Our furnace stopped working yesterday so, I looked in the…

Customer Question
Our furnace stopped working...

Our furnace stopped working yesterday so, I looked in the manual trouble shooting section for clues. The LED light was blinking three times, I checked the inlet air pipe located outside beside the exhaust pipe and there was some ice formed inside blocking/restricting the inlet. I removed the ice and the furnace started working. I also called the heating contractor that installed the furnace and the tech told me that this is a known issue with these furnaces. Is there a recommended fix?

Contractor's Assistant: Did you check the furnace's filters?

Yes, it was just replaced last week

Contractor's Assistant: Do you plan on doing the work yourself?

Yes,if possible

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
1/1/2018
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,754
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

That is a pressure switch code, meaning the pressure switch is not closing when the exhaust fan is coming on. So you need to check and make sure the exhaust fan comes on first. You can cycle the power off to the unit at the switch or breaker for a minute and turn it back on to clear the code and restart a heat cycle making sure the thermostat is on or you have R to W jumpered on the board in the furnace. If the fan does not come on check the fan for power. If the fan does come on and nothing is plugged in the exhaust or intake vent then check the pressure tube for blockages. That is the rubber tube that connects the pressure switch to the blower housing. If that tube is blocked or cracked that code will come up. You need to check the port where the tube connects to the exhaust blower housing make sure that port is not blocked with crud. Normally it is one of these issues causing that code on the furnace. Lastly you have to check all condensate lines on the unit, especially the drain line that comes out of the inducer motor housing to make sure nothing is blocked causing a backup of condensate water.

Happy New Year!.....All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 7 months ago
It's none of the issues that you have described. The inlet air piping {located outside beside the condensate discharge line} gets ice build up from the exhaust condensate coming out. I believe that the lines should be farther apart, that way the condensate doesn't get sucked into the inlet line. Is there a recommended distance between these lines that AMANA recommends?
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

Yes they should be at least 2 foot apart or more and have the intake facing away from the exhaust they should be opposite.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Thank you! Happy New Year
HVAC Technician: HVAC Guru, HVAC TECH replied 7 months ago

You too!..All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,754
18,754 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Here is the sisu. Here is the situation: Trane XR90 gas
Here is the situation: Trane XR90 gas furnace installed in 2010. Had trouble with it shutting off intermittently when it was running resulting in the three blinking lights. If we pulled the pvc intake tube out of its socket on the furnace once this happened, the unit would work without trouble. Called technician in after a year or so of this and tech spent several visits investigating the furnace. his solution was to cut the intake pipe off about 1 foot from the furnace so intake came from air in the basement; not outside. this has worked without trouble for several seasons. // We are now remodeling the basement and need to get the furnace pulling fresh air from outside instead of air from inside the basement to satisfy building permit inspectors. My contractor thinks the original trouble was that the intake piping had 4 90 degree turns in it making intake air intake problematic. I have the chance now to re-do the intake pipe on a different route to outside with just 2 45 degree angles. Would t his be a good solution that would have a good chance of fixing the issue? I assume thats since the tech spent so much time investigating the unit and the situation (and that his solution worked) that there are no internal issues with the unit causing the shut down. Thanks in advance for your reply. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
How to light the pilot light on my Enviro Plus 90?
Need to light the pilot light on my Enviro plus 90 forced air furnace. I have no clue and it's cold here in Wisconsin!… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,754 satisfied customers
I have a Carrier 96 infinity furnace and notice that the plastic
I have a Carrier 96 infinity furnace and notice that the plastic or pvc combo intake and exhaust unit that exits my house cause a large amount of condensation against the building forming a very large… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a Freedom 90 furnance and it cycles out and blows cold
I have a Freedom 90 furnance and it cycles out and blows cold air. This is the second winter we have lived in the house. If I push in the reset button the furnance will start back up and run anywhere … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,754 satisfied customers
Carrier 58MCA led light is blinking code 31. No heat.
Carrier 58MCA led light is blinking code 31. No heat but fan will run. Burner doesn't go on.… read more
Expert
Expert
How to troubleshoot Lennox ml193uh furnace that quit working?
My furnace, ML193UH, has been working very well. This morning I awoke to an unusually cool house and checked the diagnostic lights and was sure enough, the green light was blinking slowly. When I chec… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, I had a High Efficient Furnace installed last fall.
Hello, I had a High Efficient Furnace installed last fall. In the middle of winter the furnace quit working. The condensation from the furnace exhaust (water in the natural gas) slowly dripped outside… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
Hi, I have a Bryant gas home heater system; Model 311JAV048135AAJA.
Hi, I have a Bryant gas home heater system; Model 311JAV048135AAJA. The pilot will not ignite. We were on vacation for a few weeks and just tried to turn it on. Any answers?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Model M1MB-056A-A-BW. LED solid red. Thermostat starts combustion
Model M1MB-056A-A-BW. LED solid red. Thermostat starts combustion motor but LED flashing twice indicating open pressure switch. Pressure switch lines are clear. Combustion motor runs on but no ignitio… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Lennox G43UF Heat isnt turning on...Diagnostic Code LED#1
Lennox G43UF Heat isn't turning on...Diagnostic Code LED#1 Red if off and Led #2 Green is flashing...Could be Pressure prove switch open or blocked inlet/exhaust vent or pressure switth closed prior t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my goodman furnace seems to be blowing cold air temp set at
my goodman furnace seems to be blowing cold air temp set at 72 reading 67, furnace is running. through lower sight glass can see a red light blinking three times, then off and then repeats? Any ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why is Classic Rheem pressure switch shuting off burner?
Classic Rheem 90 upflow. Periodically, the pressure switch attached to the draft inducer closes and shuts off the burner. I checked the tube connected to the pressure switch and draft inducer, which i… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Goodman LP, Model#GMPN120-5 REVV, Serial #0112609216.
I have a Goodman LP, Model#GMPN120-5 REVV, Serial #0112609216. when I call for heating in either zone thae fan will start but the furnace will not fire. I have gone through the pilot restart instructi… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i have a lennox elite series furnace, first of all the thermostat
i have a lennox elite series furnace, first of all the thermostat is an older round twist mercury type, the furnace is not turning on unless i move the thermostat around a few times, but once the furn… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Trane xl 90 furnace. The blower motor will not turn off. I
Trane xl 90 furnace. The blower motor will not turn off. I had to turn the breaker off to stop it. What can I do? Thanks.… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Rheem classic 90. 3years old. when thermostat call
I have a Rheem classic 90. 3years old. when thermostat call for heat the IDT (small starter fan) begins turning and the second LED starts to bink. It runs for about 30 seconds and shuts down. NOW when… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
The exhaust vent (venting to the exterior of the house) on
The exhaust vent (venting to the exterior of the house) on our coleman furnace (3yrs old) drips so much water in the winter months that a cone of ice (2 ft high) forms outside at the vent pipe and eve… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a G71MPP-60D-135-02 gas heater. The temperature in
I have a G71MPP-60D-135-02 gas heater. The temperature in Omaha NE in the last few days has been sub zero. My unit cannot meet demand. Even with the themostat on 81 it can only get to 66. I have had t… read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x