I have a budarus boiler with two zones. My second floor zone…

Customer Question
Hi. I have...

Hi. I have a budarus boiler with two zones. My second floor zone works fine, but the first floor zone will not. I thought that it might be a t-stat issue since the existing one was digital and was not responding to any of the touch controls on it. I replaced it with a Honeywell heat only, non programmable t-stat and still have no response.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

T-stat settings are at the highest temperature. Have not looked at the filters but we did just have the unit serviced this summer. I will check them now.

Contractor's Assistant: Do you plan on doing the work yourself?

I plan to make an assessment when I get into it. If it looks a little over my head I have a pro that I use regularly.

Contractor's Assistant: Anything else we should know to help you best?

Question. When the t-stat is set at a temperature that should call for heat, the furnace should at the minimum respond to the call for heat correct? Currently it just sits idle. FYI it is a FHW, gas fired furnace

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
12/28/2017
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,389
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

Do you have a pump for each zone or zone valves (what brand?)?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Valves
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

What brand?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Boston
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

That's not a zone valve brand.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Do you know what a zone valve looks like? how many pumps do you have?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
ITs only a two zone boiler. I have theee valves. Two are on the same zone, the first floor zone. ( one of the goes to a toe kick heaterin the kitchen). The other zone is the second floor. I have three valves. One has Boston labels on it. The others are Watts and Wolverine
Customer reply replied 6 months ago
They are ball valves as far as I can see. Turn them 90degrees in either way to shut off and open up.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Again, none of those are zone valves. Zone valves are motorized valves which will have several wire connected. Taco and Honeywell are the most common brands.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Got it. I have Grindfos and Taco valves on the first floor zone
Customer reply replied 6 months ago
The Taco goes to the toe kick heater in the kitchen.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Grundfos is a pump/circulator. Taco also makes pumps. It's becoming evident you aren't at all familiar with the components on the system so I can't help you diagnose something you can't identify. You're best bet is to call a pro.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Ok. Thanks.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

You're welcome

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have got some problem on FB4BNF024 model. Old thermostat
Hello. I have got some problem on Bryant FB4BNF024 model. Old thermostat screen blacked. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
Where can I purchase 2-#-1773es-03 Honeywell thermostats? I
Where can I purchase 2-#69-1773es-03 Honeywell thermostats? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My focus pro 6000 is installed for heat only at a remote
My focus pro 6000 is installed for heat only at a remote mountain location. I set furnace temp at 40 F but room temp does not register below 50F. It is below freezing.. why does room temp not register… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am trying to see what I can find out about my thermostat
Hi, I am trying to see what I can find out about my thermostat causing short short- cycling. … read more
Rick
Rick
HVAC Supervisor
24,389 satisfied customers
My thermostat just showed 2 dashes where the temperature is
My thermostat just showed 2 dashes where the temperature is normally located. The control panel is probably 14 years old and I cannot find any info on it. I am not sure where the model number is *****… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I have an old Trane model TWE 063 P130A0. I connected a
I have an old Trane model TWE 063 P130A0. I connected a programmable Honeywell thermostat (model RTH6508WF) to it this summer. The AC worked perfectly all summer long (live in AZ). The temperatures fi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Is it better to have your heating and cooling system cycle
Is it better to have your heating and cooling system cycle every 1/2 degree like most Honeywell t-stats do or 1 degree like White-Rodgers and Robertshaw do by the factory setting?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Dear HVAC God: I have a dying Honeywell TrolATemp 3 zone controller
Dear HVAC God: I have a dying Honeywell TrolATemp 3 zone controller in my house (32003618-006 Rev D). The circuit board has burn marks and malfunctions when flexed – needs to be replaced. Zone 1 is ma… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a lennox pulse 21 furnace. propane fueled. We moved
I have a lennox pulse 21 furnace. propane fueled. We moved here bringing our outdoor wood stove. I put in the heat exchanger and plumbed for the wood stove. Now I want to use the wood stove as my prim… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have an 8-year old Carrier non-programmable digital thermostat
I have an 8-year old Carrier non-programmable digital thermostat on a standard gas-furnace and air conditioner system. I don't know if it's single or dual transformer. I'm trying to change it out with… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Honeywell T8775c digital t-stat. I wanted to upgrade
I have a Honeywell T8775c digital t-stat. I wanted to upgrade to a focus pro th6110D1005 programmable t-stat. When I installed the th6110d & even though it was set at the same temp as my Digital Round… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
In your opinion-which thermostat is of better quality & precise
In your opinion-which thermostat is of better quality & precise accuracy-HONEYWELL OR WHITE-RODGERS?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a honeywell programmable thermostat in two floors of
I have a honeywell programmable thermostat in two floors of my home - main floor and bedroom floor to allow for zoned controlled heat. The main floor thermostat is working, however the upstairs thermo… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello I have a Burnham Hydronics water boiler and a Honeywell
Hello I have a Burnham Hydronics water boiler and a Honeywell L8148E Aquastat controller, with Honeywell digital t-stats with two zones. The upstairs zone doesn't seem to respond to lower temp setting… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Trane Gas 2-Stage furnace with Trane A/C. It has
I have a Trane Gas 2-Stage furnace with Trane A/C. It has a White Rodgers control module #50A51-495. I would like a simple, digital, inexpensive, non-programable thermostat that is easy to install. Wh… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Lennox Heat Pump (seven years old). I need a non-programable
I have a Lennox Heat Pump (seven years old). I need a non-programable digital thermostat that I can set at 70 degrees and it will maintain that temp year around. I also want the emergency heat setting… read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
Our system is a two-zone. We recently had a programmable thermostat
Our system is a two-zone. We recently had a programmable thermostat installed (as main thermostat with the on/off - heat/AC switch) and kept the original thermostat upstairs (which only controls tempe… read more
Joseph
Joseph
HVAC Contractor
Vocational, Technical or Trade Scho
87 satisfied customers
I have two Honeywell CT87A 4447 thermostats used in conjuction
I have two Honeywell CT87A 4447 thermostats used in conjuction with Ultra-Zone model EWC-ST-3D (2 zones) that I would like to replace with digital Honeywell programmable t-stats. Wires connected to cu… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x