Unit doesn't have pressure...

Unit doesn't have pressure switch but the fault code is two blinks on the ignition control

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Put a new state and filters are good and induced motor is not coming on either

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I've replaced the ignition board, rollout switch and high limit switch and transformer

Submitted: 6 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
12/27/2017
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,393
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

What's the brand & model number of your unit?

Ask Your Own HVAC Question
Customer reply replied 6 months ago
Nordyne MMHA-056AAHR-02
Customer reply replied 6 months ago
I've put a new stat, ignition control, rollout and high limit switches, transformer for blower relay section
HVAC Technician: Rick, HVAC Supervisor replied 6 months ago

Ok, you may not have a pressure switch but you do have a centrifigal switch in the combustion motor that must prove it's turning. Generally the switch is integral to the motor so you'd have to replace the motor.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,393
24,393 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rheem Criterion II. Sometimes doesn't start. Inducer will go
Rheem Criterion II. Sometimes doesn't start. Inducer will go on and off and start sometimes but next time inducer motor will cycle on and off again before it starts … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace is not igniting. The red light on the control
My furnace is not igniting. The red light on the control board is blinking 4 times. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Billy-have a similar problem as above. Just did a service on
Hi Billy-have a similar problem as above. Just did a service on a Luxaire mid-efficiency furnace (Model: G8T08012UHA11A s/n WKLM029272). Main blower is not turning on. Inducer motor comes on, have ign… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Heil N9MP1100J20A2 furnace and the blower motor
I have a Heil N9MP1100J20A2 furnace and the blower motor isn't coming on. I can get the pilot to ignite and the gas to come on by turning the service switch off and on, but the gas will burn for about… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Trying to figure out whether it is the circuit board or the
Trying to figure out whether it is the circuit board or the gas valve only getting 14 vs to gas valve all switches function normally and the transformer gives me 24v igniter doesn't glow but replaced … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im working on an Armstrong furnace; Model#GUJ125D14-1B. The
I'm working on an Armstrong furnace; Model#GUJ125D14-1B. The blower stays on constantly even after bypassing/jumping the high limit and flame rollout switches. There are no other safeties. I suspect t… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a rheem RRKA-A042JK08E. The heater has stopped, though
I have a rheem RRKA-A042JK08E. The heater has stopped, though I've had intermittant running. Currently the iniator fan turns on for perhaps 10 seconds, there are two click (?circuit board and vacuum s… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello there I have a York 80 furnace, P2MP. Thermostat calls
Hello there I have a York 80 furnace, P2MP. Thermostat calls for heat, inducer motor starts, ignition comes on, gas comes on, flames start, blower motor starts. 5-10 minutes later flames stop, inducer… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Lennox 80MFG3/4-100A-8. T-stat calls for heat, (both red &
Lennox 80MFG3/4-100A-8. T-stat calls for heat, (both red & green LED blinking as normal) - furnace main blower starts (on low speed?) and nothing else happens. Red LED is now blinking and Green one be… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Lennox Model: 80UHG3-75A-9 Serial #: 6397L White Rodgers
Lennox Model: 80UHG3-75A-9 Serial #: 6397L White Rodgers 50A55-120 (56L8501) control board My furnace has will not ignite. When the thermostat calls for heat, the inducer motor starts to spin, then sl… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
I got an Armstrong G1N80AU natural gas furnace and got a 4
I got an Armstrong G1N80AU natural gas furnace and got a 4 flashes failure code which as per the O&M manual indicates an open limit switch or limit switch circuit fault. I checked the rollout switch, … read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
Hello, I have an Amana GUIC090FA30 fce with a White Rodgers
Hello, I have an Amana GUIC090FA30 fce with a White Rodgers 50A65-288 control board. My fce will not open the gas valve to ignite. Thermostat is calling for heat, fce starts after 1 blink from circuit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Ruud UGRL running on natural gas which was installed
I have a Ruud UGRL running on natural gas which was installed in December 2010. It worked perfectly for the first three months. In March it started having intermittent (once or twice a day) problems f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Bryant furnace is not putting out warm air. I just went
My Bryant furnace is not putting out warm air. I just went and looked at the RED LED status light and it was blinking. After removing both panels and then replacing the top panel, the light remained o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
carrier furnace 58m code 33 then code 13 jumped rollout
carrier furnace 58m??? code 33 then code 13 jumped rollout to test switch same issue....exhaust blower never comes on ??????… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
I have a Trane XE78 furnace. The problem I have seems electrical.
I have a Trane XE78 furnace. The problem I have seems electrical. The blower constantly runs when cooling cycle stops. Thermastat is on auto/ cooling. I disconected thermastat to c if that was the pro… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why is the indoor blower and the inducer motor on my gas pack
Why is the indoor blower and the inducer motor on my gas pack running all the time? I've unhooked the wires coming from the thermostat and put power back on the unit and the blower and the inducer mot… read more
Jim Eastwood
Jim Eastwood
Lead service
High School or GED
100 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x