My RUUD furnace blower is not turning on. The circuit board…

My RUUD furnace blower is...
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
12/28/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,846
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

The limit error is likely due to the fan not running. I need the model number of your unit. It's on the BTU rating tag inside the burner compartment. Do you have a multi-meter?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I have a multi-meter. I'll get the model #.
Customer reply replied 8 months ago
UGDJ-15EARJR.I did check for voltage across the black and white leads to blower and got 0vac
Customer reply replied 8 months ago
The blower will run if I bypass the circuit board.

Did you check after the burners had fired up?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
No change. I hear a click that I would guess is the relay, but it never turns on.

You should have power to main blower 20 seconds after the burner fires up

Ask Your Own HVAC Question
Customer reply replied 8 months ago
that's when I hear the click, but no blower.

Then you need a new board if you have no power to the blower 20 seconds after the burners fire up

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok. What about the flash code for the Limit Switch Open. Is that a symptom of a bad board, or should I check the limit switch?

Like I said earlier, if the blower doesn't run the heat exchanger over heats and will trip the limit

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ah, that makes sense. The limit switch is overtemping because of no airflow from the blower, right?

Yes

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Alright, time to track down a board. Thanks.

You're welcome.

Ask Your Own HVAC Question

I'd appreciate a favorable rating

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,846
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 months ago
Can do.

Thanks

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,846
24,846 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Trane XR80 furnace. the error code is flashing 4
I have a Trane XR80 furnace. the error code is flashing 4 times, which the manual says, its a temperature switch is open. my blower fan goes on and blows hot air for about 2 minutes, but then the fan … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Having an issue with my furnace. Flashing a code saying that
Having an issue with my furnace. Flashing a code saying that either a limit switch is open or an external load is on W. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
We have a Ruud furnace and all it does is cycle on and off,
We have a Ruud furnace and all it does is cycle on and off, with an error code of 46,what can we do … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a goodman gmh8. I am getting an open high limit. I
I have a goodman gmh8. I am getting an open high limit. I get it immediately when the thermostat calls for heat. The unit is cool. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Ruud ugdg-12earjr furnace. The unit is not heating.
I have a Ruud ugdg-12earjr furnace. The unit is not heating. (the ignition cycle does not occur). The blower is running continually as though the burners are running and will only shutoff if the power… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Gas Furnace TUE060A936K Blower does not stop after gas
Gas Furnace TUE060A936K Blower does not stop long after gas burning stopped. How to troubleshoot the problem?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Ruud 80 eff furnace blower motor running will not fire the
Ruud 80 eff furnace blower motor running will not fire the furnace , checked both heat limit switchs and they are good… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
792 satisfied customers
error code 8 red flashes furnace runs to temp shuts
error code 8 red flashes furnace runs to temp shuts off but blower keeps running even when thermostat is turned off… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Blower runs no heat, limit switch is open per panel code 3
Blower runs no heat, limit switch is open per panel code 3 blinks rolled by a 2 sec pause. Unit is a Rudd achiever 90 model RCBA. Any idea if this unit has a reset? Can not locate any. Thanks… read more
V12Tech
V12Tech
252 satisfied customers
the blower fan will not cut off when the furnace cuts off it
the blower fan will not cut off when the furnace cuts off it continue to blow whats the cause this is a Ruud furnace… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Hello....i have a blower motor on my furnace that wont shut
Hello....i have a blower motor on my furnace that wont shut off. (unless i flip the switch in the basement)...I dont think its the digital thermostat because it says its in the off position and even p… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Gettingan error code that high limit protection device open
Gettingan error code that high limit protection device open on my 3ton Ruud gaspack. Everything comes on including burners but flame goes out after a few seconds… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
My furnace is about 9 years old and has started to act up.
My furnace is about 9 years old and has started to act up. The furnace will run for a couple of minutes and then the blower shuts off but flame still runs and after a few second blower will kick back … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Carrier Weathermaker 9200. Inducer motor never comes on, faults
Carrier Weathermaker 9200. Inducer motor never comes on, faults with error code 33, eventually to 13, with a constant blower motor running. I have ran the test to com24 jump, and the inducer motor doe… read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
My Trane XB90 furnace, installed 2002, wont keep heating.
My Trane XB90 furnace, installed 2002, won't keep heating. It starts, runs a few minutes then stops. The LED error code is always 4 flashes (Open Temperature Control Circuit) after the furnace stops h… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My ruud indoor blower runs all the time, I have been told I
My ruud indoor blower runs all the time, I have been told I need to replace the honeywell board(ST9101A1014). Is there a way to test my old board? When ever I take the door off the furance the fan sto… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
carrier series 150, model 58PAV090-14 furnace, serial # 2299A07962.
carrier series 150, model 58PAV090-14 furnace, serial # XXXXX error code 33, blower does not shut off. is this the flame rollout switch and where is it. i don't see a fusable link to check. Is this sw… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
I have a Ruud furnace that the blower runs all the time even
I have a Ruud furnace that the blower runs all the time even when I have the thermostat wire off the G terminal on the board, and checked all the safetys and found none bad. The air conditioning side … read more
Rick
Rick
HVAC Supervisor
24,846 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x