Hi my carrier furnace...

Hi my carrier furnace is blinking 33 and I don’t know how to fix it

Contractor's Assistant: Did you check the furnace's filters?

Changed them out earlier today, previously it was rough

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Not that I know

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/31/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,286
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

This is a thermal rollout issue. There are high limit safety thermostats that are around the burner housing area that can trip open if they fail or the unit is overheating. Some of these have reset buttons on them that you can manually press down to reset while others do not. The ones that do not either are one time limits or are limits that are suppose to manually reset when cooled down. Now that does not always happen when they go bad so you will have to check them for continuity with an ohm meter across the two leads going to them. If you do not pwn a ohm meter you can physically bypass each rollout to make sure it is good by connecting the two wires to each rollout sensor together to see if the unit will then operate. Now once you have found the bad one you can change it out or reset it and then you should check your furnace filter for blockages and make sure you main furnace blower is running to speed. These two things can cause a unit to overheat and trip one of these rollout sensors. Mosts units have 3 of these devices and here is a link to what they can look like on your unit.

CLICK HERE

CLICK HERE

CLICK HERE

Happy Holidays..All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Do I shut off power to the furnace when resetting these?
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

You can but do not have to.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Is there a way to reset the second rollout image you sent me. I have 2 of the first image and 1 of the second. I do not own an ohm meter and not quite sure what you mean by bypassing the rollouts
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

Just remove the two wires to any that do not have buttons and interlock the wires together and tape them so they stay connected until you can get a new one. If you can not interlock them use a paperclip to connect the two wires and tape them then try it.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Oh gotcha
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

No problem!

All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I bypassed the sensor and there is smoke in the house and the fire alarm went off
Customer reply replied 3 months ago
Is something in the vents that is catching fire?
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

Yeah something is burning up not good you should call a tech or the fire department if something is in the vent possibly burning. I have no idea what would be in the vent, but something is really wrong with the unit.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Damn okay thank you
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

Yeah call a tech out for sure you got a bigger issue for sure. Do not risk burning your house down.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 3 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
Was this answer helpful?
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,286
18,286 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Carrier furnace is blinking 2 fast then 4 slow and the
carrier furnace is blinking 2 fast then 4 slow and the blower will not turn on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Furnace blower will kick on for a minute or two then stop.
Furnace blower will kick on for a minute or two then stop. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Have a carrier furnace, the pilot light is on. The burners
Hi, have a carrier furnace, the pilot light is on. The burners used to come on & off on their own (not in response to the Thermostat). Then they stopped responding all together. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Carrier furnace igniter doesn't spark. It was working but
It was working but today the electronic igniter doesn't spark … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My carrier furnace model 395baw036060. There is a clicking
there is a clicking sound and the flame comes on but goes off and it keeps clicking… read more
Bill
Bill
Service Mgr
79 satisfied customers
I have a Carrier furnace funace, and it's not blowing warm
Hi I have a Carrier furnace funace, and it's not blowing warm air … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace. Igniter comes on, but no flame. There was
Carrier furnace. Igniter comes on, but no flame. There was an electrical issue earlier today on the electric company's side of the meter. It has been repaired. Furnace was OK prior to that. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace rated at 1865 cfm was recently installed in
carrier furnace rated at 1865 cfm was recently installed in Jan 2018. Total cfm for all vents is 1056 cfm. heat distrbution for 16 vents ranges from 69 to 95 cfm. what could be the problem? Please adv… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why is there water under my furnace? Filter is clean and
humidifier is off and not leaking, AC is off, quite cold outside, no snow on chimney… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rheem furnace blower runs on low but will not run on high
rheem furnace blower runs on low but will not run on high furnace goes off on high heat limit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,676 satisfied customers
I have a Carrier furnace model 58CTA090-12114 that was
I have a Carrier furnace model 58CTA090-12114 that was installed in 2005,I am currently having an issue with it when it is called upon for heat, it will start the burner sequence with the ignitor glow… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,286 satisfied customers
The ignitor to my Carrier furnace will not trigger so no
Hi Pearl. The ignitor to my Carrier furnace will not trigger so no heat can enter the house. I've manually reset the limit switch and cleaned the flame sensor and was looking for suggestions on what t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Getting a code 33 on my carrier furnace intermittently. And
getting a code 33 on my carrier furnace intermittently … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier pad needs to be changed. Is that something easy to do? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,676 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
HVAC TECH
18,286 satisfied customers
My Carrier Furnace goes on but will not stay on,the red
My Carrier Furnace goes on but will not stay on,the red blinking code is 3blinks and pause,3 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x