I have a nit 200 boiler which was installed in spring 2010.

Customer Question
I have a nit...

I have a nit 200 boiler which was installed in spring 2010.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Sorry - didn't t finish message. I am writing from Collins wood Ontario wg here it has been very cold for the last ten days.

Contractor's Assistant: Do you plan on doing the work yourself?

For the last three weeks we have had constant problems with the boiler shutting down and showing err 04 message. Initially the shut downs occurred periodically - but over the last 2 weeks it has become more frequent . Every 24 to 48 hours. Yesterday the boiler shut down early morning - we turned off power and then restarted about one and a half hours later and it ran till about one hour ago. Our heating service company Campbell mechanical of singhampton ,Ontario has been about seven times in last few weeks and replaced various sensors and checked all wiring - but they do not seem to be able to diagnose and solve the problem - do you have any suggestions ? Could it be faulty thermostat ? Or, since the shut downs have become more frequent more recently and the weather has become extremely cold recently , could the problem be frozen condensation pipes ;?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Don t understand - what do you mean to " check thermostats settings " ? And what filters are you referring to ? Thx.

Contractor's Assistant: Anything else we should know to help you best?

Please see my reply to your previous message.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
1/1/2018
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, you were talking to our an automated that asks a few basic questions to make things go faster.

I am a live person, age 77 with 58 years in the boiler business.

If this well qualified company has been out 7 times they are obviously conscientious hard working people.. and they changed all the suspect parts. We will be looking for something unusual that they might have missed,

.

Click here please, tell me if this manual looks like its for your boiler or not

We can go from there.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I do not wish to continue .
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Tell me the temperature of the room that the boiler is located in... if the room is very cold, then moisture could be forming inside the units pressure switch sensing tubes, causing this problem.

.

OK if you do not with to continue, just do not answer my question here and ignore future notices. Good luck with it!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a fault message on my Burnham Alpine ALP150-2L02
Have a fault message on my Burnham Alpine ALP150-2L02 boiler. Window is showing (i) information pane and message is Bioler, 173F, drive lightoff. Bioler is running constant pressure steady at 15 psi, temperature cycling between 180F and 130F. When boiler reaches 180F you can hear the fan come on and spool up..... runs about two to three minutes and shuts down. Boiler has shut off three times that I know of since about 6am.... I think it shuts down on overheat, but them restarts within about 15 minutes. All circulating pumps are running. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Not enough heat from Burnham Boiler to keep house warm in
Not enough heat from Burnham Boiler to keep house warm in these cold conditions. Boiler water is cycling between 160F and 200F as seen on the temperature gauge. Can the temperatures be raised to provi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an ancient oil fired steam boiler fitted itchy a
I have an ancient oil fired steam boiler fitted itchy a Honeywell Intermittent ignition oil primary lock out switch R8184G 4074. The system operates off. basic Honeywell non-programmable thermostat. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Burnham gas fired residential Boiler,with 5 taco
I have a Burnham gas fired residential Boiler,with 5 taco zone valves Last week the hot water tank stopped heating water the Hyrdrostat apears to click when adjusted for temp setting. the taco valve t… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Morning.. I have the Honeywell CT3500 (replaced batteries)
Morning.. I have the Honeywell CT3500 (replaced batteries) and the house temp is 62 degrees while it is set to be at a steady 70. The boiler comes on but not as frequently as it should. It's 0 degrees… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have newer es2 boiler that from time to time will not
I have newer es2 boiler that from time to time will not fire. the burner shuts down but the damper will not close. I replaced the damper but it still stays open and will not fire. to get to fire I tur… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noi
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noise issues and both boilers required "tuning" - adjusting CO2 levels and other settings. Now my boiler is quiet an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I just bought a home with a Weil-Mclain boiler. I have no
I just bought a home with a Weil-Mclain boiler. I have no experience with boilers. The boiler has been turned on recently because of a cold snap in my area. However, if I do not keep the thermostat se… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hi, I have a Veissmman 100 installed 3 years ago, about a
Hi, I have a Veissmman 100 installed 3 years ago, about a month ago, the heating stopped working. When I checked the unit, it showed a F4 fault code. I did not know what that was, and I simply shut it… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My boiler - a oil fired "cam-ray 15/21 - has recently started
My boiler - a oil fired "cam-ray 15/21 - has recently started to make a knocking noise once it has been running for a minute or so - what could this be? Thanks Paul… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I am Charles Reynolds. I have aCustomersystem installed in our
I am Charles Reynolds. I have aCustomersystem installed in our basement. It was put in circa 2005-6 for jack Earnst, the President of Quietside at his then residence atXXXXX Carlisle PA. The system ha… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
The boiler is normally switched off in February because the
The boiler is normally switched off in February because the solar panels give us hot water until September before the boiler is required again. Now and then during this period (During the evening) it … read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
We have a Quantum 95 200+ boiler and it has a chronis problem
We have a Quantum 95 200+ boiler and it has a chronis problem of shutting itself off. When it does this we get an "E 02 error message. The remedy is for us to restart it by turning off the power switc… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Phil My wife has been bugging me to get back to you about
Phil: My wife has been bugging me to get back to you about our furnace - it continues to act up. As you may remember, it will fail to shut down after a heat cycle, with the result that the blower keep… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a L8124A Honeywell Aquastst on my boiler that was replaced
I have a L8124A Honeywell Aquastst on my boiler that was replaced about 4 years ago. Last year it was replaced again. Now that the colder weather has come and I turned the thermostat up to get heat I … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have an old honeywell ST6400C boiler. It heats the water
I have an old honeywell ST6400C boiler. It heats the water fine, and all the radiators get hot when the heating is on. However, the hot water in the immersion tank is going from piping hot to cold wit… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
i have burnham boiler in my church, with seven zones , the
i have burnham boiler in my church, with seven zones , the building has three levels and i can,t get the pressure right to get heat at the top floors. Can I get somes suggestion?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My series 2 Burnham gas boiler, operates fine for about 4 hrs
My series 2 Burnham gas boiler, operates fine for about 4 hrs then the pilot needs relit. I changed the thermocouple twice., I cleaned the pilot and made sure the orface was clear, I cleaned all of th… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x