I live in a Condo and my heat is inadequate. I have a pyrometer and have measured the temperature at each of the baseboards and reading no more that 106 degrees. The house plumber advised that the boiler is at 189 degrees and nothing is wrong. He also advised that while there are 25 units rhe system has only one circulator, it is zone controlled. Am I right in assuming that the baseboatds shoukd be much hotter

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The thermostat was replaced and symptom were the same.

Contractor's Assistant: Do you plan on doing the work yourself?

No, The boiler is in a locked room and they will not let me or any plumber I was to Hire to gain access. I would like to have the zone valve checked.

Contractor's Assistant: Anything else we should know to help you best?

I would like to know what the temperature of the baseboards should be when the thermostat is caling for heat.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
12/30/2017
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,878
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, on virtually all such systems the base boards should run at the same temperature as the boiler.\.

.

It is unlikely that boiler is set to run at 189F that is most likely the manually resettable boiler high temperature safety limit switch... and the boiler control itself is like set to 120F in an effort to save money and you are therefore measuring 106F at your radiators.

.

You should know that if the building runs its boiler below 120F as some do, condensate from the natural gas combustion will rot the boilers heat exchanger out... more than a few operating engineers make that mistake.

I think that is the situation... If I am wrong then its likely that there is air trapped in your radiator that is vapor locking the hot water flow.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,878
9,878 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,878 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I live in a Condo and my heat is inadequate. I have a
I live in a Condo and my heat is inadequate. I have a pyrometer and have measured the temperature at each of the baseboards and reading no more that 106 degrees. The house plumber advised that the boi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a bedarus oil fired hot water baseboard heating
I have a bedarus oil fired hot water baseboard heating system. One of the zones is 10 degrees colder than the thermostatic setting. Do I have a pump motor recirc problem… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have a Weil Mc lain series 3 boiler, this is our first
We have a Weil Mc lain series 3 boiler, this is our first heating season ( moved in 8/2015) and the thermostat is set to 68 degrees and does not rise above 63 degrees. We have hot water base board hea… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Vaillant F100-40 furnace. I'm wondering what the
I have a Vaillant F100-40 furnace. I'm wondering what the maximum temperature I can set the hot water too. It is currently at 180F but by the time the water gets to the rooms it is 105F in the baseboa… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
new weil-mclain boiler installed Oct 2014. 3 zones: kitchen, DR and 2nd floor. When 2nd fl
new weil-mclain boiler installed Oct 2014. 3 zones: kitchen, DR and 2nd floor. When 2nd floor kicks on K zone drops at least 3 degrees then takes 2-3 hours to rise to temp. K set @ 63 over night, 65 @… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Burnham Series 2 (model "") gas-fired boiler. When
I have a Burnham Series 2 (model "B") gas-fired boiler. When the temperature in our area gets below 25, the system cannot keep up. I do not believe it is air bound. The boiler appears to be firing fin… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My home has traditional gas-fired steam heat which is
My home has traditional gas-fired steam heat which is controlloed by one thermostat. Whne we added two rooms, we drew water off the boiler and circulated that water to baseboard heaters. The baseboard… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Our small condo building recently installed a Burnham Alpine
Our small condo building recently installed a Burnham Alpine 399 boiler. Problem: When it's between about 52 and 59 degrees (we have the outdoor temp sensor set at 59 degrees), it gets too hot; unit o… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I hope you can help me get the right answers...I work for a
I hope you can help me get the right answers...I work for a commercial heat and mec. contractor but I am not a plumber or pipefitter and the guys I work with aren't familiar with residential systems. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,878 satisfied customers
How do you control zones on a Vitodens 200-W boiler Two out
How do you control zones on a Vitodens 200-W boiler? Two out of three zones of our new boiler are putting out good heat and match the temperature set on our thermostats for those zones. The third zone… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My husband just replaced thermostats (hot water boiler system
My husband just replaced thermostats (hot water boiler system 6 thermostats) and it's heating tot high. Have the thermostat set at 60 and it's registering at 75 and the baseboards are still hot. Cud i… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We like to sleep in a cool bedroom and use to turn the thermostat
We like to sleep in a cool bedroom and use to turn the thermostat down to 62 at night. We installed a Knight Lochinvar boiler heating system. When we turn the thermostat down at night it takes 7 to 9 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an Honeywell Magicstat 3200 thermostat that seems to
I have an Honeywell Magicstat 3200 thermostat that seems to have a mind of its own.No problems with it over the past 4 years but in the past couple of days it will run the temperature up to 77 when it… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
we have a hydronic heating system that works of our water heater
we have a hydronic heating system that works of our water heater and it is not circulating the water trough the base boards. The circulating pump is working fine.the water pressure is at 15lbs. Do you… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Have a newly installed Buderus G115 boiler. Boiler water temperature
Have a newly installed Buderus G115 boiler. Boiler water temperature isn't getting hot enough to satisfy the thermostats. We were told we could leave the thermostats on 68 year around and not have to … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have gas hot water baseboard heaters. They are very old...Im
I have gas hot water baseboard heaters. They are very old...Im guessing over 20 years old. I installed an electronic thermostat 5 years ago. My problem is that even when I have the heat switched to "o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My house is about 10 years old and I have A White Rodgers model
My house is about 10 years old and I have A White Rodgers model no 7904 thermostat. At the end of the heating season I will have the thermostat set at maybe 60 degrees and the house inside temperature… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I got 4 zones off my boiler. One wont kick on. I tried turning
I got 4 zones off my boiler. One wont kick on. I tried turning the thermostat up, but the baseboard doesn't heat up. I felt the pipes leading to that zone, and they are only warm for about 6-8 feet. T… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less