I have a Ducane furnace about 18 years old. Model #

Customer Question
I have a Ducane...

I have a Ducane furnace about 18 years old. Model # CMPB100U4A. It's a direct vent forced air. Every time it's very cold out, as it is now, I have to remove the three black hoses and drain them and the white box they insert into. I have also cleaned out the box as best as possible to eliminate any blockages. It fails to start constantly every half hour until I drain the system. I've checked the pipes outside and there is no snow blockage.

Contractor's Assistant: Do you have fuel in the tank? If so, is the shut-off valve open and the fuel clean?

Yes to both

Contractor's Assistant: Do you plan on doing the work yourself?

I've had a contractor come for this problem the last several years only to point out this drainage problem

Contractor's Assistant: Anything else we should know to help you best?

I don't think so.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
1/2/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,695
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, if its been this way since the system was new, then a condensate trap was not installed in the exhaust vent piping.... if this problem just started then send me a few photo's of the vent piping, I will look for a problems in the exhaust vent trap drain line.

.

Use the 'add files' link next to your send button to get those photo's to me.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,695
9,695 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,695 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am a new owner of a Lennox boiler (Model# ML 193UH). Last
I am a new owner of a Lennox boiler (Model# ***** 193UH). Last week during the blizzard the pilot went out and came to realize that the intake and exhaust pipes were covered over by snow. When they bu… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Came to this site searching for "American Standard Freedom
Customer: my name is Tim. Came to this site searching for "American Standard Freedom 90 3 flash code" … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
MY ARCOAIRE FORCED AIR NATURAL GAS FURNACE IS 1 YEAR OLD THIS
MY ARCOAIRE FORCED AIR NATURAL GAS FURNACE IS 1 YEAR OLD THIS IS THE SECOND WINTER IT IS 60,000 BTU MODEL N9MSE0601714A. LATELY AND PERHAPS TWICE LAST YEAR WHEN THE WIND BLOWS 20 MPH PLUS OUT OF THE N… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a trane xr90 installed in 2006. Unit will not ignite.
I have a trane xr90 installed in 2006. Unit will not ignite. I replace pressure switch and still same problem. It give me the three flash error code (pressure switch, venting, inducer issue). When I c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a N9MSE (A Series) Furnace installed in November, 2013. There
I have a N9MSE (A Series) Furnace installed in November, 2013. There was warranty work done in March, 2014 (not sure what) to correct a problem where the furnace would lock out with a 3 blips code (Pr… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
ducane lp gas furnace. turns on and flame is fine sometimes
ducane lp gas furnace. turns on and flame is fine sometimes a minute sometimes several. hear what sounds like valve clicking. flame kicks off and on quickly. usually several times. flame then shuts of… read more
type2technician
type2technician
253 satisfied customers
My Lennox Furnace model G32Q4/5-125-2 has an intermittent
My Lennox Furnace model G32Q4/5-125-2 has an intermittent condensate drainage problem. This originally occured several years ago and again today (very cold out) The Header Box Condensation trap fill… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Ducane model # XXXXX direct vent forced air
We have a Ducane model # XXXXX direct vent forced air furnace. It runs for a minute then the flame goes out and then it continues to blow only cold air. When the flame goes out, the Honeywell gas cont… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a superior direct vent gas fireplace insert between
I have a superior direct vent gas fireplace insert between five and ten years old . It is rated at 30,000 BTUH minimum input, 38,000 BTUH max input and 27,930 BTUH output Instead of having the exhaust… read more
Electrifier
Electrifier
Owner - Contractor
Bachelor's Degree
147 satisfied customers
I have a American Standard Freedom 90. I am getting 3 blinks
I have a American Standard Freedom 90. I am getting 3 blinks which indicates a pressure switch issue. I have checked the hose and verified i here a click when blowing. The hose goes from the Pressure … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Rheem condensing gas furnace that wont go into fan
I have a Rheem condensing gas furnace that won't go into fan heat mode. I get error 57 on the furnace. The burners will light & the fan will work if I force it to on the thermostat (without the heat o… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Having an an issue with a Trane XR90. It tries to ignite kicks
Having an an issue with a Trane XR90. It tries to ignite kicks off and keeps retrying. The error code is for the pressure switch. I have checked the hoses from the pressure switch. Checked the drain l… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a GUD090B35A , Serial # XXXXXXXXXX High Efficiency
We have a GUD090B35A , Serial # XXXXX High Efficiency Gas Furnace, Direct Vent Furnance. The condensation is not draining properly through the hose. It appears to have a crack in the Plastic Heat Exch… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox G51MP furnace, less than 6 years old, with
I have a Lennox G51MP furnace, less than 6 years old, with a continuing problem. The outlet from the collector box to the left pressure switch keeps clogging with an unknown substance every couple of … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
In the afternoon, the temperture in the house goes up to 75,
In the afternoon, the temperture in the house goes up to 75, even though the thermastat is set at 71.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Our Trane XR-90 furnace is flashing 3 - pressure error. Of
Our Trane XR-90 furnace is flashing 3 - pressure error. Of course it is Friday night and it is snowing... Is this something we can fix on our own?… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I am having trouble with my furnace It is a coleman air pro.
I am having trouble with my furnace It is a coleman air pro. model number is XXXXX serial number is XXXXX it will go on then the gas will shut off after two minutes and the warning flasher flashes thr… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
how do I drain my my Rheems water heater model # XXXXX Ive
how do I drain my my Rheems water heater model # XXXXX? I've turned off the blue knob on the top turned off the breaker and attached a hose to the bottom turned the knob and still nothing except a lit… read more
Glenn
Glenn
Maintenance, Technician
Associate Degree
1,612 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.