I need a multizone controller that will function with

Customer Question
I need a multizone...

I need a multizone controller that will function with wireless thermostats. The controller energizes the relays in the radiant systems.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

No its just a way to put the thermostats in a more favorable way than the wired ones that I have

Contractor's Assistant: Do you plan on doing the work yourself?

Yes I already have 2 luxpro wirless thermostats

Contractor's Assistant: Anything else we should know to help you best?

Don't think so. The problem with the system that I have now is simply that it controls the furnace not the individual relays from their respective thermostats

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 days by:
1/12/2018
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,414
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation. How many zones? are you controlling zone valves or circulators?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
5 zone valves
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Ask Your Own HVAC Question
Customer reply replied 6 months ago
I’ve run across this before I need a wireless system the info doesn’t specify wireless
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

You connect your wireless EIM to this controller. There are no wireless controllers only wireless thermostats.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Rick, maybe I'm missing something here but there has to be a wireless receiver located near the furnace to pick up the signals from each of the wireless thermostats to activate the appropriate zone valves
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

The EIM is the receiver and you connect it to the ZVC thermostat terminals for each respective zone. When there is a call for heat the ZVC opens the zone valve and calls in the pump and burner.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Pls define EIM. If its what I think my EIM doesn't have outputs for each thermostat. It only drives the furnace
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Equipment interface module. The way it "drives the furnace" is by completing the wireless connection from the thermostat. There are multi zone EIM options. Honeywell site is down. I can't spec anything else. Maybe one of my colleagues can help.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
OK I get that. Maybe I will have to get a new system with these capabilities. I just haven't been able to find a controller with an embedded wireless receiver that would be compatible with the thermostats. Lets see what your other guy has to say. Thanks
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,414
24,414 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trying to use a new T6 Pro thermostat as the Master Zone
Trying to use a new T6 Pro thermostat as the Master Zone stat with an old MM2 Mini Zone Panel. Was hoping that I could create O & B Changeover at the panel using a relay N.O & N.C. & controlling the c… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a pair of Trane TUD100C936BO that are twinned with
I have a pair of Trane TUD100C936BO that are twinned with the Trane factory kit. This causes the fan to start without delay, blowing cold are for first 10 seconds. If I wire with relays can I delay th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Brian, I have a Lennox SLP98V furnace, a XC21 AC unit
Hi Brian, I have a Lennox SLP98V furnace, a XC21 AC unit and a 3 -zone icomfort board with nest thermostats. (dont ask:), I really liked the Nest and didnt know that you cant control the fan speed wit… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a new rheem furnace and a HC-TST412MDMS thermostat but
I have a new rheem furnace and a HC-TST412MDMS thermostat but I have a York Heat pump so heating cools and cooling heats the B termanal is energised in heat and my unit is energised in cool so you see… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
With the help of an HVAC friend I recently installed a WM GGi-8.
With the help of an HVAC friend I recently installed a WM GGi-8. To date he hasn't heard back from WM as to appropriate wiring for use with an indirect water heater, domestic priority. There are separ… read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
I have an electric Goodman Heating and Air system. I replaced
I have an electric Goodman Heating and Air system. I replaced the a daily programmable digital thermostat with non-programmable thermostat RTH111 because of the inside blower fan motor running after t… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
How do I install a Venstar t5800 to control a swamp cooler
How do I install a Venstar t5800 to control a swamp cooler and a gas furnace? I currently have 2 thermostats to control them seperately.… read more
V12Tech
V12Tech
252 satisfied customers
I have an a/c air handler (in the attic) and a furnace (in
I have an a/c air handler (in the attic) and a furnace (in the basement). On my thermostat two green wires are attached to the screw marked 'G', one for the a/c and one for the furnace fan relay. When… read more
V12Tech
V12Tech
252 satisfied customers
I have a Taco sr506 zone controller controlling 4 circulator
I have a Taco sr506 zone controller controlling 4 circulator pumps. I am installing a Honeywell hz432 zone zontroller so that I can use 4 wireless tstats. Where do I attach the 2 wires coming off the … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I am looking for a Honeywell Digital Wireless Thermostat with
I am looking for a Honeywell Digital Wireless Thermostat with relay compatible with a new heating/air conditioning unit for my apartment. It's manufactured by International Environmental Corp. Model #… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a similar question. I have a traditional gas furnace,
I have a similar question. I have a traditional gas furnace, but I also have a wood stove. I mostly heat the house with the wood stove and use the furnace as a backup. When the wood stove is burning, … read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
I have a boiler system with Aquastat L8124A,C relay and three
I have a boiler system with Aquastat L8124A,C relay and three Taco zone valves. There is a circulator pump at the boiler. One zone is radiator and controled by stand alone thermostat and water pushed … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi, I have just had a Day and Night 95% 2-Stage, Variable speed
Hi, I have just had a Day and Night 95% 2-Stage, Variable speed furnace installed. I am using a Emerson blue touch screen Stat, which controls humidity and temp. I also bought a Honeywell Tru Steam hu… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Hi....I have a 5 zone radiant heated slab in my apartment ....we
Hi....I have a 5 zone radiant heated slab in my apartment ....we have a wall mounted Purepro themostat which controls the whole room .....We would like to install themostats in the floor for better co… read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
I have a Lennox G24M furnace with standard Ram control board. The
I have a Lennox G24M furnace with standard Ram control board. The furnace occasionally goes into lockout (4 flashes) and the circulation fan will not operate. The Combustion blower and burner continue… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 6 ton Envision Water Furnace. I have 3 zones each
I have a 6 ton Envision Water Furnace. I have 3 zones each with a basic thermostat. I recently had a failure with one of my pumps and was on resistive heating for a month and only realized there was a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
we are installing vantage control thermostats and they have
we are installing vantage control thermostats and they have a single connection for 24v and a common to power the stat. thing is on this job we have a radiant heating system and a seperate hvac system… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have an TRANE XL15i air heat pump with a 19. kilowatt electric
I have an TRANE XL15i air heat pump with a 19. kilowatt electric backup. The problem I am having is when the unit goes below -17c the fans remains running at a regular speed even when the house temp. … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.