My furnace is not igniting. The blower motor runs for a bit…

Customer Question
My furnace is not...

My furnace is not igniting. The blower motor runs for a bit and the I hear a clicking sound, and then it sounds like the gas starts going just before it all shuts down. I am thinking I need a new ignitor?

Contractor's Assistant: Did you check the furnace's filters?

Yes, the filters have recently been replace. The air flow is good.

Contractor's Assistant: Do you plan on doing the work yourself?

If possible. I am a little handy and can replace capacitors and small ancillary pieces like that. I would not be comfortable beyond those types of things.

Contractor's Assistant: Anything else we should know to help you best?

I do have the model number, if that is helpful.

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 19 minutes by:
12/29/2017
HVAC Technician: David Bowden, General Contractor replied 6 months ago
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 1,165
Experience: Owner at Floridaco
Verified

Hello and welcome to Just Answer… My name is ***** ***** allow me a few moments while I do some research, my recommendation will appear shortly.

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 6 months ago

M​ost likely the problem is the gas valve is either shorting out, or has an internal problem. If the ignitor is coming on and the flame is igniting, the ignitor is basically doing its job, and something else is causing the gas valve to shut off quickly. This is usually from a direct short or no power to the gas valve.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
There is no flame. The igniter clicks but no lighting of the gas
HVAC Technician: David Bowden, General Contractor replied 6 months ago

D​oes the ignitor glow orange and then click off after about 40 seconds?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I am at work and am not sure I can talk with customers in the store.
Customer reply replied 6 months ago
Hello, are you going to try to help me, or do I have to call to get the help I need?
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Having problems with my furnace when I got home it appears a
having problems with my furnace when I got home it appears a fuse had blown. When I reset it the furncace turns on but does notigntite … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
MOBILE HOME FURNACE NOT IGNITING I CAN HEAR THE CIRCUIT
COLEMAN MOBILE HOME FURNACE NOT IGNITING I CAN HEAR THE CIRCUIT BOARD CYCLE SHOWS ONE FKASH ON SHUT DOWN … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a G9T06010UPB13C furnace. The inducer will start when
Hello, I have a Coleman G9T06010UPB13C furnace. The inducer will start when called for heat. The flame lights and the blower goes to low and will run for about 10 min. Then the system starts to making… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
Furnace would turn on and back off within 15-20 seconds.
Furnace would turn on and back off within 15-20 seconds. Service tech came out and cleaned the flame sensor and it stayed lit. Next day its out again. I pull flame sensor and clean it again with a lit… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trane xb80. Furnace comes on, but won't move the heat. The
Trane xb80. Furnace comes on, but won't move the heat. The small exhaust fan comes on, and the burners fire. Originally I had 4 flashes on the LED. I reset the limit switches and now they're reading a… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Goodman mdl # XXXXX mfg 2002...installed in residence May 2005. Gas
Goodman mdl # XXXXX mfg 2002...installed in residence May 2005. Gas flow seems to have stopped to burner. Fan works but no gas to ignite burner. I checked overflow valve...no water there.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Rheem high efficiency furnace manufactured 2004.
I have a Rheem high efficiency furnace manufactured 2004. Trying to start for first time this fall. Unit begins to fire (no pilot), but shuts off because blower doesn't start. Blower works fine when o… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
Carrier furnace 58PAV070 - 15108 Inducer starts, ignitor glows,
Carrier furnace 58PAV070 - 15108 Inducer starts, ignitor glows, then after a bit everything shuts down - retries then completes and does full heat cycle. no error code on led. Is there something faili… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman furnace model GMT090-4a. The furnace operates
I have a Goodman furnace model GMT090-4a. The furnace operates but sometimes the gas turns on and the ignitor ignites the gas for a few seconds then it stops. This happens 3 or four times then it shut… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a York diamond 80 gas furnace that will not light. The
I have a York diamond 80 gas furnace that will not light. The blower comes on and I can hear the gas but there is no flame. The ignitor has been replaced recently, what should I look for?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
HVAC Question Trane Model XE 70 with a White Rogers Model
HVAC Question: Trane Model XE 70 with a White Rogers Model 50E47-060 Ignition Control Board. Opened front panel and found board with a continuous blinking red light. Unplugged power and plugged back i… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
Have Model RGLH 10EBRJR, Shuts off after 1 minute. Has working
Have Model RGLH 10EBRJR, Shuts off after 1 minute. Has working ignitor, working gas flow, but after running for a minute shuts off. The indicator lights are green, green, solid yellow when it is worki… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Infinity 80 furnace. Its not working this
I have a Carrier Infinity 80 furnace. It's not working this year. Is there a pilot that has to be lit?… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a gas furnace, model number 394JAZ036045 that the ignitor
I have a gas furnace, model number 394JAZ036045 that the ignitor will not stop sparking. When I turn on the thermostat to call for heat, the ignitor starts sparking and the pilot lights right away. Wi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The electronic ignition on my Rheem Quiet 80 furnace does not
The electronic ignition on my Rheem Quiet 80 furnace does not trigger. I have two identical furnaces. I tested the other and it works fine. On the functional unit, I can view the flame from the view w… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My 1989 Snyder-General gas furnace has stopped lighting.
I have a 1989 Snyder-General gas furnace, Model GUD060A014AIM that has stopped lighting. I checked the hot surface ignitor and it is working properly. After the ignitor gets hot, I hear a click from t… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Amana furnace mod. GHI45A25, Command 80 wont fire all the
Amana furnace mod. GHI45A25, Command 80 won't fire all the time. I cleaned the burner tray, air flow tube, and flame sensor. The blower comes on, ignighter glows bright, gas valve clicks but no igniti… read more
Jim Eastwood
Jim Eastwood
Lead service
High School or GED
100 satisfied customers
I have York Diamond 80 furnace that is apprx 15yrs old (model#
I have York Diamond 80 furnace that is apprx 15yrs old (model# XXXXX D16N 09601D). I live in Missouri so it is quite cold now. It often takes 3 or 4 ignition cycles before the burners actually light. … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x