Our furnace is not working - we're getting fault code 13 on…

Customer Question
Our furnace is not...

Our furnace is not working - we're getting fault code 13 on our thermostat readout. It says system fault 13 - limit lockout. The temperature is going down is at 63. Its below 0 outside

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I don't know. Could be either. Last night I noticed it, the fan seems to be working on the furnace, but not sure what the problem is.

Contractor's Assistant: Do you plan on doing the work yourself?

No

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
1/1/2018
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,390
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 4 months ago

This is likely a thermal rollout issue. There are high limit safety thermostats that are around the burner housing area that can trip open if they fail or the unit is overheating. Some of these have reset buttons on them that you can manually press down to reset while others do not. The ones that do not either are one time limits or are limits that are suppose to manually reset when cooled down. Now that does not always happen when they go bad so you will have to check them for continuity with an ohm meter across the two leads going to them. If you do not pwn a ohm meter you can physically bypass each rollout to make sure it is good by connecting the two wires to each rollout sensor together to see if the unit will then operate. Now once you have found the bad one you can change it out or reset it and then you should check your furnace filter for blockages and make sure you main furnace blower is running to speed. These two things can cause a unit to overheat and trip one of these rollout sensors. Mosts units have 3 of these devices and here is a link to what they can look like on your unit.

CLICK HERE

CLICK HERE

CLICK HERE

Happy New Year!.....All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Was this answer helpful?
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,390
18,390 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
my rheem classic 90 furnace blower starts but wont' ignite
my rheem classic 90 furnace blower starts but wont' ignite.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My furnace acts like it wants to kick on but then stops -
My furnace acts like it wants to kick on but then stops - then tries to kick on then stops. It won't come on but keeps trying to. I've had 3 technicians out and they seem to think the problem is resol… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,390 satisfied customers
Explain how and where I change furnace filter on Trane XT 95
Explain how and where I change furnace filter on Trane XT 95 furnace … read more
David Bowden
David Bowden
Owner
850 satisfied customers
My furnace blower will not turn off. I removed the
My furnace blower will not turn off. I removed the thermostat but it continued to run. I had to run it off st the unit, is this a fan switch issue? Or could it be resolved with a new thermostat? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Are permanent furnace filters a better option than the one
Are permanent furnace filters a better option than the one you need to replace every 3 months?I have been using the 3M Filtrete filters for a while, but recently I was told that electromagnetic filter… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,804 satisfied customers
Furnace blower will kick on for a minute or two then stop.
Furnace blower will kick on for a minute or two then stop. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
HVAC, 30 year old natural gas furnace, blower starts and
HVAC, 30 year old natural gas furnace, blower starts and heater relay on circuit board immediately clicks off. Does not trip circuit breaker. Thinking bad relay or over amp load condition, maybe dead … read more
Bill
Bill
Service Mgr
100 satisfied customers
Why is there water under my furnace? Filter is clean and
humidifier is off and not leaking, AC is off, quite cold outside, no snow on chimney… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rheem furnace blower runs on low but will not run on high
rheem furnace blower runs on low but will not run on high furnace goes off on high heat limit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,804 satisfied customers
My Rudd furnace blower vibrates the entire house. Research
My Rudd furnace blower vibrates the entire house. Research indicates a motor/fan set screw may need tightening, but I can't see one. Where is it found? Can it be adjusted without removing the motor?… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,390 satisfied customers
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,390 satisfied customers
My furnace blower stopped suddenly. I live in about 2,000sq
My furnace blower stopped suddenly. I live in about 2,000sq feet single family home. I called an HVAC technician. They arrived and installed a new motor. However, after they left I run the furnace and… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have an older luxaire commerical furnace blower motor runs
have an older luxaire commerical furnace blower motor runs all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My furnace blower wiil not start. Hopefully. Furnace tries
my furnace blower wiil not start JA: Did you check the furnace's filters? Customer: no JA: Do you plan on doing the work yourself? Customer: hopefully JA: Anything else we should know to help you best… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.