2" and has a red and yellow wire attached but no hoses.
Customer reply replied 6 months ago
Right now the power to the furnace is off while working on it. But when there was power, there was nothing blowing even after changing the batteries in the thermostat and switching it to 'on' instead of 'auto'. Is it possible that the pressure switch circuit is closed and there is a short The Goodman owner's manual indicates replacing the induced draft blower pressure switch for this. I assume that's a different switch. Should I be looking at that as a possibility?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

The industry training course on these for established journey plumbers is 2 weeks, for novices the college course is 2 years.

.

I am able guide you quickly and effortlessly to a compete diagnosis in minutes, but if we spend time with me explaining the manual it will take hours or days..... we can do that if you wish.

.

Or you can

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

I will point the pressure switch out to you on the diagram, and give you full instructions on how to diagnose the problem

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Last photo: ***** ***** too large (> 5 MB) and trying to find way to send it.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks the 2 inch black round device to the lower left of your furnace photo with the red and yellow wire attached is the pressure switch.

.

Remove its rubber tube and blow it out, then poke a paper clip wire 1/2" into the nipple it came off of to clean the tiny orifice inside.

Try the furnace again, if that fails, restart the furnace again within 2 to 5 seconds of the inducer fan starting remove the red and yellow wires and jam them together, the furnace igniter should glow within 30 to 60 seconds.

Tell me if it does or no, we can go from there

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Removed the black hose connecting switch. Blew it out. It was clear. Used the clip on both connecting ends.Tube has been replaced. Back to basement to turn power on.
Customer reply replied 6 months ago
Flipped the breaker and there's power to the unit. Gas emergency switch is in 'on' position. (Is there another reset switch I should use?). Thermostat is set to 'auto' and 75 and current temp inside is 69. I hear and see nothing.
Customer reply replied 6 months ago
The inducer fan hasn't started at all.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Ask Your Own HVAC Question
Customer reply replied 6 months ago
OK. Earlier you noted, "Try the furnace again, if that fails, restart the furnace again within 2 to 5 seconds of the inducer fan starting remove the red and yellow wires and jam them together, the furnace igniter should glow within 30 to 60 seconds." But in this case, there has been no fan. Do the screencasts you provided still apply?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

https://www.screencast.com/t/1yWJUgE3z

We are trouble shooting, every single step of trouble shooting fails and is no longer active, until we get to the final step.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
Experience: Furnace, A/C and heat pump specialist.
Verified

My name is ***** ***** be happy to assist you.

First of all in the inducer does not start nothing else is going to happen.

Lets do this. Turn power off. Make a jumper from R to W on board where thermostat wires connect.Then power back on and tell me how far in sequence furnace goes.

Inducer,igniter, burners, maun fan

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
9,181 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,702 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have an emerson 1f97 controller for our furnance / air
we have an emerson 1f97 controller for our furnance / air conditioner. the batteries went bad..I replaced them. The unit appears to operate...except that it display 10F rather than the true temperatur… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What would cause my heat to come on blowing warm air and
What would cause my heat to come on blowing warm air and then start blowing cold air. It is a Goodman was gas controlling heat. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a thermostat with theoretically a 2 degree range but
I have a thermostat with theoretically a 2 degree range but my furnace often won't start until the temp falls 5 degrees lower than the thermostat setting. that is thermostat set to 70 but furnace does… read more
Phil
Phil
Mechanical Engineer
9,702 satisfied customers
Billy. I came across and am having a similar problem
Hi Billy. I came across http://www.justanswer.com/hvac/2hddw-troubleshoot-control-board-302075-302-carrier-heating.html and am having a similar problem with my Carrier furnace that uses this same cont… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a hunter 44905 thermostat and I'm getting an error message
I have a hunter 44905 thermostat and I'm getting an error message of check HVAC.. The AC was working and then just quit. I have replaced the batteries in the unit and reset it to factory default. Any … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I changed the batteries in my Goodman thermostat the display
I changed the batteries in my Goodman thermostat the display still says 85 is the room temperature. When I switch to heat the furnace doesn't kick on and the display doesn't show what he heat is on. I… read more
Phil
Phil
Mechanical Engineer
9,702 satisfied customers
I HAVE A WHITE RODGERS 1F78 5/2 DAY PROGRAMABLEThermostat
I HAVE A WHITE RODGERS 1F78 5/2 DAY PROGRAMABLEThermostat worked one day the next it would not show a temperature but shows the same time constantly. It will not let me program time. The time is the o… read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
Hello: my white-rogers panel shows a low battery sign on
Hello: my white-rogers panel shows a 'low battery' sign on the panel. I took off the cover, changed the batteries, but the 'low battery' message is still there and I cannot get the panel to work to tu… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My thermostat has been blinking what looks like a battery sign,
My thermostat has been blinking what looks like a battery sign, and it says "filter" underneath. I changed filter but blinking continues, and now furnace will not go on. Is there a battery I should be… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a VT3000 thermostat and need to know how to turn off
I have a VT3000 thermostat and need to know how to turn off the "call for service message" and the report message. Thanks… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Have a gas fed HVAC system. Two days ago, the system would
Have a gas fed HVAC system. Two days ago, the system would not turn on (even while the thermostat shows the "flame" for the unit to kick the heat on). Went and checked the breaker, and nothing tripped… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My Tstat came up with an error message. I changed the batteries
My Tstat came up with an error message. I changed the batteries and it seems to have recovered but the heating unit is not coming on. It is a gas fired unit and when I took off the door there appeared… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a gibson hvac unit and the heat will not turn on. My
I have a gibson hvac unit and the heat will not turn on. My thermostat clicks to send the heat message to tge unit but the gas does not turn on. The fan continuall runs however. The red light on the e… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
furnace went out because filter was clogged. Changed filter,
furnace went out because filter was clogged. Changed filter, turned furnace off and back on at the electrical box to reset. Now what do I do to get furnace to work. Goodman Gas Pack… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a 1F80-51 thermostat. new batteries, and cleaned away
I have a 1F80-51 thermostat. new batteries, and cleaned away the dust. the display reads a higher temp then the actual temperature of the house. It reads 77 degrees, and it must be in the low 60's her… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My Honeywell thermostat RTH 230B displayed on the digital screen
My Honeywell thermostat RTH 230B displayed on the digital screen today the word "Filter"--I have a gas furnace and hot water baseboard heat--no HVAC. I purchased the house about 6 months ago and bough… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Have a Ruud UPRL 060JEZ Heat pump and a UGFD 10EZCMS gas furnace
Have a Ruud UPRL 060JEZ Heat pump and a UGFD 10EZCMS gas furnace (on propane) with a UHC-TST411MDMS Thermostat (w/outside temp sensor). Live in southwest Iowa with cold temps. What setting (on Thermos… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I just installed a Goodman GHM95 my Questions are on the control
I just installed a Goodman GHM95 my Questions are on the control board were do the dipswiches position go for best all around performance. My field is automotive and how important is factory set blowe… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x