My furnace is firing up about 50% of the time when calling for heat. I can hear hear the inducer fan run then a click for the gas but no ignition. Seems like sometimes the surface ignitor doesnt want to glow every time. I've changed the surface ignitor but still having the same problem. Any help would be much appreciated
Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 minutes by:
12/28/2017
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the ignitor relay mounted on the printed circuit board is the next prime suspect.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
I hope these pictures suffice, I can take more if needed.
20171228_184613.jpg2017122...jpg20171228_184602.jpg2017122...jpg20171228_184634.jpg2017122...jpg20171228_185450.jpg2017122...jpg
HVAC Technician: Phil, Mechanical Engineer replied 6 months ago

Thanks, ***** ***** jumper wire as shown in red, if the gas valve then opens and furnace fires, the problem is that one of those switches has tripped, use you ohm meter with the wires from each device disconnected to discover which has tripped or gone bad,

click here please

,

If you have 24vac to the gas valve and there is no fire and you can smell gas, then the gas valve is going bad.

We can go from there as needed,

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
9,703 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,703 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnance is giving me the code, soft lock out- max trials
Hello. My furnance is giving me the code, soft lock out- max trials for ignition reached. How do I know why the gas valve will not open to allow ignition? Is there a way to check if it's an open limit… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, i have a carrier weathermaker series 100. About a month
Hi, i have a carrier weathermaker series 100. About a month ago i noticed after the thermostat was satisfied and shut off but the inducer motor runs constantly. i have to shut the main power off to th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Rheem 80 furnace in a rental unit. Renter called
I have a Rheem 80 furnace in a rental unit. Renter called today because furnace fan was only blowing cold air. When I arrived, I cycled the furnace at which point the induction motor and main blower m… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Goodman mdl # XXXXX mfg 2002...installed in residence May 2005. Gas
Goodman mdl # XXXXX mfg 2002...installed in residence May 2005. Gas flow seems to have stopped to burner. Fan works but no gas to ignite burner. I checked overflow valve...no water there.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Rheem Criterion II, when I select heat I the small
I have a Rheem Criterion II, when I select heat I the small fan kicks in, both lights come on, the igniter fires up, the burners never light up then the igniter cuts off. The igniter then cycles again… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My gas furnace will not ignite. Here is the initial cycle.
My gas furnace will not ignite. Here is the initial cycle. Post reset, a call for heat is made. The inducer motor spins up. I hear a click (pressure switch), another click (gas valve opening) and gas … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Nordyne furnace Model M1MB-070 A-BW. It has been
I have a Nordyne furnace Model M1MB-070 A-BW. It has been very cold in the morning for the past week and we had to turn the furnace on and off a few times to get it to stay on. Now it will not stay on… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Lennox furnace and my problem is it doesnt work. I
I have a Lennox furnace and my problem is it doesnt work. I opened the furnace and found two LED lights(green and red colored) and they're both blinking rapidly at the same time. How do I deal with th… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have an amana 80sv gas furnace and am having a intermitten
I have an amana 80sv gas furnace and am having a intermitten problem. When the furnace first kicks on the combustion fan will run before the valve will open up, well sometimes that fan continues to ru… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Every once in a while (1 out of 20 times) when the thermostat
Every once in a while (1 out of 20 times) when the thermostat calls for heat the furnace will not create the flame. This symptom started after replacing the original, but broken glow plug with a unive… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Carrier 58MTB furnace that will fire only occasionally.
I have a Carrier 58MTB furnace that will fire only occasionally. Inducer starts at high speed, ignitor lights, gas valve opens but no ignition. After 4 tries of course error 14 appears. With the burna… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Gibson furnace. On start-up this heating season it
I have a Gibson furnace. On start-up this heating season it blows out cold air right from being turned on, and then the fan won't go off - I have to cut the power to get it to stop. The furnace is abo… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We were trying to turn our Gas furnace on for heating but it
We were trying to turn our Gas furnace on for heating but it won't work. I can hear the click sound(from the automatic ignitor) but it's not getting lit. Aircon function is fine. Pls help. Ours is Mod… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
i have a lennox e1603-20-ip when i put the heat on ,,,the
i have a lennox e1603-20-ip when i put the heat on ,,,the fan on auto the heat wont come on but when i put the stat on (fan on ) the fan and heat come on… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Coleman Evcon DGAT090BDE gas furnance in which the
I have a Coleman Evcon DGAT090BDE gas furnance in which the pilot light will not come on. There are also 4 flashing lights. What do you suggest?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a GMP050-3 and the gas furnace will not fire up. The
I have a GMP050-3 and the gas furnace will not fire up. The AC works ok. I replaced the control board ICM280C B1809913S and no change. The rollout and safety detection circuits have 0 resistance. The … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Rheem Criterion gas heater, when the thermostat is
I have a Rheem Criterion gas heater, when the thermostat is turned up, I can hear the blower turning on, but the gas is not igniting and no heat. What's broken?… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
I have a Bryant horizontal furnace, model 373LAV. When furnace
I have a Bryant horizontal furnace, model 373LAV. When furnace comes on, it fails to ignite the gas. Igniter rod (for lack of a better term) does not get hot. I have shut gas off and disconnected. Any… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.