Courier 9300TS LED light on board is dim, not bright, about…

Customer Question
Courier 9300TS LED light...

Courier 9300TS LED light on board is dim, not bright

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About an hour

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
12/31/2017
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,687
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, is that a Carrier thermostat? TS indicates thermostat, but then you said the LED on the BOARD (which is inside the furnace as a rule) is dim.... can you clarify? LED's are either lit or not lit, I guess its possible to have a dim one but in my 58 years in the business all is LIT or not lit, never dim.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

,

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks, ***** ***** between R and C both at the furnace thermostat terminal strip and at the thermostat... if you have 24vac between those two at the thermostat, and the thermostat is dark. replace its batteries if it has any. set the thermostat to heat and up to 90F

IF that fails, jumper R to W1 at the furnace thermostat terminal strip then close the blower door door switch manually, if the furnace comes on then the thermostat is bad.

We can go from there without a time limit.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Ok changed out thermostat code is one long two short
Customer reply replied 6 months ago
I am changing out old Honeywell Progam to new Honeywell Wi-Fi I turned off furnace installed blue wire on furnace panel common. Replace thermostat. Turned on furnace. I reverted back to old thermostat and I have heat. Still cannot figure out why yellow light is dim compared to my other furnace which is bright.
Customer reply replied 6 months ago
Almost gives me the indication not enough power to feed the new thermostat
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

The photo of the yellow led showed a bright LED if that is the one you are talking about.

Did you check power between R and C at the thermostat and at the printed circuit board? tell me which color of wire is attached to C at the thermostat, we can go from there

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It is much brighter in the picture then in real life
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks, ***** ***** be surprised however if the dimness at that level is a sign of trouble.

You still need to use a multi meter to measure the voltages across R and C terminals I need, you can buy a decent one for $30 at any hardware store

Ask Your Own HVAC Question
Customer reply replied 6 months ago
ok have the meter set it for DCV 20, it moves between -1 and +5
Customer reply replied 6 months ago
Now I get a code 24
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

set meter to 0-100 volts AC and measure again

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,687
9,687 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,687 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnace is a lennox furnace automatic gas furnace.... its
My furnace is a lennox furnace automatic gas furnace.... its turns on, the gas flame turns on and then it shuts off … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Comfort Maker N8MPN100F14B1 and I can't get the
I have a Comfort Maker N8MPN100F14B1 and I can't get the heat to come on. The diagnostic LED is off. I have checked the circuit breaker and it is not tripped. I have checked the 5A fuse on the control… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a comfort maker 9mpv100J and the inducer will not come
Have a comfort maker 9mpv100J and the inducer will not come on. I have checked all the seneors and they are fine, new mother board and fan motor. furnace fired up and heated for 2 days then quit. I ha… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an arcoaire furnace and it won't light. Also the led
I have an arcoaire furnace and it won't light. Also the green led goes from bright to dim repeatedly. When I try to start it all inhear is humming… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have bryant furnace model number 359aav036060aaaa.the green
I have bryant furnace model number 359aav036060aaaa.the green diognostic light is flashing and only thing it does is make a humming buzz noise from the cpu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Ignitor glows, gas starts blowing as ignitor is going out,
Ignitor glows, gas starts blowing as ignitor is going out, pilot doesn't light, cycle starts over... Replaced high temp control switch last year. Can u help??… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have an Coleman EVCON Model HW SV9500 / 409290 C HVAC System.
I have an Coleman EVCON Model HW SV9500 / 409290 C HVAC System. The heater will not come on. When I turn it a relay kicks, but nothing happens. The control LED is flashing bright to dim which indicate… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Comfort Maker natural gas forced air heating furnace.
I have a Comfort Maker natural gas forced air heating furnace. Model#C9MVX080J20A1. When the thermostat calls for heat the furnace comes on as it should. It runs as it should and after a few minutes t… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi everyone, Im having an issue with my 373lav horizontal
Hi everyone, I'm having an issue with my 373lav horizontal furnace. It starts up for about 10 seconds and then shuts off with the LED blinking the 21 code. While it's on it the ignitor glows a bright … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our gas furnace isnt starting. The thermostat clicks but the
Our gas furnace isn't starting. The thermostat clicks but the furnace does nothing. No buzzing, no humming, no motor kicking on. If we manually turn the fan on from the thermostat, something turns on … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a armstrong ultra v tech 80 furnance. When I turn the
I have a armstrong ultra v tech 80 furnance. When I turn the heat up the led on the smart valve is blinking bright then dim like it is in the stand-by mode and that is it. The induction fan does not s… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Residential house propane fueled furnace will not fire up.
Residential house propane fueled furnace will not fire up. Components are: Circuit Board: Honeywell ST9141A 1002 Burner Valve: Honeywell "Smart Valve" SV9502H 2707 Hot Surface Pilot/Sensor Assy: Honew… read more
hvac-technician
hvac-technician
Service Manager
Vocational, Technical or Trade Scho
62 satisfied customers
B"H Good Evening, I have a Trane XE 90. It works fine usually
B"H Good Evening, I have a Trane XE 90. It works fine usually but sometimes it blows cold air ( well not really cold but normal air). The ignitor is brand new. When there is a call for heat i hear the… read more
hvac-technician
hvac-technician
Service Manager
Vocational, Technical or Trade Scho
62 satisfied customers
when i turn my air conditioner on my lights dim and then get
when i turn my air conditioner on my lights dim and then get bright/same thing has happend about 4 times,i turned the air off,what is going on,is this pretty common? thank you… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an SV9520M2403 smart valve running my furnace. The furnace
I have an SV9520M2403 smart valve running my furnace. The furnace is not coming on at all though the fan is running. The furnace filters are clean. I have cleaned the flame sensor as well. My thermost… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York package unit that is about 14 years old. No
I have a York package unit that is about 14 years old. No problems until I started it this season. Have had same recurring issue since it started and have had multiple service calls to try and diagnos… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I installed a new dual fuel heat pump this summer. Emergency
I installed a new dual fuel heat pump this summer. Emergency heat is natural gas. A/C works great. Green light on circuit board stay on, but flashes. Exhaust fan doesn't come on. No emergency heat. An… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
t stat calls for heat inducer fan kicks on igniter turns on
t stat calls for heat inducer fan kicks on igniter turns on gas valve kicks on for about 5seconds then turn off right awaycheckd voltage to igniter red 114 to115 volts sometimes when burners do light … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x