I have trane xr90 and heating is not coming up, it is trying…

Customer Question
I have trane xr90...

I have trane xr90 and heating is not coming up, it is trying to start and resrarting itself

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostat is fine, it was working till morning

Contractor's Assistant: Do you plan on doing the work yourself?

Didnt get any emer service today as new year

Contractor's Assistant: Anything else we should know to help you best?

Blower is trying to start and immediately getting restarted continuously, I see red light blinking continuously

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
1/1/2018
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,711
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like a bad ignition module, locate that on the wiring diagram then check for 120vac across its two terminals in a window of 30 to 60 seconds after the inducer fan comes on.

.

If you have 120v there and the igniter is not glowing, then replace the igniter.

.

If you do not have 120vac there and the inducer fan was running when you checked that voltage, the printed circuit board is bad.

.

If you need more specific instructions

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,711
9,711 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,711 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trane XR80. Thermostat is from Honeywell. Everything was
Trane XR80 . Thermostat is from Honeywell. Everything was working till yesterday but suddenly now, thermostat restarts when trying to make heat a call. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a York Diamond 90 HVAC system that isn't producing
I have a York Diamond 90 HVAC system that isn't producing heat. At first it wouldn't light the flame and I observed the error code of the red light flashing 4 times. I tapped the pri***** *****mit swi… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Trane XR90 furnace about 12 years old. It's blowing
Hi, I have a Trane XR90 furnace about 12 years old. It's blowing cold air not warm. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a Trane XB 80 installed 2002. Replaced circuit board
Hi, have a Trane XB 80 installed 2002. Replaced circuit board a couple of years ago after burn out with White-Rodgers 50A55-486 and added a Nest thermostat. Been working well but two days ago blower s… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
hi there im not sure if i have a problem or not... i just bought
hi there im not sure if i have a problem or not... i just bought a house and heard a blower motor go on every two minutes and i automatically assumed it was my furnace... but it was my hot water tank … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My trane xr90 furnace isnt working. The gas turns on and it
My trane xr90 furnace isn't working. The gas turns on and it fires up, but When it comes time for the air to begin blowing it makes A "whisk" sound and restarts. The light is blinking Continuously rap… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
My trane xr90 furnace is in a lockout mode and is continuously
My trane xr90 furnace is in a lockout mode and is continuously blowing cold air. I took off the covers and the red led light is blinking 9 times for check ignitor. So I replaced the ignitor because it… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,711 satisfied customers
I have a Trane XV80 furnace, was working fine for the last
I have a Trane XV80 furnace, was working fine for the last 2 weeks since we started it back up this season. Today it quit igniting the elements, kinda weird since it started fine this year. Changed th… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Trane XR90 furnace with a Trane condenser. Tried to
I have a Trane XR90 furnace with a Trane condenser. Tried to start the cooling yesterday for the first time this year and the T'stat engaged the furnace/blower, but the condenser did not start. T'stat… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
thermostat Honeywell TH8321U is applied to a GEO thermal system. The
thermostat Honeywell TH8321U is applied to a GEO thermal system. The RED light in the upper right hand corner has been on a few times. I powered down and then restarted to clear, but do not know what … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Trane XV90. Has been working flawlessly for over a
I have a Trane XV90. Has been working flawlessly for over a year. This morning, after heating for a while, I noticed that we had not reached temp, fan still blowing, but not heated air. Turned off the… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Good evening. My Trane XR90 forced air furnace is not working.
Good evening. My Trane XR90 forced air furnace is not working. It was installed October 2003. I have never had any problems, EVER! This is the first. The red light is blinking continuous. I can't tell… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Im having an issue with my Trane AC unit. My fan will blow
I'm having an issue with my Trane AC unit. My fan will blow just fine when I set my thermostat to fan always on. When I then set my thermostat to cool, the fan shuts off and the control goes into lock… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We have a trane system with 2 zones and a clean effects filtration
We have a trane system with 2 zones and a clean effects filtration system. the blower is working but their is no heat. the system light is not indicating that heat is being called for and the red LED … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane XR90, LED blinking twice, blower running constantly -
Trane XR90, LED blinking twice, blower running constantly - only cold air. Air intake was covered by snow for about 48 hours (I was gone when big snowstorm hit) is now clear. What do I need to do?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
my furnace isnt working right it was just blowing cold air
my furnace isnt working right it was just blowing cold air last night when i turned it off waited 5mins and turned it on it would work for a little bit but then the warm air turned cold again today th… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
What does the light in my Xr80Trane furnace with no heat indicate?
I have a XR80 Trane furnace with no heat and the led blinks 1x continuously. What does the light indicate?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane xr90 heat system blowinng only cold air. Checked thermostat,
Trane xr90 heat system blowinng only cold air. Checked thermostat, breaker and filters...all were fine. There is a flashing red light coming from front panel, which we opened and reclosed to try to re… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x