No heat. Help! Replaced batteries on thermostat. Turned up…

Customer Question
Hello. No heat...

Hello. No heat. Help!

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Replaced batteries on thermostat. Turned up to 90. It is on heat and the fan is on auto.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

At the furnace.

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/31/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,304
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

Can you get to the furnace and check the control board to see if you have any error codes flashing on it?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
No flashing
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

OK can you get to the thermostat wires?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
You want me to check voltagem
Customer reply replied 3 months ago
Voltage?
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

No I want you to take the Red wire off the R terminal and the White wire off the W terminal and put them together and see if the furnace comes on.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Did I lose you?
Customer reply replied 3 months ago
Ok one sec
Customer reply replied 3 months ago
Touched them together. Nothing
Customer reply replied 3 months ago
You there?
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

Get to the furnace board and see if the fuse on the board is blown or make sure you have power to the furnace. Note there is a delay in responses please do not post until you get one from me. Thanks

Ask Your Own HVAC Question
Customer reply replied 3 months ago
5 amp fuse looks good. Tested with meter. Has continuity.
Customer reply replied 3 months ago
Should I put the red and white wires back into place?
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

You can also confirm you have 24 volts across R to C at the board

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Just a side note. The flame rollout switch has been jumpered. When I remove the jumper the flu motor starts right up along with the blower motor.
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

So it was jumpered previously?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Just replaced the jumper. Both blower stay on now.
Customer reply replied 3 months ago
No flame. No clicking for the ignitor. Wiuld be very hsrd to hear with all of these blowers going.
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

Let me see if another tech can help, I am not sure what unit you have.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Blower motor went off. Induction motor is still on.
Customer reply replied 3 months ago
What? Just gonna dump me? I can tell you the model.
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,315
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, I am another technician, the odds are in the 90%+ range that the printed circuit board is bad..

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Wher can I get one on New Years Eve??
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

After the furnace sits for 10 minutes with the burners and blower off, use a hair drier to warm up the printed circuit board that is mounted on the blower to 130F or so. then try the furnace again, if the main blower does not come on then the board is bad, it has microscopic cracks in it.

You will have to order one online Monday or tuesday, http://www.shortyshvac.com OR call in a local technician who might be able to buy one from his local wholesaler.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

Meantime you can try setting the thermostats *fan switch, to FAN ON... that has a good chance of working

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I can get the main blower to come on. Just no ignition or flame.
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

We can also try hot wiring the blower motor directly to a 120 volt power source, that takes some time and some skill. If you want to try that

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
When I remove the jumper from the flame rollout switch the main blower come right on.
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

.

In that case it could also be a bad ignitor, locate the two igniter connection points on the printed circuit board, and measure for 120vac there, in a time frame between inducer fan running and the time it stops... if you get 120v and the igniter is not glowing, then its a bad igniter... same story on availability.

When you remove jumper from the flame roll out switch you simulated an open switch, that tells the board that the furnace is over heating and turns on the blower. that does not change our diagnosis so far

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Should I leave the flame rollout jumper on or off? Is the normal state open or closed. I'm assuming closed because it has likely bern on here for years working fine.
Customer reply replied 3 months ago
3 wires come from the ignitor/flame sensor and plug into the gas valve. They do not go directly to the cicuit board.
Customer reply replied 3 months ago
Can I light it manually?
Customer reply replied 3 months ago
If I heat up the flame sensor.......will the gas valve open to light the burner?
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

click here please, disconnect the heat and cool motor wires as shown by yellow x's then run the heat wire to the blower door switch.

Heating the flame sensor changes nothing, it does not sense heat it senses the actual flame, that changes is 24vAC input to DC and the board senses that change

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

reconnect the flame roll out switch... is normally closed

If we to too many things at once. we will get all messed up

Earlier you said the burners lit, so we know the ignition is OK

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

When you get the blower running its time to rate my work for the day, that is how the company pays me. Locate the 'Finish and rate your expert' link near the top of your page and click on it.... I will hold the question open to for any follow up needed later when you post back to this thread.

Thanks

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,315
9,315 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,315 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Honeywell T3 thermostat and a heat pump. The heat
I have a Honeywell T3 thermostat and a heat pump. The heat comes on no matter what the setting is. I need help. … read more
hvacdave84
hvacdave84
53 satisfied customers
My furnace is running continually. I have it shut off and it
my furnace is running continually. I have it shut off and it is still running. It is 82 degrees in here. … read more
Phil
Phil
Mechanical Engineer
9,315 satisfied customers
What's code 13 on a Richmond tankless water heater? Just
What's code 13 on a Richmond tankless water heater? … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,304 satisfied customers
I have a luxaire furnace. Installed a new pressure switch
I have a luxaire furnace. Installed a new pressure switch but it still flashes pressure switch open. Blower comes on and line is clear. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
I've lost the code to unlock my Honeywell T4 thermostat?
I've lost the code to unlock my Honeywell T4 thermostat? … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I am trying to put the top of my Honeywell thermostat back
I am trying to put the top of my Honeywell thermostat back on … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
Munchkin boiler not firing. Goes through blower cycle and
Munchkin boiler not firing. Goes through blower cycle and stope with water temp on doisplay. No error codes reported. Unplugged all sensors one at a time and made sure proper error code reported. Al f… read more
Bill
Bill
Service Mgr
80 satisfied customers
I'm trying to troubleshoot an error code on a Evolution Plus
I'm trying to troubleshoot an error code on a Bryant Evolution Plus 90i. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a property where I am having my HVAC completely
I have a property where I am having my HVAC completely replaced. The existing line sets are in the ceiling and it will not be easy to run the new line sets. The contractor is saying that I really have… read more
Phil
Phil
Mechanical Engineer
9,315 satisfied customers
I looking new gas steam boiler, How much Input BTU or Steam
Hi,I looking new gas steam boiler, How much Input BTU or Steam Sq. Ft. Should I need?2nd fl. Slenderized Radiators 9” W X 22” L X 19” H --- 5 tubes and 9 sections4” W X 21” L X 18” H --- 4 tubes and 1… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Our inducer motor p/n 25J1201 needs replacement and my
Our inducer motor p/n 25J1201 needs replacement and my husband ordered one (he is in the industrial heating business). It appears to be just a matter of a few screws and the wire hookup for replacemen… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
York model ZJ036C00A2AAA1C, First time, Yes, How often
How often should this unit be serviced to check refrigerant and replace filter? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
Venstar T1100REC to Taco boiler controller. All I need is
Venstar T1100REC to Taco boiler controller. All I need is the T1100REC to close the loop between R & W on the Taco... how do I configure that?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have just moved into a house and I cannot figure out how
We have just moved into a house and I cannot figure out how to program the thermostat. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
Burnham sea 15 code. All day. Maby. No sea 15 code wating
burnham sea 15 code JA: I'll do all I can to help. How long have you been dealing with this? Customer: all day JA: Do you plan on doing the work yourself? Customer: maby JA: Anything else we should kn… read more
Phil
Phil
Mechanical Engineer
9,315 satisfied customers
Elec furnace- I replaced blower mtr, sequencer, limit
coleman elec furnace- I replaced blower mtr, sequencer, limit switch, transformer, coil elements I tested and found them good working. So I by past thermostat, but still does same thing. Turns on, run… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
Heat would not turn off even though the thermostat was off.
Heat would not turn off even though the thermostat was off. I had my heat set at 67 and I woke up sweating because it was 85 degrees in the upsatairs and it kept getting hotter. It's a 2 zone unit, up… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
AN OLD HONEYWELL MERCURY THERMOSTAT WITH A 1F80-0471 RODGERS
I AM REPLACING AN OLD HONEYWELL MERCURY THERMOSTAT WITH A 1F80-0471 WHITE RODGERS PROGRAMABLE THERMOSTAT. 4 WIRES COMING OUT OF WALL, W,G,Y, R. NEW THERMOSTAT HAS RC JUMPED WITH RH. CANT ADD RED TO TH… read more
Phil
Phil
Mechanical Engineer
9,315 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.