5 flashes on my gms90904cxa furnace and I hear a loud

Customer Question
5 flashes on my...

5 flashes on my gms90904cxa furnace and I hear a loud humming because the blower motor is NOT turning on

Contractor's Assistant: Did you check the furnace's filters?

Took it out

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, if I can.

Contractor's Assistant: Anything else we should know to help you best?

I watched a YouTube video which showed me to turn off the power to the unit and try and turn the actual fan by hand. The fan kind of fellwhen I attempted to turn it

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/30/2017
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,726
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, tell me please if the burners ever fire, or not... even for a brief time.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
There are 4 flashes on my gms90904cxa furnace. Blower motor not blowing. I turned off power and tried to turn the fam by hand and the fan fell. It's just rattling around FREELY now inside that compartment. I won't turn the power back on now.
Customer reply replied 6 months ago
There is no wiring diagram inside either of my furnace doors (upper or lower)
Customer reply replied 6 months ago
The induced motor starts, the burners fire up, then 30 seconds later, very loud humming and blower motor doesn't move
Customer reply replied 6 months ago
Hello? Are u there?
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

I am here, but I come and go to handle many things at once

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

It is most likely that the blower motor is bad, or its run capacitor is bad.

Tell me if you can spin the blower freely by hand, if its tight, the blower motor needs to be replaced.

.

If it spins easily then replace its run capacitor ($7 item) its the size of a cigarette package made of metal like a tin can, with two brown wires attached. IF you do not see that, then you have a different type of motor that we can discuss next

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Did u receive my other replies? And what do you think is the problem? By looking on YouTube, it looks like it's the motor but I'd like confirmation or what else it could be.
Customer reply replied 6 months ago
I tried to spin it by hand and it wouldn't move, instead it kind of fell off inside the compartment
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

You found the problem, both the motor and the blower hub are broken, best replacement is the entire motor and blower assembly.

You can order it at the link below in most cases

http://www.shortyshvac.com

The will be open Monday or Tuesday.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

The blower assembly slides out of the furnace after you disconnect its wiring on two rails, there is a stop screw at end of each rail,. remove those and the blower slides out.

If you are lucky and the motor is not over 5 years old, you might get by just replacing the squirrel cage blower wheel itself... you can attach photo's by using the 'add files' link next to your send button. I will assess that for you

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,726
9,726 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,726 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Im getting a two flash code ( primary limit switch open ) on
Im getting a two flash code ( pri***** *****mit switch open ) on my board in my furnace. What does that mean? … read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
My fan is not turning on, just now, yes, model TDDO 60C936A1
My fan is not turning on JA: I'll do all I can to help. How long have you been dealing with this? Customer: just now JA: Do you plan on doing the work yourself? Customer: yes JA: Anything else we shou… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
The ignitor on my furnace does not ignite. Need help to fix it!
I just replaced my ignitor and my lennox G27 furnace still won't ignite. I checked the furnace filters, and cleaned the flame sensor. The ignitor doesn't even turn pink or warm up at all when I switch… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
My furnace has been humming before the pilot lights-call
My furnace has been humming before the pilot lights-call for heat loud hum then turns off. Tried it on fan only and same thing happened. So I figured it needed a new fan blower motor and capacitor as … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I turnen on my hvac unit yesterday and realised that the fan
i turnen on my hvac unit yesterday and realised that the fan didn't run. It took me couple hours to find that out. The fan motor is hot. Is my condensor affected now as well. Thanks… read more
EnviroDesign
EnviroDesign
Bachelor's Degree
43 satisfied customers
just got back from a couple days vacation. My goodman furnace
just got back from a couple days vacation. My goodman furnace is not firing. House is cold. The indicator light was flashing 3 times. I turned the power switch off and then on. There was a buzzing noi… read more
Appliance Guru
Appliance Guru
18,166 satisfied customers
I've got a Rheem RCFA-HM3617AC HVAC unit - 6 years old. Decided
I've got a Rheem RCFA-HM3617AC HVAC unit - 6 years old. Decided one morning to not heat. Since I have two of the same units, I took the thermostat from one and put it on the non-functioning one. Still… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Hello, My husband and I bought our condo at the end of summer
Hello, My husband and I bought our condo at the end of summer in 2013 and now that we are using heat, we notice the system is VERY loud the entire time it is working. Like a fan on full blast times 5.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi,My heating/cooling system is about 15 years old. Its
Hi, My heating/cooling system is about 15 years old. Its made by American. My heating system was working fine, but my thermostat for some reason would not turn on my ac unit. So, I decide to replace m… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
We have a Lennox G16Q4/5-125-1 furnace/AC unit. Sometime today
We have a Lennox G16Q4/5-125-1 furnace/AC unit. Sometime today the unit failed to come on when the thermostat told it to. The power to the blower motor kicks on, but the blower doesn't turn. Instead t… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
very loud humming, stops after 5 mins. then starts humming
very loud humming, stops after 5 mins. then starts humming loudly again. no heat. 3 flashes diagnostic on newer keeprite.… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
Bryant Plus 80 series B 311aav - Intermittent loud humming
Bryant Plus 80 series B 311aav - Intermittent loud humming when thermostat calls for heat - the blower was sluggish to come up to speed. Auto shutdown and Fault code 32. (Guilty dog - I neglected my m… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Merry Christmas! In South BEnd IN, Ive an Armstrong (Air
Merry Christmas! In South BEnd IN, I've an Armstrong (Air Ease Series), 200000 btu--I'm a new owner in this 1929 house, so do not know much history on the furnace. August 31st it was reviewed as in go… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
We have a Heil central air unit which wont turn on. The battery
We have a Heil central air unit which won't turn on. The battery in the thermostat died, and once I replaced batteries, the therostat came back. I turned the degree setting below the room temperature,… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
When the thermostat is signaling my home furnace (Carrier)
When the thermostat is signaling my home furnace (Carrier) to come on, the burners come on, however the hot air is not pushed out of the furnace to be distributed throughout the house; you only hear a… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
Ruud Silhouette-Two furnace (UGPH-10EBRJR) suddenly started
Ruud Silhouette-Two furnace (UGPH-10EBRJR) suddenly started making extremely loud humming noise as if fan is stuck. We turned it off completely, but it's cold here. Is there any danger in turning it b… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
motor kicks on and hummms but wont actually come on! We replaced
motor kicks on and hummms but won't actually come on! We replaced filter and fuse. also for the last few weeks it has been struggling to come on as indicated by loud noise… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
i own a luxaire hvac system itis about 25 years old themodel
i own a luxaire hvac system itis about 25 years old themodel is 2HL06502506A WHEN IT SHUTS DOWN IT MAKES A LOUD CLICK JUST BEFORE IT SHUTS DOWN WHAT CN I DO THE MOTOR STAARTS UP QUIET BUT A CLUNT WHEN… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.