I have a Goodman gmh80803BN and it is blinking 3 times. I…

Customer Question
I have a Goodman...

I have a Goodman gmh80803BN and it is blinking 3 times. I have replace the ignitor (because it wasn't working) and the flame sensor. it ignites, and then shut off again.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

I guess it started last year but wasnt' consistent. This year my heater wouldn't come. So I just replaced the ignitor yesterday and that worked but would't stay. so I changed the flame sensor today and the same thing.

Contractor's Assistant: Do you plan on doing the work yourself?

I would like to

Contractor's Assistant: Anything else we should know to help you best?

I replace the thermostat last year. that's it

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Something with the furnace

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
12/28/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,614
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

A 3 flash error is an open draft pressure switch. The question is do you have a bad switch or a weak fan ( is the draft fan running?) or a blocked exhaust vent. You can check the vent for blockages and also the vac tubing connected to the switch. Be sure the tubing is not kinked, deteriorated or doesn't have water in it. You can also poke a paper clip into the port where the tubing connects but not into the switch connection. If all that checks out. Turn the power off to the unit wait a couple minutes then turn it back on. After the fan starts remove one of the leads from the pressure switch and connect it to the other lead. If the sequence continues then you may have a faulty pressure switch or possibly a weak fan. The next thing we would do is put a manometer on the exhaust to check the actual draft pressure but you aren't likely to have a manometer and they are expensive. Replacing the switch is one other option since it's less money than a manometer (or a new draft fan) and it is a likely culprit.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,614
24,614 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a payne furnace that ignites, burns for a short time
i have a payne furnace that ignites, burns for a short time and the flame goes out, sometimes this will happen once or twice before the flame stays ignited, i changed the flame sensor yesterday and th… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I cant get my furnace to stay lit and create heat, all these
all these are ok. Have replaced the flame sensor. Furnace lights but blows out. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Ninety Percent Goodman gas furnace that is 15 yrs
I have a Ninety Percent Goodman gas furnace that is 15 yrs old. It's giving me a fault code of one blink. The ignitor comes on and glows and the gas ignites and runs for two seconds and cuts off. It d… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 2002 Goodman GMS 809003BNA furnace. I have taken a
I have a 2002 Goodman GMS 809003BNA furnace. I have taken a three week vacation each year and when I come back after setting the temp. to 60 it is no longer working. It cycles but never kicks in. Last… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Maytag MGC2SA108C35C - Blower isn't kicking on. Furnace ignites
Maytag MGC2SA108C35C - Blower isn't kicking on. Furnace ignites and then shuts down. 2 years old.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Trane XE 80 and the burners wont stay lit. They cycle
I have a Trane XE 80 and the burners wont stay lit. They cycle up, 4 blinks when thermostat calls for heat. They burn for a minute or less then go out, after so many attempts two flashing lights indic… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Goodman gms80703anbd that is blinking 5 times indicating
I have a Goodman gms80703anbd that is blinking 5 times indicating a flame sensor. didn't look bad but replaced anyway. Still same problem. The furnace fan wont shut down. Just keep blowing cold air ou… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
have a rheem furnace.... 3 lights in the window. left yellow,
have a rheem furnace.... 3 lights in the window. left yellow, middle and right are green. when not on, left light off, right green on, middle green blinking. when i turn up thermostat, the furnace com… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a coleman T H E 90 gas furnace 1990 vintage, the furnace
I have a coleman T H E 90 gas furnace 1990 vintage, the furnace goes through the ignition process correctly but after the gas lights it goes out after being lit for 10 or 15 seconds, if I shut the fur… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a goodman GMT-115-5 on natural gas that is about 7 years
I have a goodman GMT-115-5 on natural gas that is about 7 years old. It sometimes has trouble starting. The venter blower starts then after about 20 sec the ignitor glows, and when it works the gas va… read more
Mr. Jeff Pearson
Mr. Jeff Pearson
Refrigeration Systems
Associate Degree
145 satisfied customers
Good morning, I have a Coleman furnace model # DGAT095ADA and
Good morning, I have a Coleman furnace model # XXXXX and the furnace will not stay lit. I have replaced the hot surface ignition and it works, the gas valve opens for about 0.5 seconds then shuts off.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Goodman Furnace installed 6 months ago and yesterday
I have a Goodman Furnace installed 6 months ago and yesterday when I turned it on it fired up then shut down, so I went in the basement and looked at it and noticed there was an LED that was blinking … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have the same problem with the Goodman Dependable Ninety-Two
I have the same problem with the Goodman Dependable Ninety-Two furnace. Intermittently, sometimes days and weeks apart, the furnace will not ignite although you can see the electronic ignitor glowing.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my furnace isnt working right it was just blowing cold air
my furnace isnt working right it was just blowing cold air last night when i turned it off waited 5mins and turned it on it would work for a little bit but then the warm air turned cold again today th… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I HAVE A GOODMAN 70,000 BTU 80% FURNACE, ABOUT 4 YEARS OLD.
I HAVE A GOODMAN 70,000 BTU 80% FURNACE, ABOUT 4 YEARS OLD. INTERMITTANT PROBLEM HAS NOW BECOME CONSTANT. FURNACE GOES INTO LOCK OUT AFTER TRYING TO FIRE 3X. WHEN CALLS FOR HEAT, INDUCER FAN STARTS, I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
nordyne M1MA 070A AW series furnace. Keeps blowing luke warm
nordyne M1MA 070A AW series furnace. Keeps blowing luke warm air and HSI continuously lights, because flame keeps going out. Sometimes locks out due to failed ignition (4 blinking red lights). HSI rep… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Heil Gas-Electric Combination Unit. Model #NPGAA24C1K3
I have a Heil Gas-Electric Combination Unit. Model #NPGAA24C1K3 I am having a problem with the furnace...the gas will ignite for a few seconds and then shut off. I can turn the unit off and on a few t… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
I have a Nordyne MMHB-090ABHR-06. I replaced the igniter last
I have a Nordyne MMHB-090ABHR-06. I replaced the igniter last week. Now the flame kicks on and off. My research would lead me to the flame sensor. But I can't find a flame sensor on this furnace. Wher… read more
Al
Al
Master Service Technician
Votec, College, Master Electrical S
24 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x