We have a York model YP9C100C16MP12CB, with a heat pump.

Customer Question
We have a York...

We have a York model YP9C100C16MP12CB, with a heat pump. When the outside temperature is around 30 degrees or less, our unit is calling for the heat pump and blowing cool air. Is there a way to change the set points so that only the furnace comes on when it’s that cold?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes, the tstat is set correctly and the filters are clean. We’ve had the unit 2 1/2 Year’s and it’s always been a problem. We have indoor and outdoor faults constantly. Also we have changed out the thermocouple 3 times in 2.5 years.

Contractor's Assistant: Do you plan on doing the work yourself?

Ok service provider can’t seem to fix it. They claim they have to call tech support at York and sometimes wait her at the house and can’t get thru to them for 2 or 3 hours. The latest thing they did was to turn off the fancy tstat it originally had and just hang a Honeywell tstat from the door of the mechanical closet, thereby disabling the heat pump and that’s when the latest thermocouple had to be replaced.

Contractor's Assistant: Anything else we should know to help you best?

I think that’s all. I do have pictures on the near constant faults if that would help but I’m not sure how to upload them to you.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 hours by:
12/31/2017
HVAC Technician: airheatman, HVAC Technician replied 6 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified

This is going to be a complex troubleshooting issue rather than a simple question and an answer.First let me say it sounds like you have more than one problem.If your hvac guy is a York dealer he should have a direct number to call his field manager while onsite.

Together we can figure this out and try to get to the bottom of the problems but as stated is not going to be a brief one or two correspondence answer.After the first hour of guidance I will present an additional service offer so you can accept and compensate me for my time .

I will start by answering the initial question.Afetr rating that answer we can continue to get to the bottom of this or you can get a York dealer who knows what he is doing.

YES.Your thermostat should have settings which can adjust that will lockout the heat pump below a given temperature as well as lock out the furnace from coming on at warmer temperatures

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
9,213 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a york yp9c080c16mp12ca furnace. When the call for
I have a york yp9c080c16mp12ca furnace. When the call for fan is applied, the EAC relay is clicking on and off, and when it does, the STATUS LED blinks red momentarily. I dont see what should be a cod… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a venstar T5900 and the heat pump setting are
I have a venstar T5900 and the heat pump setting are disable. Even if the jumpers at the back are set to HP … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
I had a contractor convert my 800 sf garage into a family
I had a contractor convert my 800 sf garage into a family room and expanded our existing master bedroom to 850 sf and added a new 500sf closet directly above the family room. The HVAC contractor put i… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I was sustituted a 3ton heat pump air handler instead of a 2.5 ton. I did not get the heat
I was sustituted a 3ton heat pump air handler instead of a 2.5 ton. I did not get the heating unit, wron one sent for only 6kw instead of 15 kw. the only circuit board in it is the fan board and 24 vo… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
I am replacing an older thermostat on a Heat Pump system that
I am replacing an older thermostat on a Heat Pump system that also has Emergency heat and perhaps might have a humidifier (as I see it attached to the heat pump). The old Tstat is a Carrier HH07AT171 … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
We are currently shopping to change our havoc system. Our system
We are currently shopping to change our havoc system. Our system is approximately 27 years old, we received quotes from three different suppliers. We livening Montreal quebec, our homers as split leve… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We have an older (approx.. 25-30 years) Carrier heat pump.
We have an older (approx.. 25-30 years) Carrier heat pump. It's one of the large bulky beige units. Can't tell you the model # XXXXX it's faded and can't read. It is Nat gas only for heat and electric… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I have a York (Honeywell) heat pump with strip heat emergency
I have a York (Honeywell) heat pump with strip heat emergency heat. New thermostat is Vision Pro 8320 3h/2c. Need where to put wires from heat pump , W,R,O,B,G,Y are wires from heat pump. Old thermost… read more
joeydelia
joeydelia
HVAC-R Tech supermarket refrigeration
182 satisfied customers
I have a thermolec b15m standard boiler. A recent storm left
I have a thermolec b15m standard boiler. A recent storm left us with a power outage. Once the power was restored the boiler seemed to be constantly running. It will provide heat only when we turn up t… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Hi. I need to install a Honeywell RTH7400D programmable thermostat.
Hi. I need to install a Honeywell RTH7400D programmable thermostat. I have a York heat pump with an air handler. On the original thermostat, I had a Yellow wire (Y), Blue (B), Red (R), Green (G), Oran… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I am a realtor and sold a home with a home warranty for the
I am a realtor and sold a home with a home warranty for the rheem system. It was checked and in good working order just before closing by Advantage Mechanical HVAC. Now the company allowed to service … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Rheem PTG2-42PVP water heater worked great for 28 months, then
Rheem PTG2-42PVP water heater worked great for 28 months, then would intermittently fail after approximately 5 seconds and show error 12. After some research, I determined that the flame sensor(s) sho… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I just self installed a Hunter touch screen thermostat (model
I just self installed a Hunter touch screen thermostat (model 44860)and as the directions suggested I marked all the wires . I connected those wires to the appropriate terminals on the new tstat. The … read more
ComfortZone
ComfortZone
Associate Degree
515 satisfied customers
trane summit--vav box is locked on 75.3 no matter what i do--changed
trane summit--vav box is locked on 75.3 no matter what i do--changed tstat-enable,disable thumbwheel-changed occupy,unoccupied--rewired and achnged connectors at board--board has power com light blink… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have just recently (about 4 months ago) had the thermostat
I have just recently (about 4 months ago) had the thermostat on my central ducted heating replaced. The new thermostat is the HONEYWELL FOCUS PRO TM 6000 (and it was installed by a technician recommen… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have two questions. 1. During the heating season, is it
I have two questions. 1. During the heating season, is it best to run with the fan in the "on" position all the time? 2. Where can I find the wattage ratings for my York heat pump? Thanks… read more
Bill
Bill
High School or GED
318 satisfied customers
I have a carrier thermostat. Worked fine until the recent cold
I have a carrier thermostat. Worked fine until the recent cold snap. It works fine until about 12 at night. It wont kick on the furnance. It is on the heat setting and I rasie it about 1 to 2 degree a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Hello, Have a York heat pump in N. E. Ks. condensor is E1FB036S06A
Hello, Have a York heat pump in N. E. Ks. condensor is E1FB036S06A SN EMAM411412 with air handler F1SA036R06FFA SN EBRS050013. What is the minimum temp to set the heat pump lockout ie switch to coil h… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x