Heat pump blowing cold air, Yes have checked thermostat,

Customer Question
Heat pump blowing cold...

Heat pump blowing cold air

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes have checked thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Fan turns on and thermostat was reset

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
12/31/2017
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,709
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, heat pumps cease heating when its colder than 10 or 20F outside and rely on back up booster heat in that case to heat the house,

Tell me what the outside and inside air temperatures are please., that will let me know if you have booster heat or not and if its working.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
We are in Florida. It’s in the 50s
Customer reply replied 6 months ago
Booster heat not working
Customer reply replied 6 months ago
House is very cold
Customer reply replied 6 months ago
House is 60
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks gently pry the thermostat off the wall, and use a multi meter to measure voltage across the R and C terminals... if you do not have 24vac there, look for a blown 3 amp fuse on the air handlers printed circuit board.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 6 months ago
We have an rc and an rh which one?
Customer reply replied 6 months ago
by terminals do you mean where the wires are or on the back of the unit where the batteries are?
Customer reply replied 6 months ago
Says 2.8
Customer reply replied 6 months ago
Is that 28?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Either Rh or Rc they are jumpered together at the thermostat on most systems

I mean the wires attached to the wall mounted plate that remains after you remove the thermostat.

.

28 volts would be good, its unlikely you have 2.8 volts

Connect Rh, W/E and G wires, that will run the emergency heat

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

You can take them off of the thermostat sub base and twist them together

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Emergency heat also runs cold
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

In that case you do not have any emergency heat installed (common if florida)....if the blower runs we know that your 24volt control circuit is OK. The problem is with the heat pump itself, one of its printed circuit boards or a sensor is bad...

.

If you want help locating a well qualified service outfit, in some areas not common in Florida. tell me which direction you are from the center of the the nearest town and I will see who I can find for you.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I was expecting help with figuring out if I had bad sensors?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

I stand ready and able to help you on an unlimited time basis on any aspect of the system you need help on.

.

Use the add files link to send me a close up, well focused photo of the wiring diagram glued to the heat pumps electrical controls box (inside the heat pump) and I will mark it up with trouble shooting instructions

Add files link is next to your send button

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Another question is why two of three of the limit sensors are not connected? Does that matter? I’ll go take a pic.
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks for the photo's the wiring diagram is too far gone to be useful,... the heat pump itself from the look of it is 40 or 50 years old, way past its normal life span and in a condition that few if any reputable service outfits would accept money for working on it.

You will not be able to find any parts, including defrost controls for that system, the compressor and 4 way valve will already be worn past any hope of efficient operation.

.

I will opt out in case other of our experts here want to get involved..

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,709
9,709 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,709 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We installed a new theromostat. Honeywell RTH6360 but it is
We installed a new theromostat. Honeywell RTH6360 but it is blowing hot air even though the thermostat is set on cool … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
What would cause my heat to come on blowing warm air and
What would cause my heat to come on blowing warm air and then start blowing cold air. It is a Goodman was gas controlling heat. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have Honeywell TH8000 Series programmable thermostats
hi I have Honeywell TH8000 Series programmable thermostats that the fan only blows out hot air. I have tried new batteries, changing the settings and unplugging it still does the same things. I am lea… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I had my AC and propane furnace replaced with a heat pump
I had my AC and propane furnace replaced with a heat pump last year. I would notice when I set the thermostat that once in a while, after the room would initially heat up and the unit would turn off, … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Honeywell thermostat. The air conditioner fan is
I have a Honeywell thermostat. The air conditioner fan is blowing, but the air is not cold. If you physically pull the thermostat out of the wall then replace it, the air blows cold again. I replaced … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Honeywell Chronotherm III unit shows 9642 and 189459D inside. We
Honeywell Chronotherm III unit shows 9642 and 189459D inside. We had a normal yearly service and now it keeps resetting the unit internally to cool when it is set on heat for the bottom setting and th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Goodman Heat Pump - three years old. cools but does not heat.
Goodman Heat Pump - three years old. cools but does not heat. Condenser fan does not come on at 60 degrees outside air temp and unit blows no warm air.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My Air (Heat Pump) Thermostat DICO (type no. 1F89-73) MALF
My Air (Heat Pump) Thermostat DICO (type no. 1F89-73) MALF Light is on and the unit is blowing warm air. What do I need to do? Can I reset? I've tried turning off the breaker and the light stays on. T… read more
SWFLHVAC
SWFLHVAC
67 satisfied customers
I have a Goodman heat pump that is only about 2.5 years old,
I have a Goodman heat pump that is only about 2.5 years old, package unit on roof of a Washington DC row house. #GPH1336H21 AE serial #0904601905 last winter was working fine and this summer it worked… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Two years ago I purchased a 5 ton York Affinity 2 stage compressor/variable
Two years ago I purchased a 5 ton York Affinity 2 stage compressor/variable speed blower Heat pump and AC unit. Heat strips were also installed to defrost the coils in cold weather. Since then I have … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My new Goodman heat pump and furnace is new. The blower fan
My new Goodman heat pump and furnace is new. The blower fan runs 24-7 without shutting off and sometimes blows cold air. My installer says everything is working OK. My electric bill the past month was… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, We have a honeywell thermostat. It says -AC. What does
Hi, We have a honeywell thermostat. It says -AC. What does that mean? It was on Auto and Heat.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Why would my Rheem heat pump blow cold air when set to heat?
Why would my Rheem heat pump blow cold air when set to heat but blow hot when the aux heat kicks in?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
We have a trane weathertron heat pump. The temp is set for
We have a trane weathertron heat pump. The temp is set for 78 but warm air is coming out of the vents and the temp is increasing. We have checked the breaker and reset it. There is nothing dripping ou… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Heat pump will not blow cold air but the fans are running.
My heat pump will not blow cold air but the fans are running. What can I do to make it cold? I reset the breaker, but the fans on the unit is blowing out.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have central AC and oil heat. I am getting cold air through
I have central AC and oil heat. I am getting cold air through the vents and that is all but I have the electric thermoset on heat and cannot turn off the cold air. Any suggestions? I had turned the em… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
We are in a new home this winter. Our Air Handlers heat system
We are in a new home this winter. Our Air Handlers heat system is about 4 y/o. We have our temps set really low due to high electric costs in our area. The problem is as long as the system is turned o… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I HAVE A GOODMAN HEAT PUMP, MODEL AR30-1. iT TAKES A LONG
I HAVE A GOODMAN HEAT PUMP, MODEL AR30-1. iT TAKES A LONG TIME TO RAISE THE TEPERATURE IN OUR HOME. iT BLOWS HEAT OUT VERY SLOW. WHAT CAN WE DO?… read more
Joseph
Joseph
HVAC Contractor
Vocational, Technical or Trade Scho
87 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x