I have a 170,000 BTU heater for the shop. After giving up on…

Customer Question
I have a 170,000 BTU...
I have a 170,000 BTU heater for the shop. After giving up on constantly re-lighting the pilot light I installed a Honeywell Y8610U Pilot Retrofit Kit. After completing the installation and turning everything on the pilot lit and the main burner came on within about 2 seconds. PROBLEM - the main burner stays on exactly 20 seconds then goes out. Then everything recycles, the main burner comes on again stays on for 20 seconds and goes off. The flame recertification probe wasn't directly over the main burner flame so I repositioned the Pilot/Ignitor plate so the probe was directly over a main burner.... no change. I added redundant ground wires... no change. I don't completely understand how the recertification system works, especially the path of current flow. I am going to measure the mA current to the probe, but I don't know what to do if it the current flow is good or not good. What do I do next?
Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
1/2/2018
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, you have done almost everything imaginable to solve the problem..

.

The flame rectification probes works this way, the system sends 24voltsAC into the probe, if there is flame there, and you have a good ground, the positive side of the AC sine wave leaks through the flame to the ground.... but the negative side of the sine wave stays put in the probe.... resulting an DC current... the control board senses this DC as proof of flame.

.

We can go from here as needed.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Phil,
Do you have access to the installation instruction sheet? Mine is 68-0291-04. I might have found my problem, I need your input. .........Frank.
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

I do not know what brand the heater is, so am unable to pull the manual on it, if you can tell me the brand name I can often pull the manual..... or.... you can just tell me what you think the problem is, and that might do it

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Phil,
The Honeywell Y8610U Pilot Retrofit Kit has been installed on a Reznor XL-170 heater. The manual I referenced is the one for the Honeywell Retrofit Kit.
I have customers coming in the shop all the time so I can't stop and work with you on the phone, although I agree that would be much easier. If you can take a look at the manual see what you think of the following:Page 14 figure 16 - shows a schematic for “Connections in a heating system with an atmospheric burner and No vent damper.” This is how I wired my controller. It shows running a wire from the hot side of the transformer to the 24V terminal on the controller.Page 13 figure 15 – NOTE: The 24V terminal on the S8610U is used only when a vent damper is installed.Page 12 under the heading “Connect Vent Damper (Optional) in the second paragraph in italics, “Once an ignition control module powers up with a vent damper connected, the module will not function without a vent damper being connected.Question: Does my system think there is a vent damper connected even though there isn’t anything wired to P1? If it does, could that be the reason it is shutting off?
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

Hello again, there is no online access to instruction sheet printer reference numbers... those are internal printer order document references.

I need the brand name of the heater to pull the manual on it, that is how all these things are filed.

.

The phone call offer is automated, I do not send it, a phone call is optional.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Try this link for the Manualhttps://forwardthinking.honeywell.com/related_links/combustion/y8610u/install/68_0291.pdf
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

Thanks, ***** ***** a great manual, each furnace however has a different set up and if I am to help you I need to know all about the furnace that this retrofit kit is going into.

Brand name of the furnace will work in most cases, unless predates the internet

Ask Your Own HVAC Question
Customer reply replied 1 month ago
As mentioned above, the furnace is a Reznor XL-170. This furnace has a heat exchanger and a fan with a thermostatic control... that's it. It came with a Honeywell External controller #V800A. This is a continuous pilot light type controller with a thermocouple sensor for only the pilot light... nothing sensing the main burner. It might be hard to find manuals for either of these.
Customer reply replied 1 month ago
I found the manual for the original controller.
https://customer.honeywell.com/resources/Techlit/TechLitDocuments/95-0000s/95-6996.pdf
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

Thanks for trying... this thing will have to be seen in person to straighten out, it can be unsafe otherwise. I will opt out.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Below your reply it says: "Phil has referred you to a new HVAC Technician. You'll get a response here and by email typically within 24 hours." Is this correct?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,200
9,200 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,200 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My boiler (forced hot water heating system) has been running
My boiler (forced hot water heating system) has been running when no zones have been calling for heat. Why?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I own a Payne heat pump air conditioning/heating system
Hello. I own a Payne heat pump air conditioning/heating system that's been in my home for 10 years or more. I'm sure it replaced the unit originally in my home. There's an air return in the largest ro… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The heating system seems to be on a hold for one day that I
The heating system seems to be on a hold for one day that I cannot chnge Help! … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
XR80 Trane furnace, no heat. system powered, blower starts
XR80 Trane furnace, no heat. system powered, blower starts as normal, observed igniter glow, but glow shuts off in 10 seconds with no ignition. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox rooftop heating system. For some reason, it
I have a Lennox rooftop heating system. For some reason, it is not working. I have had 3 contractors out that have replaced almost every part (gas valve, igniter, etc and the thermostat). It is still … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
277 satisfied customers
We had a new heating system put in this fall, and the
We had a new heating system put in this fall, and the contractor has been back 6 times trying to get the T6 thermos. working right. The down stairs thermo. operates a heat pump until the temp gets to … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
We had a new heating system installed a month or two ago and
We had a new heating system installed a month or two ago and the is a terrible squeling whenever the heat comes on. Our apartment maintence crew has tried eerything they know and it is still there. Wh… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heating system working but is making a buzzing type sound
Heating system working but is making a buzzing type sound every minute or so. It sort sounds like it's trying to start but it's already running. You can hear the sound at the electrical panel inside o… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an electric heating system with a heat pump, and a
I have an electric heating system with a heat pump, and a Totaline thermostat model P274-1200. I received a NEST Pro thermostat that I would like to install. I want to make sure I have the wiring corr… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Within a day of turning on our home heating system for the
Within a day of turning on our home heating system for the cold weather months, I noticed dark streaks beginning to appear down the front of our kitchen cabinets and also dark black spots that looked … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
9,200 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x