Boiler wont heat water past 160 degrees

Customer Question
Boiler wont heat water past 160 degrees
Submitted: 6 months ago.Category: HVAC
Ask Your Own HVAC Question
Answered in 1 minute by:
12/29/2017
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,400
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

Is the burner firing all the time? never shuts off?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
burner doesn't shut off. Its a Converted Weil oil burner converted to gas. has an air intake adjustment wheel on the burner to adjust flame. I;ve tried more and less air. Also shut off all of my zones so there was no circulation to see if just the water in the boiler would heat up hotter. I popped the relief valve in case the chamber was air locked. Water is in the system as no steam is created and the pressure relief valve holds.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Generally if the burner doesn't shut off on high limit and it's real cold then the boiler can't keep up with the heat demand. Meaning it's undersized or in this case may be under fired.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
That would more be the case if it was circulating all four of my zones. It should heat up when I shut the zones down as it only has to heat non circulating water
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

yes it should shut down on limit fairly quickly if no water is circulating so it's possible the gauge or the limit control is inaccurate.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
That's what I thought but thought they're might be another issue. Its a dual gauge, the pressure is on the top and the water temp is on the bottom. If the guage isn't working the high limit should still cut off at some point if I don't have water circulating.
Customer reply replied 6 months ago
The pressure part of the guage is working properly as it rises if I add water through the feed.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Yes unless it's not working. Even if the burner is under fired (unless the flame is very weak) the boiler should shut off in a matter of minutes on limit. Temp and pressure are unrelated gauge functions. 1 can work while the other doesn't.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
there is no resolution to this that you know of. Even a weak flame would eventually heat the water above the limit, it would just take longer.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Yes, as far as a resolution you haven't given me enough confirmed info to make a diagnosis. All I can do is speculate based on your description so far.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I told you all the trouble shooting steps Iv'e taken, What other information do you need?
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

A confirmed water temp. You're relying on a gauge that may not be accurate. There's no way the burner doesn't shut off on limit in a few minutes with no flow. When I say no flow I mean you have positive shut off (manual valve off) to every branch. The burner flame would have to be pretty weak for it to take more than a couple minutes

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Was hoping you would offer some other trouble shoot options, but it seems like I've covered them all.Still not sure what the problem is.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

I'm completely blind here except for what you tell me. So far what you tell me doesn't add up. So until you can prove water temp there are no other trouble shooting options.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I guess this isn't a suitable forum for this problem. Thanks anyway.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

ok

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,400
24,400 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Your thermostats heat systems use to have heat compensators
your thermostats for hydronic heat systems use to have heat compensators the new solid solid state don't have them. How do you stop the overheating with cast iron radiators… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
I have a biomass direct outside water furnace. the pump operates
I have a biomass direct outside water furnace. the pump operates continuously, my coil above the blower will loose 20 degrees when the blower kicks on. every one who ive talked to said it shouldn't be… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We just bought a house that has a Munchkin Boiler as its main
We just bought a house that has a Munchkin Boiler as its main radiant heating and hot water source. The house sits at 11,000 feet and is unable to heat the house to 68 degrees. The master bedroom, whi… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a hot water oil fired boiler that was originally equipped
I have a hot water oil fired boiler that was originally equipped with a tankless coil. We added an indirectly heated water tank and added a zone to the boiler to accommodate this. The tankless coil ha… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
The water heated connected to my Buderus boiler is heating
The water heated connected to my Buderus boiler is heating the water to 160 degrees F. Is that too hot? I cannot find a temperature regulator on the water heater. Help.… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
I had a new boiler and controls installed as follows Taco
I had a new boiler and controls installed as follows: Taco zone valve 9300-1044 4 heating zones and one hot water tank zone Taco PC 700-2 Boiler reset Honeywell L7248L1070 Honeywell wireless controls … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I recently had a Munchkin boiler 80M-R2 installed. The contractor
I recently had a Munchkin boiler 80M-R2 installed. The contractor (a heating and plumbing specialist) installed the pump on the outbound line but the Munchkin boiler drawing (from the internet) shows … read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I just looked at a 1 to 2 year old boiler which supplies forced
I just looked at a 1 to 2 year old boiler which supplies forced air for two floors (two different plenums/units for one boiler) Only information I could get weas Q90 125-200. I think it was Lennox, at… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Just looked at a house with my son who is hopefully going to
Just looked at a house with my son who is hopefully going to buy it. It has a 5 year old Buderus g115 oil boiler. The water in the boiler was only 80 degrees but the aquastat was set to 180. As soon a… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,027 satisfied customers
I have a burnham model E420 series 1 electric boiler that has
I have a burnham model E420 series 1 electric boiler that has overheated and blown off the pressure. The thermostat was set at 160 degrees and the water temp got to 220 degrees. What could be the poss… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi there, in a new home,....I have a forced hot air, oil
Hi there, in a new home,....I have a forced hot air, oil fired heating system for my second floor....(first floor baseboard....dont ask)....I have issues with the second floor fan cycling on/off after… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
We just had the plumber install 3 Smiths Quite-One 2000 Kickspace
We just had the plumber install 3 Smith's Quite-One 2000 Kickspace heaters with their own circulator pump for our kitchen remodel. A Honeywell programmable thermostat was also installed. The boiler is… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
Have a newly installed Buderus G115 boiler. Boiler water temperature
Have a newly installed Buderus G115 boiler. Boiler water temperature isn't getting hot enough to satisfy the thermostats. We were told we could leave the thermostats on 68 year around and not have to … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
We have a new Burnham 84% efficiency boiler with 3 zones 2500+
We have a new Burnham 84% efficiency boiler with 3 zones 2500+ sq ft ranch(2 levels). Last year we just let it go, without any tweaking in the season. (did have issue with zone valves - they got fried… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
On my electric boiler for heating water for baseboard heat.
On my electric boiler for heating water for baseboard heat. Temperature runs from 160 t0 190 and pressure runs from 12psi to 25 psi. Why does the pressure drop imediately from 25psi to 12 psi when the… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
L8124A in service and working ok 12 years. LO set 120, HI set
L8124A in service and working ok 12 years. LO set 120, HI set 180,Differential set 12. Burner has been shutting off 135-140 reading on boiler thermometer. Recently started shutting off at 180. Reset H… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a MI-05 boiler in my property a 2 flat building. BOILER
I have a MI-05 boiler in my property a 2 flat building. BOILER INSTALLED 3 weeks ago. Problem is that the boiler seems to run forever to reach room temperature and aquastat takes forever to cycle exam… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
i cannot get my building to to temperature i set on the thermostat.
i cannot get my building to to temperature i set on the thermostat. i set the thermostat to 80 last night at 5pm- it still syas it is only 74 inside.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x