My 1yr old furnace HEIL High Efficiency Condensing Gas

Customer Question
My 1yr old furnace...

My 1yr old furnace HEIL High Efficiency Condensing Gas Furnace started giving us problems Sunday Morning. We woke up to a cold house. The furnace wouldn't turn on. I changed the dirty clogged air filter and it briefly started working, then stopped. I looked in the installation manual and did the reset by turning it off for 5 mins and turning it back on. It worked for several hours, then stopped again. I once again had to reset it and it started working. Several hours again, it did it again. I reset it again for the 3rd time. So far, it is still going. What could be the cause of this?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes, the thermostat is working. I changed the clogged filter 1st, like I said earlier. Is there another filter somewhere?

Contractor's Assistant: Do you plan on doing the work yourself?

I just want to know the cause. If its a simple fix, then yes I will do it myself. If its more complex requiring calibrations, then no.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
1/1/2018
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified

First of all since furnace is new, I suggest calling the installer if you can wait until he arrives before we start doing any major work as the unit is still under warranty.

Now with this said lets take a look at a couple of things and see if it is a simple fix.

When it fails we should get an error code on control board.Look on board and see if we have an error code.

The most common on these furnaces is an open pressure switch.

We will go from here. Also give me model from label in burner section.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 6 months ago

Absolutely.But if you want to check a couple of things let me know.When it fails we should get an error code on control board.Look on board and see if we have an error code.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I don't see a control board
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Phil I have a nordyne furnace model number kg7sc072d-24b. We
Hi Phil I have a nordyne furnace model number kg7sc072d-24b. We have had trouble getting the furnace to operate this season. we have changed the filter and the system is trying to fire up. The ignitor… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
It says Calib, checked the calibration switch and it is set
It says Calib, checked the calibration switch and it is set to off. … read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
Our Heil DC90 ultra gh efficiency furnace has the blower
Hi our Heil DC90 ultra high efficiency furnace has the blower running but is generating no heat. Can you help?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier furnace that is showing error code 33. I
Hello. I have a carrier furnace that is showing error code 33. I opened the door on the back and flipped the switch on the side and it worked for a few minutes. I just did the same thing again, this t… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an AS Freedom90 that was installed without intake
I have an AS Freedom90 that was installed without intake filters about 7 years ago. This year I figured out how to put a 16x20 filter in the opening and have had some ignition failures. I had a tech c… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I hope you can help with my problem. First an explanation. I
I hope you can help with my problem. First an explanation. I am trying to figure out where the filter in my Heil furnace actually should go. Two different repair technicians have given two different o… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a York lx series condensing furnace. It rruns
I have a York lx series condensing furnace. It rruns for a few minutes then shuts down for hours. Then starts up and runs minutes then shuts down again. This cycling repeats but the house never gets t… read more
airheatman
airheatman
HVAC Technician
9,213 satisfied customers
I have a Tempstar T8MPV075F two-stage variable speed mid-efficiency
I have a Tempstar T8MPV075F two-stage variable speed mid-efficiency gas furnace which I bought in February 2009. Sunday morning it had stopped sometime during the night and the thermostat was showing … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Im having trouble with the high limit switch fault on my furnace.
I'm having trouble with the high limit switch fault on my furnace. It's happening intermittently--the four flashes of the LED light & boom, there's the cold air blowing again. This happened last winte… read more
airheatman
airheatman
HVAC Technician
9,213 satisfied customers
My Lennox G60UH(X) Series furnace is experiencing problems
My Lennox G60UH(X) Series furnace is experiencing problems indicated by the alternating fast blink. These problems began when I changed the filter. I noticed that my filter was filling up, so I put in… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a Honeywell Chonotherms III model 8602. No matter whether
I have a Honeywell Chonotherms III model 8602. No matter whether I set it for heat or cool or off and turn the fan on auto, the fan runs constantly. I replaced the batteries. The fan runs without rega… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hi, I have a RHEEM gas furnace. On the front is a Honeywell
Hi, I have a RHEEM gas furnace. On the front is a Honeywell part; it's a small plastic box with a little glass piece. The words on it are: Filter Flag, Adjust, a curved arrow pointing to - and + symbo… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I recently replaced the blower motor in my Coleman furnace.
I recently replaced the blower motor in my Coleman furnace. The furnace worked fine for a fews days but then the auxilary switch needed resetting indicated by four flashes. I would reset the switch an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a new York Affinity 9.C series furnace which was installed
I have a new York Affinity 9.C series furnace which was installed in July 2009. When I first turned it on in Sept. it didn't work and a repairman had to come and put in a new part. A week ago I woke u… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello, I have a Carrier Weather Maker High Efficiency model
Hello, I have a Carrier Weather Maker High Efficiency model number 58sxc080-JG and the manual reset limit switch on the ouside of the burner compartment has tripped 4 times in the last 4 days, twice t… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Trane X80 furnace. The other morning I woke up and
I have a Trane X80 furnace. The other morning I woke up and the house was 56 degrees and the "flame" icon was showing that the heat was on. I go the the themostat toggle it to "off" and back to "heat"… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Trane XB 90 Gas furnace. I have cleaned all the drainage
I have a Trane XB 90 Gas furnace. I have cleaned all the drainage hoses, replaced the filter and have installed a new thermostat. The furnace starts its cycle as the fan blows. It starts and stops sev… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
regarding heil blower p/n from fasco industires #1010928 115
regarding heil blower p/n from fasco industires #1010928 115 volt hz 60 amp 2.3 hp 1/25, what would the approximate replacement time in hours be to put it in the furnace, a 90% + efficiency furnace fr… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.