Where can i find a schematic for a three wire pilot and gas valve. some idiot cut the green wire and the yellow wire between the gas valve and the ignitor module (spark) and tied all four loose ends togather.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About two years. the same idiot removed all the paper inside the furnace the problem is getting the blower to come on.

Contractor's Assistant: Did you check the furnace's filters?

A call for blower from the thermostat brings on the ac condenser. moving the wire to gc gets the blower, but no auto blower. a jumper from w to gc works but only in the winter. also the blower goes off and then after a few seconds comes back on. if i cant get a handle on this, i think i am going to get a drinking problem. its making me nuts

Contractor's Assistant: Do you plan on doing the work yourself?

I am the only ac tech in a small town. all my competitors got old and died, except for special ed. if it wont cool add more freaon says ed.

Contractor's Assistant: Anything else we should know to help you best?

I just need a schematic for the pilot, spark ignitor, and gasvalve. furnac has no combustion blower.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
12/30/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 8 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,362
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here. What is model number of unit. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The problem is after replace the control board, I jump R and
the problem is after replace the control board, I jump R and W, still nothing happen, the inducer blower should run… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a AIRQUEST natural gas furnace that is about 20 years
I have a AIRQUEST natural gas furnace that is about 20 years old model #NNCU075AG01. The blower would come on when the thermostat called for heat but only cold air came out. When I turned the thermost… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
Need a wiring diagram for a Lennox mid-efficient furnace with
Need a wiring diagram for a Lennox mid-efficient furnace with intermittent spark pilot . Model # XXXXX XXXXX , S/N is 6385K 78322 . The original control was part of the gas valve . The replacement kit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
icp furnace model#t9mpv075f12a1 serial#l012836314 wont light.
icp furnace model#t9mpv075f12a1 serial#l012836314 wont light. combustion blower comes on with call for heat,after purge igniter glows and gas valve wont open. all limit switches and pressure switches … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace retries after three times. Turn off furnace and then
Furnace retries after three times. Turn off furnace and then back on Furnace will start. But not always. Is the Natural Gas Valve Sticking and in need of replacemet… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Olsen Doumatic High Efficiency Furnace dates back
I have a Olsen Doumatic High Efficiency Furnace dates back to 1985 era. The Thermostat call for heat and the purge timer Induced draft blower is activated. The spark ignition starts and pilot flame is… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have had problems where my Bryant Plus 90 Model 398AAW036080
I have had problems where my Bryant Plus 90 Model 398AAW036080 furnace starts fine upon a call for heat: inducer fan turns on, pilot lights, burners come on, blower kicks in and then the burners shut … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Tempstar furnace #NUGK075DG03 867.769422. The main
I have a Tempstar furnace #NUGK075DG03 NNN-NN-NNNN The main burner will not light. the blower works, the ignition blower works, the pilot lights. What's broke?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Carrier Weathermaster SX (1987 ivintage). When calling for
Carrier Weathermaster SX (1987 ivintage). When calling for heat, pilot intermitently lights. No moisture in system. All gas orfices cleaned off. New pilot installed by Tech. There is gas to pilot as c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
A gas furnace with a Honeywell smart valve; vent blower kicks
A gas furnace with a Honeywell smart valve; vent blower kicks on, ignitor doesn't heat and don't hear pilot gas. Ignitor appears to have a crack, very light and am unsure that this is the problem. How… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
What electrical power does the Lennox G8 gas furnace require
What electrical power does the Lennox G8 gas furnace require and what are the connections?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Coleman Evcon DGAT090BDE gas furnance in which the
I have a Coleman Evcon DGAT090BDE gas furnance in which the pilot light will not come on. There are also 4 flashing lights. What do you suggest?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Good Morning, Janitrol 92 (Mfg by Goodman) Model GUN075-3,
Good Morning, Janitrol 92 (Mfg by Goodman) Model GUN075-3, 75,000 BTU, unit equiped with spark ignition & White-Rogers gas control valve with (four) terminals. Symtom: When calling for heat, combustio… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Bryant Plus 90 Model 398A Hot Air furnace that is
I have a Bryant Plus 90 Model 398A Hot Air furnace that is not firing when calling for heat. I checked to make sure that there is gas going to the furnace first which there is. Sounds of a blower is r… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a gas furnace, model number 394JAZ036045 that the ignitor
I have a gas furnace, model number 394JAZ036045 that the ignitor will not stop sparking. When I turn on the thermostat to call for heat, the ignitor starts sparking and the pilot lights right away. Wi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a furnace that does not blow out heat and i dont see
i have a furnace that does not blow out heat and i dont see the poilot light lit. what should i do?… read more
Jim Eastwood
Jim Eastwood
Lead service
High School or GED
100 satisfied customers
Bryant Downflow furnace model # XXXXX Short in gas
Bryant Downflow furnace model # XXXXX Short in gas valve..replaced..gas valve..now furnace heat blower won;t start..replaced circuit board..still no fan.. found a short in 3 wire pilot assemb;y..repla… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Does anyone know where to get a wiring diagram for an old carrier
Does anyone know where to get a wiring diagram for an old carrier Fan control board? I attempted to install a replacment (ICM271) and am not getting the pilot to light and think I might have got some … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x