Have a 398B furnace with code 14 then code 34 after restart,

Customer Question
Have a Bryant 398B...

Have a Bryant 398B furnace with code 14 then code 34 after restart, This is no pilot proving, replaced the pilot assy with a new one, but still nothing, also no pilot comes on at all and I don't hear the pilot solenoid clicking to tell me gas is flowing.

Contractor's Assistant: Did you check the furnace's filters?

Filter new

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

No I gave a pretty complete desprition

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
1/2/2018
HVAC Technician: Daniel Plourde, HVAC Technician replied 6 months ago
Daniel Plourde
Daniel Plourde, HVAC Technician
Category: HVAC
Satisfied Customers: 455
Experience: I've been in the HVAC buisness since 2008 working on residential, commercial, and industrial buildings
Verified

HI I AM DAN I CAN HELP YOU WITH THIS. DOES THE INDUCER MOTOR RUN WHEN IT TRIES TO START UP

Ask Your Own HVAC Question
HVAC Technician: Daniel Plourde, HVAC Technician replied 6 months ago

OK DO YOU HAVE A VOLT METER TO CHECK A FEW COMPONETS

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Give me a minute to get it.
HVAC Technician: Daniel Plourde, HVAC Technician replied 6 months ago

OK INSTEAD OF ME WALKING THROUGH EACH STEP THIS TROUBLESHOOTING GUIDE WILL BE A LITTLE BIT EASIER TO FOLLOW, FOLLOW EACH STEP AND LET ME KNOW IF YOU HAVE ANY QUESTIONS ON IT.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Got the meter.
HVAC Technician: Daniel Plourde, HVAC Technician replied 6 months ago

OK FOLLOW THE STEPS IN THE TROUBLESHOOTING GUIDE

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Will nothing on that guide was really right for my furnace. But I finally figured out there is a small fusible link in the pilot proving switch that was not proving cold junction so no gas valve no pilot to start with.
Customer reply replied 6 months ago
Want my money back. Had to figure it out myself.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How much does this cost? I have a furnace flashing 34 error
I have a bryant furnace flashing 34 error code-ignition failure, I am an hvac tech myself, not sure what is going on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm trying to figure out how to light the pilot on my
Hi. I'm trying to figure out how to light the pilot on my bryant furnace. Seems it went off. … read more
Rick
Rick
Supervisor
24,226 satisfied customers
I'm trying to restart heat after having run AC all summer..
Hi, I'm trying to restart heat after having run AC all summer. . .getting an error 34, which transitions to 14. THis is a Bryant 80. - Geof … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have 340mav furnace and noted that last night it was no
I have Bryant 340mav furnace and noted that last night it was no longer going on. Getting error code 34 followed by error code 14. Getting no ignition, any thoughts … read more
Webb-Guy
Webb-Guy
Maitenance Supervisor
Associate Degree
3,206 satisfied customers
Bryant model 330 AAV upflow. Very clean condition, filter
Bryant model 330 AAV upflow. Very clean condition, filter clean, attempting to restart after a few months non-use during remodel. upon call for heat from Bryant t-stat, goes through the three cycle at… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
after turning heat on, furnace fan comes on, then shuts off,
after turning heat on, furnace fan comes on, then shuts off, followed immediately by igniter/pilot glowing through window. I looked at power board for any burnt traces or similar and nothing. all gas … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a bryant 355mav giving trouble code 34, & then 14 after
I have a bryant 355mav giving trouble code 34, & then 14 after 4th ignition attempt. I have checked the gas supply it appears fine, all other applicances working good. I have taken the burner assy out… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
I have a 30-year-old Bryant Furnace that has a Essex pilot
I have a 30-year-old Bryant Furnace that has a Essex pilot light control valve. I cannot light the PowerLite there seems to be no gas available. I disconnected the gas line from the control valve to t… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
162 satisfied customers
i have a payne pg9maa036080 furnace that will not turn on.
i have a payne pg9maa036080 furnace that will not turn on. The red led light blinks 14, or maybe 41. The filter was pretty dirty and that has been changed. Any thoughts?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Bryant 395CAV036111, 111,000 BTU, Installed 1-4-00.# LED
I have a Bryant 395CAV036111, 111,000 BTU, Installed 1-4-00.# LED code is: 14 - IGNITION LOCKOUT - Control will auto-reset after 3 hours. Refer to #34 Problem: Furnace stops operating. Can restart fur… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
What does fault code 14 mean for Carrier weathermaker Model
What does fault code 14 mean for Carrier weathermaker Model 58SXB? How do i fix it or get my furnace to work until the technician gets here tomorrow?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
I have a carrier weathermaker 8000 58wav and it shuts down
I have a carrier weathermaker 8000 58wav and it shuts down after running properly for about 5 minutes or so. I then get an error LED blinking message as follows: short blink, long blink, short blink, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Bryant day & night furnace Payne (elrctronic ign.
I have a Bryant day & night furnace Payne (elrctronic ign. )It clicks clicks, pilot goes on, burners ignite,then burners go out.clicks,clicks,clicks again burners go on then go off,does this about 4-5… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
i have a Bryant model 350MAV036000. It returns an error code
i have a Bryant model 350MAV036000. It returns an error code 14 which refers to error code 34. I tried disconnecting the power to reset the furnace two different times with no lick. It is set in the d… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
Our carrier gas furnace went out during the night. I reset
Our carrier gas furnace went out during the night. I reset the furnace and the pilot light goes on and off. in conjucntion with teh furnace going on and off. I have a blinking red light on my gas furn… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
my bryant Mav355 is not blowing enough heat and its running
my bryant Mav355 is not blowing enough heat and its running under the code low heat what is wrong… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
I have a Heil DC90 unit that seems the ignition module or smart
I have a Heil DC90 unit that seems the ignition module or smart valve is not working No pilot light Turned power off everywhere and then turned back on. No clicking, does not seem like I have gas flow… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Hi, I have a Carrier furnace that is approximately 14 years
Hi, I have a Carrier furnace that is approximately 14 years old. It has electronic ignition with a White/Rodgers 36e gas valve. Today it wouldn't light. I got the code that says low inlet pressure. Ho… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x