Heil electric furnace model EF08B1500A3 no heat. Fan runs,

Customer Question
Heil electric furnace model...

Heil electric furnace model EF08B1500A3 no heat. Fan runs, thermostat works properly.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filter clean. Thermostat shuts off fan when set a few degrees below current room temp, and turns system on when set to a few degrees higher than room temp.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

That’s it.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 31 minutes by:
12/30/2017
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,721
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

So far it sounds like a bad heating element sequencing relay or a bad heating element.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
It’s pretty tight in there. The circuit board is mounted on the top. The furnace itself is horizontally mounted, air flow is left to right while looking at the wiring diagram. The 5-amp automobile-type fuse on the circuit board is not blown. I hope that the photos are suitable. Thanks for your help.
- mark
4734080F-BCCC-4C5D-82BC...jpeg473408...jpeg2B3ED166-FEC2-4EE8-8B52...jpeg2B3ED1...jpeg03EA2358-2E16-4CA1-B514...jpeg03EA23...jpeg8AD406DE-75B8-4ADD-95B0...jpeg8AD406...jpegF0585BE2-17E9-431C-9F26...jpegF0585B...jpeg
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks, click here please. let me know what you can discover, we can go from there

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,721
9,721 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,721 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Heil split system ac which has not been blowing
I have a Heil split system ac which has not been blowing cold air the last few days(or at least not enough to cool the house). I cleaned the condenser outside, changed the filter(which was actually st… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Heil furnace about 5years old. Thermostat will kick
I have a Heil furnace about 5years old. Thermostat will kick on the Fan and the AC when set to,but furnace will not kick on when set to heat. thermostat clicks but nothing turns on at furnace. LED lig… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
yesterday morning about 6 am, the heat pump fan was running
yesterday morning about 6 am, the heat pump fan was running blowing cool air and the indoor temp was 68 degrees and the thermostat was set at 71 and the outdoor temp was about 36 degrees. We cut the p… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, My Heil 4 ton heat pump periodically engages heat strips
Hi, My Heil 4 ton heat pump periodically engages heat strips for no discernible reason. example scenario: 60 degree outside temp, freon level/pressure verified to be correct, thermostat room temp 65, … read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Should the outdoor compressors come on one the heat is turned
Should the outdoor compressors come on one the heat is turned on in the house? Currently they are not running, but the heat is on and it is blowing mostly cold air.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Totaline wireless thermostat (P474-1100RF) that controls
I have a Totaline wireless thermostat (P474-1100RF) that controls our upstairs heat pump. Recently, when the exterior heat pump turns off, the fan continues to run resulting in cold air being blown in… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Now, I have another problem with the furnance heater. The flame
Now, I have another problem with the furnance heater. The flame does not stay on until the thermostat temp. is met. In fact, the furnance will not start if the thermostat setting is more than a few de… read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
Heil high efficiency furnace from 1988 did not turn off with
Heil high efficiency furnace from 1988 did not turn off with thermostat automatic set-back last night. Ran all night with temps outside at about 30 deg F - house temp hit 82. Fan seemed to be running … read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Dear Sir, We have a ritetemp thermostat which controls the
Dear Sir, We have a ritetemp thermostat which controls the heat in our house. When the room temp goes below the set temp, the thermostat switch clicks on, switches on the fan and then a few seconds la… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a lennox furnace. The problem started with the temp
I have a lennox furnace. The problem started with the temp falling 5 or 6 degrees below the set temp before the furnace would start. (the instructions for the digital honeywell thermostat said one deg… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
My Heil furnace(forced air) is turning on & off to often before
My Heil furnace(forced air) is turning on & off to often before it reaches it's set temperature. Example:Was set for 66-When temp. was at 65, I turned it up to 68 degrees. Furnace turned on then went … read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Hello, I have a Trane XL80 that appears to be running fine.
Hello, I have a Trane XL80 that appears to be running fine. When it reaches the desired temperature set by a programmable thermostat it shuts down as it's supposed to. The problem somes when the tempe… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Brand new heat pump, package unit, reaches room setting, and
Brand new heat pump, package unit, reaches room setting, and doesn't shut off, and room temp never gets higher than what is set no matter how long unir runs. lower the setting, the unit shuts off and … read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
my thermostat is set and 60 degrees and the temperature keeps
my thermostat is set and 60 degrees and the temperature keeps going to 80 degrees I have oil heat furnace… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Rheem RGPH-10EAMER furnace shuts down while the thermostat
My Rheem RGPH-10EAMER furnace shuts down while the thermostat is still calling for heat. It starts again right after it shuts down and finishes heating to the called for temperature. I thought it migh… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a forced hot air, gas fired furnace controlled by an
I have a forced hot air, gas fired furnace controlled by an analog thermostat, like the one posted on your web-page. When I set the temperature above what the room is at expecting the heater to come o… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I just got a house with a two year old gas forced air furnace
I just got a house with a two year old gas forced air furnace which is in an unheated attic. It rarely brings the temperature up to the level set on the properly programed digital thermostat. It doesn… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
I recently had a problem with my standing pilot on my york
I recently had a problem with my standing pilot on my york furnace blowing out do to backdraft. I had a tech come in and install a new honeywell electronic ignition and a new fan limit swith. since th… read more
Rick
Rick
Supervisor
24,233 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x