Hi I have a Gibson air exchanger heat unit and AC, blowing circuit braker

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Model GB5BM-T24k-B, sn GBD06060501619, filter is good clean breaking the braker 40 amp in Panel and on the heater side drawing 31 AMP

Contractor's Assistant: Do you plan on doing the work yourself?

I did notice their a 40 amp on panel, should it be 50 AMP ?

Contractor's Assistant: Anything else we should know to help you best?

I have a licsence electrian getting a new permit this week, if its the heater system after the panel replace, who in the NJ area services the heat unit. ?

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
1/2/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,708
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, that is an air handler/ blower unit with electric resistance heaters.... if its drawing a total of 31 amps it should not trip a 40 amp breaker unless the breaker is bad.

You cannot increase the breaker size to 50 amps without installing larger wire.

.

That type of air handler is normally connected to a 'heat pump' (type of AC unit that runs in summer for cooling and winter for heating)..... it could be the problem ... it depends on how its all wired.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Thx Phil , I have a HVAC TECH COMING IN THE MORNING, and we are also doing
A replacement panel, need to summit s permit in the morning with a license electrian contractor, so at this time, not sure where the problem is just yet
The breaker panel is a federal pacific that will be replaced in a few days thank you for your help on this matter,
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thats a good plan, and good to be get rid of that Federal panel as well, those are fire hazards.

.

Its time to rate my work for the day, that will get me paid as well, it will not increase your charges but is how I earn a living.

Locate the "finish and rate your expert' link near the top of your page and click on it... I will appreciate that very much, thanks!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,708
9,708 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,708 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
New cbx25uhv and Xp14 installed July2017, turned heater on
new cbx25uhv and Xp14 installed July2017, turned heater on for the first time last week, the heat strips are causing the house breaker (50amp) to trip b/c dealer says the heat strips are drawing appro… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,944 satisfied customers
I have a Bryant plus 90 that was built in 1998. Last night
I have a Bryant plus 90 that was built in 1998. Last night I noticed that the blower motor was going and it seemed cold. Checked t-stat. Was at 67. Normally set for 72 degrees. Turned off power to fur… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a York 4 ton AC unit (5 years old) that stopped working
I have a York 4 ton AC unit (5 years old) that stopped working last week (neither fan nor compressor on the unit would start up). I called an AC specialist out to come check it out. He showed me that … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,708 satisfied customers
I have a GPH1348H21AB goodman heatpump like to no how I can
I have a GPH1348H21AB goodman heatpump like to no how I can wire it to my thermostat in my house the outside wires are white-brown-blue-red-orange-yellow-green and the thermostat is a white rogers and… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
What is the proper fuse type and part number for the dual 250V
What is the proper fuse type and part number for the dual 250V fuses inline between the electrical panel circuit breaker and my Lennox 10ACB60-5P. We live in Oregon, US. The fuses have been blowing on… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We have a York Model #n2ahd14a06dac airconditioner/heater.
We have a York Model #n2ahd14a06dac airconditioner/heater. The airconditioner worked good but the heater would run a few minutes & kick the blower circuit breaker. We replaced a 30 amp circuit breaker… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,708 satisfied customers
Ac runs for about 10 minutes then blows 40 amp brker, replaced
Ac runs for about 10 minutes then blows 40 amp brker, replaced run capacitor, no change problem began overnight… read more
spivco
spivco
153 satisfied customers
Paloma is made by Rheem? And has a model without electric which
Paloma is made by Rheem? And has a model without electric which can be vented thru a B vent galvanized steel..Can this vent be shared with a gas forced air heating system?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,708 satisfied customers
I recently had a goodman heat pump installed - model # XXXXX
I recently had a goodman heat pump installed - model # XXXXX 130 601 AC - serial # XXXXX It is 40 feet from power suppy with a 35 amp circuit breaker and 10 AWG wiring. After about 1 hour operation it… read more
Drew1315
Drew1315
Over 5 years of college education
86 satisfied customers
I have a bryant furnace model 350MAV. Last year I noticed
I have a bryant furnace model 350MAV. Last year I noticed a puddle of water at the base of the unit. I just took of the bottom panel and i noticed rust. It looks like the water was dripping down just … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, I have a Goodman Heat Pump MODEL GSH 130361AC.
Hello, I have a Goodman Heat Pump MODEL GSH 130361AC. The information on the unit states: MAX FUSE AMPS OR HACR TYPE FUSE BREAKER - 20 I have a 40 AMP breaker at my main power panel and a house inspec… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Pilot light wont stay lit, we just installed a new thermostat
Pilot light won't stay lit, we just installed a new thermostat which did not cure the problem and now when we physically light the pilot ourselves, it will only bring up the temp in the house 1 degree… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a heater/air evaporator air conditioner combo. Part
I have a heater/air evaporator air conditioner combo. Part is in a closet in my condo and the rest on the roof...a couple of floors up. A few weeks ago…..the heater/air cond. started tripping the brea… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I live in a 3000 sf home with my wife and daughter.My home
I live in a 3000 sf home with my wife and daughter.My home has 2 1/2 baths a laundry room and a dishwasher.What tankless water heater by RUUD do you think will best meet our needs.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
my furnance cuts off and the 40 amp braker get very warm almost
my furnance cuts off and the 40 amp braker get very warm almost hot. I changed out the braker every thing was good for about three weeks and the problem started all over again. the furnance is a goodm… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Robert Johnson, Union Baptist Temple, Atlantic City, New Jersey We
XXXXX XXXXX, Union Baptist Temple, Atlantic City, New Jersey We are tax excempt and we are looking for a condenser coil for our unit. Model #50EW-024---510NA, Serial #1600F94649. We have members who c… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Mr slim Split type AC/Heating unit in the wall.....about
I have a Mr slim Split type AC/Heating unit in the wall.....about a year and a half old.....recently it began blowing out only cool air, then when on heat it wasn't blowing hot....I went to the Manual… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I AM AN ARCHITECT WORKING ON A TENANT FITOUT LOCATED IN CHERRY
I AM AN ARCHITECT WORKING ON A TENANT FITOUT LOCATED IN CHERRY HILL, NJ THE OWNER WANTS TO USE RUDD EQUIPMENT FOR A ROOFTOP INSTALLATION. THE TENANT IS A MEDICAL BLOOD DRAW FACILITY 2100sf. CLIENT WAI… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x