HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

Diagnostic code: Red-Slow Flash, On. Indicates limit switch…

Customer Question
Diagnostic code: Red-Slow Flash...

Diagnostic code: Red-Slow Flash, Green On. Indicates limit switch open. How do I reset the limit switch?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

It stopped working in the middle of the night.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I have followed the procedure for restarting, but no luck

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
12/28/2017
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,414
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation. What is the brand and model of your furnace?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Lennox G43UF
Customer reply replied 6 months ago
I don't want a phone call. Are you there?
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Call prompt is automatic I have no control over it. We can continue here

Have a little patience, I'm not a machine and it takes a while to research your model.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

You can't reset the limit. If it's working properly it will reset itself once it cools down. Do you know where it is? do you have a multi-meter?

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

When was the last time the filter was changed? There is a primary on the front and possibly a secondary on the blower housing. Do you have continuity across the main limit and where the limit circuit leads connect to the board?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
The filter was dirty. I'll have to find the leads.
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Ok, dirty filters can mean poor air flow and an overheating heat exchanger which trips the limit but it should reset on its own after it cools down. If the limit is still open it will have to be replaced.

Ask Your Own HVAC Question
Customer reply replied 6 months ago
OK. I'll check it out. Thanks
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

You're welcome

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,414
24,414 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a York Diamond 80 furnace, part P4hub16n08001a, that
I have a York Diamond 80 furnace, part P4hub16n08001a, that showed a blank (off) thermostat after a power outage yesterday. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I too have a York Diamond 80. The heat does not come on. The
I too have a York Diamond 80. The heat does not come on. The thermostat seems to be doing its job. The blower comes on but the heat does not. I checked the pressure switch by blowing into the tube and… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,948 satisfied customers
My G51MP Lennox furnace's DS2 light is flashing slow. The
My G51MP Lennox furnace's DS2 light is flashing green slow … read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
Of the two indicator lights, red and on my Lennox furnace,
Of the two indicator lights, red and green on my Lennox furnace, the green light is no longer flashing. It stays on constantly and my unit will not run.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox G60UHV, the furnace will light and run for
I have a Lennox G60UHV, the furnace will light and run for a short time and kick off. It gives the fault Primary/secondary limit switch open Primary secondary or rollout switch open. Any help would be… read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
Power went off in our home for 9 hours saturday. Since coming
Power went off in our home for 9 hours saturday. Since coming back on furnace isnt lighting. Its a goodman gch90904cx. Led flashes 4 times indicating high open limit. I replaced pri***** *****mit swit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a lennox furnace wont turn on and blinking only the
i have a lennox furnace wont turn on and blinking only the green light slowly model c50uh-48b-090-12, the induced motor is keep spinning and wont stop even its not calling for heat… read more
DennisMooreAC
DennisMooreAC
Service Engineer
Associate Degree
76 satisfied customers
I have a Lennox ch33 and woke up to the fan running but no
I have a Lennox ch33 and woke up to the fan running but no heat. Went up in the attic and opened it up. When it gets a signal from the thermostat to run, both flashing lights change to flashing red co… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE A LENNOX 80UHG FURNACE. IT WILL NOT COME ON AT ALL.
I HAVE A LENNOX 80UHG FURNACE. IT WILL NOT COME ON AT ALL. CODE LIGHTS BLINK AT THE SAME TIME SLOW. WHEN THERE IS A DEMAND FOR HEAT THE LIGHTS BLINK FAST AT THE SAME TIME. AFTER A FEW MIN. THE LEFT LI… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a York Gas Furnace model GY9S1000C20DH11G that has a
I have a York Gas Furnace model GY9S1000C20DH11G that has a Fault Code 3. How do you reset the limit switch? Thanks… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a york gas furnace FG8 125000 BTUH The air circulating
I have a york gas furnace FG8 125000 BTUH The air circulating blower was running continuous. The furnace started normally, but had 1 yellow 5 second flash diagnostic, (indicating false flame sense)? T… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Payne 373LAV horizontal furnace It will not light Flame
Payne 373LAV horizontal furnace It will not light Flame sensor is clean A blower is running There is gas The hot surface igniters do not get hot What do I do next?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
My furnace has two green lights - one is on and the other is
My furnace has two green lights - one is on and the other is doing a slow flash Accordng to the chart on the furnace, it says that this indicates "open rollout switch circuit" Does anyone know what th… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My trane XV90 is not igniting and the two lights on the panel
My trane XV90 is not igniting and the two lights on the panel are blinking green, green, red, both, red, both. Any Ideas?… read more
THEFIXER1966
THEFIXER1966
High School or GED
12 satisfied customers
I have a Carrier Weathermaker sx. It runs for about ten minutes
I have a Carrier Weathermaker sx. It runs for about ten minutes and shuts down. After about an hour or two I can restart it again and the same thing happens. It also won't start on auto. Bruce… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Our Bryant furnace stopped working last night. I replaced
Our Bryant furnace stopped working last night. I replaced batteries in the thermostat and restarted the furnace following manual procedure. Furnace kicks off but shutsdown after 2 minutes. I noticed t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Myy Carrier furnace is not comming on, I have replaced the
Myy Carrier furnace is not comming on, I have replaced the filter, turned the system off and then back on, the blower will come on but pilot isnt lighting and then it cycles back off. It is a 3 yr old… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
I have the the Amana Air command 80 High Eff gas furnace and
I have the the Amana Air command 80 High Eff gas furnace and the unit works for 3-4 hrs cycling on and off normally then will shut down and won't start again until the unit is powered off / reset. Whe… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.