Furnace model G9T10014UPC13C burner will not ignite. Fan…

Customer Question
Coleman furnace model G9T10014UPC13C...

Coleman furnace model G9T10014UPC13C burner will not ignite. Fan runs in continuous on setting thermostat but not in auto mode. Red light flashing on board.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I don’t think thermostat is problem. I did change batteries

Contractor's Assistant: Do you plan on doing the work yourself?

Only if it’s something simple. Trying to get repairman but not available immediately. It’s 14 below here and we will be in trouble in the next several hours . If can’t start burner

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
12/27/2017
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

How many red flashes between pauses?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
58MSA-100 no display at thermostat. no heat. led status
58MSA-100 no display at thermostat. no heat. led status light is on solid, no flashing. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Red T mobile home furnace model dgaa090bdta made
I have a Red T mobile home furnace model dgaa090bdta made by Coleman. I ran out of propane and after I filled the tank my furnace will not ignite. The light is a steady flash indicating ignition failu… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My rheem gas furnace heat does not ignite in manual or auto
my rheem gas furnace heat does not ignite in manual or auto mode but the blower comes on in manual mode with no heat. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My American Standard freedom 80 two stage furnace won't come
my American Standard freedom 80 two stage furnace won't come on. I have a white rodgers programmable thermostat and the program is above room temp and I tried to manually increase it as well--to no av… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The batteries in my Noma 2 thermostat went dead last night and the furnace stopped. After
The batteries in my Noma 2 thermostat went dead last night and the furnace stopped. After changing the batteries in it the fan will work if set to ON, but will not blow hot air (even if Heat is set to… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a trane gas furnace that is one year old. When I put
I have a trane gas furnace that is one year old. When I put the thermostat in heat mode, I hear it click and it shows heating but heat does not come in and the fan does not come on. I go to the furnac… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Troubleshooting a Trane XL80. On heat, vent fan does not cycle on and off, but if I put f
Troubleshooting a Trane XL80. On heat, vent fan does not cycle on and off, but if I put fan on Auto, it runs and the furnace works. On A/C, fan cycles normally.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
20 yr old Coleman brand mobile home propane central heating
20 yr old Coleman brand mobile home propane central heating unit. Last year the fan started coming on for only 1 second after the burner started and short cycled for hours. I replaced batteries in the… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a goodman gms8 single stage warm air furnace. Set the
I have a goodman gms8 single stage warm air furnace. Set the tstat to call for heat. Have the settings to auto fan and heat mode. Unit does not start. set the fan to On mode and fan started but draft … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have Carrier Standard Programmable Thermostat - Power Stealing ,
Have Carrier "Standard Programmable Thermostat" - "Power Stealing", no model record or markings on thermostat that I can find - Manual #NNN-NN-NNNN Rev C. During current extreme cold snap, temperature… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
we are in the middle of the ice storm belt. Yesterday the power
we are in the middle of the ice storm belt. Yesterday the power went out and came back on 3 hours latter 8:30 pm. gas Furnace came on. Woke up at 4 am. House down to 58. Gas hot water heater works, so… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
I have a Merit Series G40UH(X) gas furnace. It starts up normally
I have a Merit Series G40UH(X) gas furnace. It starts up normally when the thermostat kicks it on, and the burners will ignite and will run normally. However, frequently it will kick on, light the bur… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My 1996 Lennox Conservator III G16 gas furnace will not start
My 1996 Lennox Conservator III G16, ELECTRIC START, gas furnace will not start and stay running. I have an old mercury round thermostat. How should I trouble shoot this to DIY fix? I spent 2 hours str… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hi. Over the weekend I replaced our old thermostat (with the
Hi. Over the weekend I replaced our old thermostat (with the mercury) with a new Honeywell RTH2410. When I turned on the heat I noticed that the temperature is not getting hot. On the old thermostat t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox elite g26q3-75-2, When in heat mode the blower
I have a lennox elite g26q3-75-2, When in heat mode the blower motor does not come on, the burners will ignite and stay on until it overheats and shuts off. but if i select fan on the thermostat contr… read more
John
John
High School or GED
27 satisfied customers
I have an Arcoaire furnace (RPJ II) about 14 years old. I
I have an Arcoaire furnace (RPJ II) about 14 years old. I have been having problems with ignition. Sometimes the burner will ignite and sometimes it won't. The furnace will shut off and turn on immedi… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Coleman Evcon DGU LP Gas.... Intermitent heat Getting
Coleman Evcon DGU LP Gas.... Intermitent heat Getting 7 flash fault code for No Ignition Thermostat calls for heat, Ventor motor runs, Ignitor glows bright, Gas valve clicks but does not Ignite .....a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a old Rheem furnace.model RGDD-08NE-GR. Pilot light
I have a old Rheem furnace.model RGDD-08NE-GR. Pilot light is up for more than 10 minutes but burner won't light up. How can I fix it? Joe… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less