The control board on my Goodman seems to be bad. When the furnace would not start I opened it up and only if I moved around the control board would it start making some clicking noises, almost like it has a short.

Contractor's Assistant: Did you check the furnace's filters?

I replaced the igniter, the flame sensor and the air pressure switch. And yes, the filters are fine as I change it every two months.

Contractor's Assistant: Do you plan on doing the work yourself?

I think I have done all I feel comfortable doing.

Contractor's Assistant: Anything else we should know to help you best?

The red light on the circuit board is constantly red. Whenever it is in just the right position to actually send power out, it will click several times somewhat similar to when the starter on a car is going out.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/29/2017
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Whats the exact model number( found inside furnace on sidewall sticker)

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have two furnaces each 20 years old both are not working
I have two miller furnaces each 20 years old both are not working all of a sudden … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My RHEEM Criterion II furnace started out acting like the
My RHEEM Criterion II furnace started out acting like the others, I set the thermostat to above room temperature, the purge fan would start, the igniter would light, the flames would start, and after … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman GMNT060-3 furnace that cycles constantly and
I have a Goodman GMNT060-3 furnace that cycles constantly and will not stay lit. When I turn on the power, it will start a normal cycle, the inducer fan starts, the HSI will glow and the gas comes on.… read more
3genhvac
3genhvac
2 satisfied customers
I have a goodman GMP075 and startup sequence is not correct,but
I have a goodman GMP075 and startup sequence is not correct,but shut down sequence is OK. I'm thinking control board,but need to verify. thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
American standard freedom 90 with 50a61-605 control board.
American standard freedom 90 with 50a61-605 control board. furnace lights up, burners on, couple seconds shuts off starts all over again. Furnace cuts off and goes into blower on "alert" mode after 3 … read more
V12Tech
V12Tech
252 satisfied customers
Please help. Frigidaire Furnace FG6RA072C-12A, serial #FGA010204217.
Please help. Frigidaire Furnace FG6RA072C-12A, serial #FGA010204217. Installed in new home 12 years ago. November 2003 = bearings on inducer motor whining; need to replace motor cycled on/off December… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Goodman GDT070-3B seems to click on and off while trying to
Goodman GDT070-3B seems to click on and off while trying to start. Then heat is on properly and shuts down normally. Would this be a problem with the control board?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
hi...i have a goodman furnace gmp075-3 ..its having trouble
hi...i have a goodman furnace gmp075-3 ..its having trouble starting up sometimes..kicks on for a few seconds then shuts off..sometimes 2 or 3 times before it works...the filter is clean,fiame sensor … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a goodman GMT-115-5 on natural gas that is about 7 years
I have a goodman GMT-115-5 on natural gas that is about 7 years old. It sometimes has trouble starting. The venter blower starts then after about 20 sec the ignitor glows, and when it works the gas va… read more
Mr. Jeff Pearson
Mr. Jeff Pearson
Refrigeration Systems
Associate Degree
145 satisfied customers
I have a Lennox Model G23Q2/3-75-2 Furnace. I had the control
I have a Lennox Model G23Q2/3-75-2 Furnace. I had the control board replaced 3 years ago. I have been having to reset the furnace due to it stops cycling. I perform the reset procedure on the furnace … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
my igniter lights and the flame only burns for 1 minute and
my igniter lights and the flame only burns for 1 minute and goes out then about 20 seconds the igniter comes on and ignites the flame for about a minute, this continues over and over. Replaced the ign… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hi i have a heil model ntc6/gne forced air furnace my problem
hi i have a heil model ntc6/gne forced air furnace my problem is the exhaust fan comes on but the pilot light and main burner won't come on put new control board in below but did't fix problem… read more
Charles
Charles
State Licensed HVAC Contractor
Associate Degree
68 satisfied customers
Please help! I have been dealing with this issue for almost
Please help! I have been dealing with this issue for almost the entire 5 years I have been in my new home. My Lennox G40UH(X) Series randomly will not kick on. I have had so many service calls by the … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have an XE 90 Trane furnace approx 10 yrs old,it has started
I have an XE 90 Trane furnace approx 10 yrs old,it has started making a clicking noise when it is about to turn on and while running. I have noticed that intially a bright yellow light will ignite a b… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have had to replace my flame sensor several times recently.
I have had to replace my flame sensor several times recently. Now the furnace will only stay lit as long as the electronic pilot is lit when the electronice starter(pilot) starts to dim the furnace cu… read more
Bill
Bill
High School or GED
318 satisfied customers
have a 96 ngoodman system in my house the furnace will light
have a 96 ngoodman system in my house the furnace will light and stay on for 30 seconds then shuts off what may be the problem… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a cacf042b2a Goodman model furnace and it it appears
I have a cacf042b2a Goodman model furnace and it it appears to "light up" when I first turn it on, the flame then dies down after a few seconds , and then the "fan(?)" stops after a few more seconds. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
hello - on tuesday, and sometimes friday, furnace will ignite
hello - on tuesday, and sometimes friday, furnace will ignite but not stay lit- while its igniting, solid red light on control board, after its off it flashes red every couple of seconds. Ignitor look… read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x