I'm trying to install a new thermostat. My old one has wires…

Customer Question
I'm trying to install...

I'm trying to install a new thermostat. My old one has wires that go to the B and to the O circuit, the new one only has an O/B. For what its worth, the fan and AC come on, the heat does not.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yep

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
12/31/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,641
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
No worries, thanks.
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

OK if your old one had a separate O and B you would need one with that or can only connect one or the other to the O/B terminal for heating or cooling. You need to put one on there likely Orange to the O/B tape the other one off for heating. If that is not it try the other one. It will be one or the other. Then in the summer you would have to swap them.

Happy Holidays..All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 5 months ago
The new thermostat is a Honeywell rth6360 if that helps
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

If old one had a separate O and B you normally need a thermostat like that or you will need to just put one wire to the O/B for heat then swap it to the other in the summer for cooling. I would tyr one of those wires to it for heat and whichever works leave the other taped off until summer then swap it.

Happy Holidays..All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I have tried them both, neither works.
Customer reply replied 5 months ago
You still there?
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

OK if neither work do you have the thermostat set to the right system and crossover setting right for the unit?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
There were no options, it is for a heat pump.
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

What is the make and model of the thermostat you are installing?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Honeywell rth6360
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

Do you have option 218 set to 1?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
What is option 218?
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

That is the crossover valve setting you need it set to 1 not 0

Ask Your Own HVAC Question
Customer reply replied 5 months ago
How do I do that?
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

CLICK HERE setup starts at page 8 you have to have it all setup correctly or it will not work for the heat pump.

Happy Holidays..All I ask is please use the....FINISH BY RATING link at the top your page to select a 5 STAR RATING before leaving today....this is important for my status on the site plus without a rating I will receive ZERO credit(NO PAY) from the site for assisting you. Also rating now does not close the question out and you can come back anytime for FREE right here to me......Happy Holidays!

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I cannot get to system set up options. How do I do that?
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

Go to page 14....CLICK HERE it is right on page 8

Ask Your Own HVAC Question
Customer reply replied 5 months ago
That didn't get it either.
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

Then I would say the thermostat is faulty you have to get into the installers setup for a Heat Pump to set that crossover correctly or it will not work and only cool. You may have just got a bad unit as there is no other reason it would not go into the mode are you sure you are doing exactly what it says on page 14? If so I would say it is just a bad thermostat.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
After playing around with a couple of wires it now turns on. But it's blowing cool air out.
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

That crossover valve is just not set right for heat it defaults to 0 for cool that is the issue.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 5 months ago

Hi there,
I was just touching base with you because I have not heard back from you and the question is still open and unrated, I am not credited anything until a good star rating is supplied I would really appreciate it if you could do that thanks!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,641
18,641 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My contactor is not pulling the plunger in. started 2 weeks
started 2 weeks ago, ac was working intermittent. Last 2 days, no ac at all. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell thermostat in a rental home. It has a
I have a Honeywell thermostat in a rental home. It has a triangle with a !. What does this mean? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Does a Trane TCC036F100BD A/C unit have an air mover with a
Does a Trane TCC036F100BD A/C unit have an air mover with a belt, or is it a direct drive blower? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Lockout code 81 on a carrier infinity system. Few minutes.
lockout code 81 on a carrier infinity system JA: I'll do all I can to help. How long have you been dealing with this? Customer: few minutes JA: Do you plan on doing the work yourself? Customer: if I c… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Gibson furnace, split system model #JS5BD-030KA. ac was
Gibson furnace, split system model #JS5BD-030KA. ac was running fine, putting out cold air but now the air is luke warm. What should I check … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a CGP20TB have replaced the thermal couple. the pilot
i have a CGP20TB have replaced the thermal couple. the pilot does stay lite every thing else checks out. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How do i remove the system malfunction call tech notice. It
How do i remove the system malfunction call tech notice … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have an RTH6350 D1000 in combination with a heat pump
Second opinion] Hi I have an RTH6350 D1000 in combination with a heat pump (Unico) … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Honeywell thermostat seemed to be stuck...heat is on and
My Honeywell thermostat seemed to be stuck...heat is on and rising even when I've programmed it for AC at 62 degrees. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a rite temp thermostat in the condo I purchased. I
Hi I have a rite temp thermostat in the condo I purchased. I can't get it to cool the house off … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Not sure how this works but I have a Amana 5000 btu window
not sure how this works but I have a Amana 5000 btu window are unit and the room thermostat reads now in Celsius but the ac cool thermostat reads in fahrenheit so with the room temp reading 38 the a/c… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,641 satisfied customers
Can a 440 volt wall heater work in a building using 408 volt
Hi, Can a 440 volt wall heater work in a building using 408 volt system? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I'm getting an E2 error code on my thermostat and my A/C
I'm getting an E2 error code on my thermostat and my A/C isn't working. What's up with my system, never got a manual when I moved in, so I have no idea what the code means. How do I clear it and get m… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Might you be able to assist me in setting up the wires for a
Might you be able to assist me in setting up the wires for a nest t-stat? I'm converting over from an older Lennox icomfort unit. Heat pump is CBx32MV-060-230-6-06… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,641 satisfied customers
Thermostat will not givereading, screen shows blank. Changed
Thermostat will not givereading, screen shows blank. Changed batteries but it still does not show a reading. Air conditioner runs constantly, cannot stop unit without pulling thermostat from unit, ple… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Trane Air Handler Model 4TEE3F49A1000AB Motor not starting.
Trane Air Handler Model 4TEE3F49A1000AB Motor not starting … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a d708bp setup using the built in pump. The pump
I have a d708bp setup using the built in pump. The pump stopped working and had to empty bucket manually. Now it sounds like pump is running continuously, but not draining … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have a UAPC-024JAZ, getting 25AC signal from upstairs,
Have a UAPC-024JAZ, getting 25AC signal from upstairs, change relay and start cap. TS, 26AC getting through the switch attached to compressor, but not through the switch that has a coiled tube attache… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x