My RUUD furnace blower is not turning on. The circuit board…

My RUUD furnace blower is...
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/28/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,193
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

The limit error is likely due to the fan not running. I need the model number of your unit. It's on the BTU rating tag inside the burner compartment. Do you have a multi-meter?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I have a multi-meter. I'll get the model #.
Customer reply replied 5 months ago
UGDJ-15EARJR.I did check for voltage across the black and white leads to blower and got 0vac
Customer reply replied 5 months ago
The blower will run if I bypass the circuit board.

Did you check after the burners had fired up?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
No change. I hear a click that I would guess is the relay, but it never turns on.

You should have power to main blower 20 seconds after the burner fires up

Ask Your Own HVAC Question
Customer reply replied 5 months ago
that's when I hear the click, but no blower.

Then you need a new board if you have no power to the blower 20 seconds after the burners fire up

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Ok. What about the flash code for the Limit Switch Open. Is that a symptom of a bad board, or should I check the limit switch?

Like I said earlier, if the blower doesn't run the heat exchanger over heats and will trip the limit

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Ah, that makes sense. The limit switch is overtemping because of no airflow from the blower, right?

Yes

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Alright, time to track down a board. Thanks.

You're welcome.

Ask Your Own HVAC Question

I'd appreciate a favorable rating

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,193
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 5 months ago
Can do.

Thanks

Ask Your Own HVAC Question
Was this answer helpful?
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,193
24,193 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Ruud furnace that is not working this morning. The
I have a Ruud furnace that is not working this morning. The "OK" light on ckt brd is flashing 5 times in a row with a call for heat. The light goes soild when I lower the thermostat to current conditi… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Ruud furnace model rgrc-09ezajs and it keeps short
I have a Ruud furnace model rgrc-09ezajs and it keeps short cycling and giving a twinning error. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How to clean heat exchanger coils, filters have been clean
filters have been clean recently and I am getting an airflow alarm on the thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,862 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Just replaced my fan blower motor on my ruud furnace and it
hi , just replaced my fan blower motor on my ruud furnace and it spoils up and right back down with a error code 68 - no blower communications any ideas, steve … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I changed the filters on my Ruud furnace in the garage. Then
I changed the filters on my Ruud furnace in the garage. Then when i went in the house to turn on the thermastat it doesnt fire up? … read more
Rick
Rick
HVAC Supervisor
24,193 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
278 satisfied customers
We have a Ruud furnace and all it does is cycle on and off,
We have a Ruud furnace and all it does is cycle on and off, with an error code of 46,what can we do … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I am getting a Twinning Fault on my new Ruud furnace. It was
I am getting a Twinning Fault on my new Ruud furnace. It was working fine during the summer when I was using it for cooling, but now when I turned it on for heating I am getting the Twinning Fault Fau… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
We have a Ruud furnace and the code on the thermostat reads
Hi we have a Ruud furnace and the code on the thermostat reads A033_F Over temperature switch roll out open. Is there a way to reset this? The blower works but won't ignite. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Ruud Furnace Flame Sensor cleaned but heat still does not
Ruud Furnace Flame Sensor cleaned but heat still does not stay on … read more
Rick
Rick
HVAC Supervisor
24,193 satisfied customers
Ruud furnace 62-25338-01 the 3amp fuse keeps blowing. I
Ruud furnace 62-25338-01 the 3amp fuse keeps blowing. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Ruud Furnace Flame Sensor cleaned but heat still does not
Ruud Furnace Flame Sensor cleaned but heat still does not stay on … read more
Rick
Rick
HVAC Supervisor
24,193 satisfied customers
My Ruud furnace unit shut off while I was unscrewing the
My Ruud furnace unit shut off while I was unscrewing the cover for the blower. I did not shut the system off before I started unscrewing the cover. I did hit the shut off switch after the unit shut do… read more
Rick
Rick
HVAC Supervisor
24,193 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick
Rick
HVAC Supervisor
24,193 satisfied customers
We have a Ruud furnace that is continually making a clicking
We have a Ruud furnace that is continually making a clicking noise as if the igniter is trying to relight the pilot light. The continuous clicking noise is irritating, is that how it is supposed to be… read more
Rick
Rick
HVAC Supervisor
24,193 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x