I have a 170,000 BTU heater for the shop. After giving up on…

Customer Question
I have a 170,000 BTU...
I have a 170,000 BTU heater for the shop. After giving up on constantly re-lighting the pilot light I installed a Honeywell Y8610U Pilot Retrofit Kit. After completing the installation and turning everything on the pilot lit and the main burner came on within about 2 seconds. PROBLEM - the main burner stays on exactly 20 seconds then goes out. Then everything recycles, the main burner comes on again stays on for 20 seconds and goes off. The flame recertification probe wasn't directly over the main burner flame so I repositioned the Pilot/Ignitor plate so the probe was directly over a main burner.... no change. I added redundant ground wires... no change. I don't completely understand how the recertification system works, especially the path of current flow. I am going to measure the mA current to the probe, but I don't know what to do if it the current flow is good or not good. What do I do next?
Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
1/2/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,708
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, you have done almost everything imaginable to solve the problem..

.

The flame rectification probes works this way, the system sends 24voltsAC into the probe, if there is flame there, and you have a good ground, the positive side of the AC sine wave leaks through the flame to the ground.... but the negative side of the sine wave stays put in the probe.... resulting an DC current... the control board senses this DC as proof of flame.

.

We can go from here as needed.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Phil,
Do you have access to the installation instruction sheet? Mine is 68-0291-04. I might have found my problem, I need your input. .........Frank.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

I do not know what brand the heater is, so am unable to pull the manual on it, if you can tell me the brand name I can often pull the manual..... or.... you can just tell me what you think the problem is, and that might do it

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Phil,
The Honeywell Y8610U Pilot Retrofit Kit has been installed on a Reznor XL-170 heater. The manual I referenced is the one for the Honeywell Retrofit Kit.
I have customers coming in the shop all the time so I can't stop and work with you on the phone, although I agree that would be much easier. If you can take a look at the manual see what you think of the following:Page 14 figure 16 - shows a schematic for “Connections in a heating system with an atmospheric burner and No vent damper.” This is how I wired my controller. It shows running a wire from the hot side of the transformer to the 24V terminal on the controller.Page 13 figure 15 – NOTE: The 24V terminal on the S8610U is used only when a vent damper is installed.Page 12 under the heading “Connect Vent Damper (Optional) in the second paragraph in italics, “Once an ignition control module powers up with a vent damper connected, the module will not function without a vent damper being connected.Question: Does my system think there is a vent damper connected even though there isn’t anything wired to P1? If it does, could that be the reason it is shutting off?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Hello again, there is no online access to instruction sheet printer reference numbers... those are internal printer order document references.

I need the brand name of the heater to pull the manual on it, that is how all these things are filed.

.

The phone call offer is automated, I do not send it, a phone call is optional.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Try this link for the Manualhttps://forwardthinking.honeywell.com/related_links/combustion/y8610u/install/68_0291.pdf
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks, ***** ***** a great manual, each furnace however has a different set up and if I am to help you I need to know all about the furnace that this retrofit kit is going into.

Brand name of the furnace will work in most cases, unless predates the internet

Ask Your Own HVAC Question
Customer reply replied 6 months ago
As mentioned above, the furnace is a Reznor XL-170. This furnace has a heat exchanger and a fan with a thermostatic control... that's it. It came with a Honeywell External controller #V800A. This is a continuous pilot light type controller with a thermocouple sensor for only the pilot light... nothing sensing the main burner. It might be hard to find manuals for either of these.
Customer reply replied 6 months ago
I found the manual for the original controller.
https://customer.honeywell.com/resources/Techlit/TechLitDocuments/95-0000s/95-6996.pdf
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks for trying... this thing will have to be seen in person to straighten out, it can be unsafe otherwise. I will opt out.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Below your reply it says: "Phil has referred you to a new HVAC Technician. You'll get a response here and by email typically within 24 hours." Is this correct?
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,708
9,708 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,708 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I recently installed a Y8610U retrofit control valve on a
I recently installed a Y8610U retrofit control valve on a 170,000 Btu heater that had a standing pilot light. It started without any issues and the main burner came on. It stayed on for about 20 secon… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Raypak 267A. When it lights the burners they only
I have a Raypak 267A. When it lights the burners they only light and go out over and over again. I've replaced everything in the heat exchanger and also the gas regulator. I've cleaned the thermocoupl… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We are dealing with a hydrotherm 175,000 BTU boiler about 4
We are dealing with a hydrotherm 175,000 BTU boiler about 4 years old. It has a history of occasionally having the pilot light go out with the last incident resulting in $75,000 water damage. To allev… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,708 satisfied customers
We have replaced both the pilot assembly and the S6810U
we have replaced both the pilot assembly and the S6810U controller, the pilot lights, we have 24v in all the appropriate places, but the main burner never lights… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Gas heater problem in an apartment. Replace old heater valve
gas heater problem in an apartment. Replace old heater valve that did not have a pilot safety with a new Robert Shaw 400-700 universal and installed new thermocouple to pilot. Tenant moved in January … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a circa 1987 Dunkirk boiler. Honeywell l8148e
I have a circa 1987 Dunkirk boiler. Honeywell l8148e aquastat and a y8610u replacement kit including the new gas valve and control. Boiler has a power inducer vent. Installed by a pro, and still no he… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Hi, 1998 lennox, model G20Q3/4E-100-1, pilot comes on, blower
Hi, 1998 lennox, model G20Q3/4E-100-1, pilot comes on, blower runs, but burner doesn't light, so no heat. Where to start?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Diagnosing a Heatilator Gas Log Furnace, model GC300E / LE,
Diagnosing a Heatilator Gas Log Furnace, model GC300E / LE, that will not stay lit. Problem: Ignitor fires when activated by switch, gas valve opens, gas ignites, stays lit for about 4 seconds, gas va… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
brand new vent free wall mounted NG heater. New gas line to
brand new vent free wall mounted NG heater. New gas line to the unit, black pipe about 25 feet of it, 60" flex pipe to heater itself. Pilot light: won't come on with the ignitor, will come on if I put… read more
hvacdave84
hvacdave84
53 satisfied customers
looked on ebay you gave 2 different numbers you gave a Y8610
looked on ebay you gave 2 different numbers you gave a Y8610 u 3003 and a y8610 F 5003 I also found a y86 H 3014 which one would you recommened… read more
V12Tech
V12Tech
252 satisfied customers
I have a AIRQUEST natural gas furnace that is about 20 years
I have a AIRQUEST natural gas furnace that is about 20 years old model #NNCU075AG01. The blower would come on when the thermostat called for heat but only cold air came out. When I turned the thermost… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have ventless gas fire place log set I can light the pilot
I have ventless gas fire place log set I can light the pilot and it will stay on but when you turn on the logset it lights for about a 30 second and completly shuts down? Harvey… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a tempstar natural gas furnace model nug5075bfb1 with
I have a tempstar natural gas furnace model nug5075bfb1 with a S8600M ignition module that is giving me trouble. The furnace operates correctly most of the time but occasionally requires multiple trie… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Woke up this morning to no heat from the gas furnace (20 years
Woke up this morning to no heat from the gas furnace (20 years old, Duomatic-Olsen). Thermostat calls for heat, induction fan starts, intermittent igniter-sensor lights the pilot, which then goes out … read more
ClimateCreator
ClimateCreator
28 satisfied customers
I have an empire space heater direct vent 35,000 btu. The
I have an empire space heater direct vent 35,000 btu. The pilot would not stay lite. I had the service man out, he replaced the thermopile, lite the pilot and the heat came on. I tried it several time… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Rudd gas pack URGG05N36JKR with a Honeywell S8610U
I have a Rudd gas pack URGG05N36JKR with a Honeywell S8610U Intermittent Pilot Module..Problem Main burner comes on, good flame for 10 to 15 second and then shuts down and recycles. The component part… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a DESA Model CBP20T wall-mounted convection heater.
I have a DESA Model CBP20T wall-mounted convection heater. The original homeowner did not leave a user manual. The Propane supply is good, the kitchen stove is fed from the same pipe and is working). … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Comfortmaker Gas furnace The call for heat gets following results.
Comfortmaker Gas furnace The call for heat gets following results. Inducer motor starts, gas valve clicks and gas for pilot flows. HSI ignites pilot gas. The main burners do not light. The HSI/Flame s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x