Customer Question
Have a Intertherm M7RL 072A...
Have a Intertherm M7RL 072A BW. The question is when there is a call for heat the Blower motor will run every once in a while for a minute or 2 then run the normal heat cycle. Any ideas, already swapped out thermostats.
Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
1/2/2018
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
Experience: Furnace, A/C and heat pump specialist.
Verified

Are you saying main lower comes on before the ignition process begins?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
not Everytime though. Just every once in awhile according to the homeowner. I haven't witnessed it yet.
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

If blower is starting before the inducer ,igniter or burners, You have a board that is starting to fail.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Okay, any thoughts on I just noticed alot of there Registers are closed.
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

You can close up to 30 per cent of registers without causing adverse effects but if too many are closed we would get an overtemp limit error.That would not cause blower to come on before ignition

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

These boards as you probably know develop stress cracks and will start giving erratic operation .It will continually get worse unitl eventually fails all together if that is the case.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Just wondering because unit is only 4 months old
Customer reply replied 6 months ago
After new board still produces the same problem.
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Let me grab a manual and see if there could be anything telling fan to come on. Meanwhile lets do this.

Disconnect the thermostat wires from the board. Then jumper R to W and see if that blower comes on first or just the normal sequence beginning with inducer.

Also tell me the model on the thermostat you are using

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I'm not there anymore, it was cycling just fine when I was there. But homeowner says it still cycling like that. But it never does it in front of me. There is a little prong connector on the board that has different positions, but nothing in the manual about it
Customer reply replied 6 months ago
I was using a Honeywell 6000 but now using a Honeywell T4 Pro
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Do you know what thermostat is installed. As I think it over the though comes to me that perhaps if the thermostat has a setting for "Fan controlled by thermostat or Fan controlled by furnace". if that setting was on electric, it could e confusing the board

Ask Your Own HVAC Question
Customer reply replied 6 months ago
No it was left on 2
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

I would try changing that to 1.

I am looking now to see what those pins do.I think they control how longer blower stays on after burners shut down

Ask Your Own HVAC Question
Customer reply replied 6 months ago
No there is a whole different pin section for blower off delay for heat
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

I am still looking through manuals. I do see that those pins are in the "speed select" block on board so probably a way to chose how many cfms fan moves so they can be adjusted to move more or less air as needed.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I will try that tomorrow, thanks.
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Let me know if that solves. Hate you changed board but at least it was a warranty issue.Wish I had thought about the thermostat setting confusing the board

Ask Your Own HVAC Question
Customer reply replied 6 months ago
That thermostat setting can only be adjusted if it is set up for electric heat? I'm lost with the thing
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

I see that now.

I think I would try to call Nordyne directly and see if they have records of other people having same issue and if so what solution they suggest

Ask Your Own HVAC Question
Customer reply replied 6 months ago
That's what I have done but they say they will return your call and it takes them a day to call you back. And then of course your not on that job.
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

That sucks. I have been there and done that. Wish I could be more help

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
9,181 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Intertherm Model M3RL080A BW: 1. Furnace comes on normally,
Intertherm Model M3RL080A BW: 1. Furnace comes on normally, as set by thermostat. 2. When thermostat temperature is reached, burners turn off, but fan continues to run. 3.Why won't the fan turn off?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My intertherm furnace is giving me nothing but problems. It
My intertherm furnace is giving me nothing but problems. It is a modelM7RL 060A B W. Now my problem is the blower fan cuts in first then the purge fan then the burner then the fan again. Any help woul… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm having an issue with a combustion fan the furnace works
I'm having an issue with a combustion fan the furnace works normally but after it shuts down the combustion fan turns off the main blower turns off 7 minutes later with no call for heat of combustion … read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
Intertherm M7RL 060, High efficiency furnace will will constantly
Intertherm M7RL 060, High efficiency furnace will will constantly cycle off and then on again before the thermostat is even satisfied. No error codes ever show up. Also, this is with a new filter. lea… read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
Good day, I have an Intertherm (Nordyne) FEH-015HA-03 electric
Good day, I have an Intertherm (Nordyne) FEH-015HA-03 electric furnace. Furnace will run if 1) Thermostat setting is "Auto" and furnace switch is "On" or 2) thermostat setting is "On" while furnace sw… read more
V12Tech
V12Tech
252 satisfied customers
Lennox G26Q4/5-100 Burner lights fine but blower will not come
Lennox G26Q4/5-100 Burner lights fine but blower will not come on with the thermostat set to "auto". If I set the thermostat to fan the blower works fine and the burner shuts down when the temp reache… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
wondering what is the next step in trouble shooting my furnace
wondering what is the next step in trouble shooting my furnace if the ignitor works and I see a flame but the blower won't come on Intertherm model M1MB090A BW… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a brand new never fired up intertherm m7rl I cant get
I have a brand new never fired up intertherm m7rl I can't get this furnace to light, it had a green light on as we'll as a red light , I can get the fan to run with the continuous fan switch but the f… read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
I have a Reheem furnace #RGFD10EZCMS with the programmable
I have a Reheem furnace #RGFD10EZCMS with the programmable modulating thermostat. At the ending of the heating season last spring with the thermostat called for heat ther wouldbe a longer than normal … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Why is SV9502H2522 using a ST9120U1011 unit short cycling
I have SV9502H2522 using ST9120U1011 unit "short cycling" in odd way. Inducer comes on, normal ignition. Blower cuts off mid-cycle, with stat calling. Gas valve closes, blower comes back on. Reignites… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have an Intertherm Heat Rite Furnace, Model MGH-075-ABWN-05.
I have an Intertherm Heat Rite Furnace, Model MGH-075-ABWN-05. Just last night I noticed my furnace had not been running, while I slept. The place was an ice cube when I awoke. When I slid the tempera… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Rheem RGRA - 09EZAJS turns on the blower every once in a while
Rheem RGRA - 09EZAJS turns on the blower every once in a while for about 20 to 120 seconds. The furnace operates properly by turning on when the thermostat calls for heat. It turns off when up to temp… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My Trane XE78 Blowers continue to run after the gas burners
My Trane XE78 Blowers continue to run after the gas burners have been shut down by the thermostat. Blowers will run until the power to the furnace is interrupted. Furnace will restart normally after t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We have a Nordyne/Intertherm gas furnace. Model M1GB 070A
We have a Nordyne/Intertherm gas furnace. Model M1GB 070A BW Serial M1B010305674 Our pilot is on. When we turn the furnace on the flame gets bigger and he blower runs and heat comes through the vents,… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
The inducer motor for my Intertherm model M1MC 0568 BW,
The inducer motor for my Intertherm model: M1MC 0568 BW, series#: M1980803929 has stopped running and I need to know what it's replacement will intail.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Wondering if anyone can help me out on this. I have a Rheem
Wondering if anyone can help me out on this. I have a Rheem oil furnace model ROBC-067LBEA controlled by a Honeywell programmable thermostat. The furnace runs fine and goes through its normal cycle wh… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a york diamond 80 mod. p3hva12no6401a. Used furnace
I have a york diamond 80 mod. p3hva12no6401a. Used furnace for first time last week didnt work had to replace draft inducer. Furnace worked fine for a couple of days. Noticed yesterday blower would ru… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I purchased a 80t furnace and ac unit this is my second heating
I purchased a 80t furnace and ac unit this is my second heating season I change my media filter every 3 months and unit is clean I woke up to a very cold house and notice my thermostat was calling for… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x