On an Empire wall furnace, after start, burners burn for a few minutes, then flame appears between orifices and bottom of burners and burns a little outside of the burners. Is this normal, and is there a safety issue?

Contractor's Assistant: Do you have fuel in the tank? If so, is the shut-off valve open and the fuel clean?

It's a natural gas furance.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 hours by:
12/28/2017
HVAC Technician: David Bowden, General Contractor replied 6 months ago
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 1,210
Experience: Owner at Floridaco
Verified

N​o this is not normal. The gas flow and flame are designed to be controlled throughout the appliance. If you have gas and/or flame outside of these areas, then something is not right and is a potential safety/fire hazard. From you description it sounds like you may have a cracked burner assembly that is not noticeable when cold or no flame, however once it heats up and expands, then the gas is allow to escape through the crack and ignite creating a flame outside the burner. If you do have a cracked burner, then you will need to replace the entire heater as these parts are not available unless you can locate an old heater somewhere.

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 6 months ago

Greetings… Just following up to see if you were still needing some help answering your question?

Thanks,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 6 months ago

As of this posting I have not been able to locate any additional information on this specific issue, and since I have not received any reply or feedback from the recommendations I mentioned above, I trust they have been helpful in resolving this problem. However, if you are still needing additional assistance, please let me know by using the reply box below, otherwise I will proceed in closing out this question.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 6 months ago

Hello...

I am not sure if you have been receiving my follow up messages regarding this question however, if you would be so kind as to please respond and let me know if the information I provided initially was helpful or if you still require some assistance, I would sincerely ***** ***** that way I can either continue helping you or forward this to customer support for further processing.

Thank you very much,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 6 months ago

Hello... I would very much appreciate if you can take a few moments and reply to this email and let me know if you still require assistance, or should I proceed forward to closing out this question since it has been open for so long.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 5 months ago

Hello... As part of our continuous follow up procedures, every open question requires it to be closed out once it has gone past a reasonable time, and that the expert has provided an answer that should have helped resolve your question. This can be done simply by completing the 5 Star Rating once it appears. If you still require assistance or have additional questions, you can let the expert know by replying to this posting that you still need their advice and recommendations.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 4 months ago

Your assistance is needed... A​s of today this question is almost 60 days old and based on the nature of the problem along with the recommendation that were provided, I would like for us to close out this question, however to do that it requires a rating by you as explained below.

Please note that the rating is only based on the experts attempt to resolve the problem. If you feel a credit or refund is applicable, please contact customer service directly as the experts are not authorized to handle these matters.

One of the goals here at Just Answer, is to provide each customer with the best experience possible and for the experts to earn a 5 Star Rating based on their responses, recommendations, and professionalism, when answering questions. If I have achieved that goal for this question, please take a few moments to rate my service and select the 5 Stars before logging out.

​Thank you very much for your assistance with this, I sincerely ***** *****

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 4 months ago

If you could please respond and let me know if you still need assistance or if I can proceed in closing out this question, I would sure appreciate it as it is several months old.

Thanks

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 3 months ago

Greetings...

I was reviewing my open questions and noticed this one has not been rated yet. If you could take a couple of moments and complete the 5 Star Rating which will close out the question I would appreciate it.

Thanks,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 2 months ago

I do apologize for these continuing follow-up messages, however since this question remains open and will only close out once the rating portion has been completed by you. Please assist me by taking a few moments to fulfill the rating requirement and this will satisfy the system.

Thank you so much, I sincerely ***** *****

Best,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 1 month ago

Hello... As part of our continuous follow up procedures, every open question requires it to be closed out once it has gone past a reasonable time, and that the expert has provided an answer that should have helped resolve your question. This can be done simply by completing the 5 Star Rating once it appears. If you still require assistance or have additional questions, you can let the expert know by replying to this posting that you still need their advice and recommendations.

Thank you,

Dave

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask David Bowden Your Own Question
David Bowden
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 1,210
1,210 Satisfied Customers
Experience: Owner at Floridaco

David Bowden is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
M1MB07ABW //// FURNACE LIGHTS ..FLAME COMES ON FOR A SHORT
M1MB07ABW //// FURNACE LIGHTS ..FLAME COMES ON FOR A SHORT RUN ,,BLOWER CONTINUES TO RUN .................... HEAT SENSOR??? … read more
Rick
Rick
Supervisor
24,242 satisfied customers
I am a retired PE and my daughter just called me with a
I am a retired PE and my daughter just called me with a question about her RUUD UGRA07EMAES furnace. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I need help diagnosing an issue with a 80% Payne Home
I need help diagnosing an issue with a 80% Payne Bryant Home Natural Gas furnace. iThe problem: Furnace pilot igniter clicks 5 or 6 times and lights pilot light (normal), pilot burns several seconds, … read more
Rick
Rick
Supervisor
24,242 satisfied customers
Burner lights everything looks normal flame goes out after a
burner lights everything looks normal flame goes out after a few seconds goes through the cycle 3 times and shuts off code comes up ignition failure what could it be changed flame sencor still does th… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Furnace. Thermocouple and regulator replaced last week.
Bryant furnace. Thermocouple and regulator replaced last week. Circuit board replaced a couple of years ago. Pilot light stays on when lit. Burners come on when thermostat is set at appropriate temp. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have the same problem listed in the question and answer here:
I have the same problem listed in the question and answer here: 6 blinks, heat turns off within a few seconds. I pulled out both ceramic pieces, the straight ignitor and the bent copper electrode and … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a rheem furnace that starts normal but after 20-30 seconds
I have a rheem furnace that starts normal but after 20-30 seconds the flames on the burners reduce down to low flames. The furnace is blowing lukewarm warm air.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have Trane XE 90 furnace, works on propane. It is 13 years
I have Trane XE 90 furnace, works on propane. It is 13 years old, has been regularly serviced, no major issues. Failed once in the past and orifices were changed to fix it. This is a unit in the attic… read more
Appliance Guru
Appliance Guru
18,166 satisfied customers
I am converting my Empire wall furnace from LP to NG. I have
I am converting my Empire wall furnace from LP to NG. I have a conversion kit coming from Empire for my model. It is basically a spring, orifice and label. Do I need to adjust anything on the Robertsh… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
I smell gas at the exhaust/ intake piping outside my home for
I smell gas at the exhaust/ intake piping outside my home for a few moments after my G32 furnace fires up. Apparently the gas accumulates in combustion chamber during furnace off period. Is this norma… read more
MRANSWER
MRANSWER
TECHNICIAN
Bachelor\u0027s Degree
6,158 satisfied customers
mobile home funrace seems not to get enought air to burn. Lights
mobile home funrace seems not to get enought air to burn. Lights up comes on then goes out .… read more
servtech50
servtech50
HVAC/R service tech
296 satisfied customers
I serviced a Goodman model GPD100-4 furnace yesturday. A previous
I serviced a Goodman model GPD100-4 furnace yesturday. A previous service person had turned the manifold pressure way up to compensate for a flame sputter problem with the left #4 burner which in turn… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Hi. I have a 9 year old carrier 58tma 085 120 furnace. I think
Hi. I have a 9 year old carrier 58tma 085 120 furnace. I think I let the filter get too dirty and now I get very intermittent heat. When the house gets cold, I trip the furnace circuit breaker and wai… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Coleman Evcon Furance in a moble home . Model # dlaso75bdd.
I have a Coleman Evcon Furance in a moble home . Model # XXXXX When we check it out the furance would light and burn for while, then go out, then the fan kept going on and off so we bumped the circuit… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have an Arcoaire GUA060A012-IL furnace. The 2 burners on
I have an Arcoaire GUA060A012-IL furnace. The 2 burners on the right are working fine, but the left one lights OK, but after a short period of time (10 to 20 seconds) the flame starts to die off at th… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
i have a gas fireplace after being on for awhile it completely
i have a gas fireplace after being on for awhile it completely turns off .pilot also turns off… read more
Commercial Facility Manager
Commercial Facility Manager
Regional Facility Manager
Vocational, Technical or Trade Scho
have a gas furnace convertered from natural gas to propane.
have a gas furnace convertered from natural gas to propane. The manual reset limit switch keeps popping up disabling the furnace. What could be wrong… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
13,790 satisfied customers
I recently purchased an Empire Direct Vent Natural Gas Wall
I recently purchased an Empire Direct Vent Natural Gas Wall Furnace (Model DV-215-7SG) for my bedroom. The gasket between the observation hole cover and the unit turned black and partially disintegrat… read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x