Brand new furnace get an immediate 33 code have continuity…

Customer Question
Brand new furnace...

Brand new furnace get an immediate 33 code have continuity through roll-out circuit and high- limit pressure switch seems functional

Contractor's Assistant: Did you check the furnace's filters?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Tried to start furnace without exhaust pipe connected no difference

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
12/27/2017
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

Whats model number?

Are you ready

Ask Your Own HVAC Question
Customer reply replied 7 months ago
R92pa1001521msa
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

Thanks

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Did you get my model#
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

Yes

Make is Rheem?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Rudd. Same thing
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

OK...

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

Did you OHM test every limit switch?

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

Take one wire off each component when checking them.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I ohmed every and the circuit I have continuity
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

There should be 3 roll out switchs and one main limit switch

Ask Your Own HVAC Question
Customer reply replied 7 months ago
2 roll out 1 high limit for
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

Wiring diagram shows 3 roll out, check on the side of burner box

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

It might be a faulty wire that connects all limit switchs,

Check wiring diagram bottom right of page 96

https://www.hvac.com/media/manuals/installation/RHEEMR92P.pdf

Bypass R/W and R/BK to see if that will work

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

I noticed question is still opened and unrated please dont forget the 5 star rating if we are done

Sincerely

Customer/p>
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
937 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a carrier furnace 58mca120 16-120 error code 33
I have a carrier furnace 58mca120 16-120 error code 33 followed by error code 13. replaced both the high limit and roll out switch and still have the error code. There are no other switches in the cir… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Have a 90 Plus furnace built 4798 Model 350MAV060140. Got a
Hi Pearl Have a Bryant 90 Plus furnace built 4798 Model 350MAV060140. Got a status code 3 3. House fan is blowing, exhaust fan is not. Been working for about 1 month. No problems. Same thing happened … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Code 33 on a payne furnace. Furnace cycle on and off,
Code 33 on a payne furnace. Furnace cycle on and off, kicking code 33 everytime, until it reaches the temp. Also, when that code comes up the power to my thermostat gets cut and it takes five minutes … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Trane XE 80. So the furnace hasn't been on since
Hi Brian. I have a Trane XE 80. So the furnace hasn't been on since last winter/spring. The blower motor and exhaust fan come on but the gas never flows/ignites. The status indicator blinks 4 time. I'… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am trying to do a high limit reset on my furnace, model number
I am trying to do a high limit reset on my furnace, model number carrier furnace 58sta135 code 33 error… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
, I have a Bryant 355AAV furnace and I have error code 24
Hi, I have a Bryant 355AAV furnace and I have error code 24 after I replaced the Inducer motor with a brand new one, the circuit board with a new one, the manual rest limit switch, the low pressure sw… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a Goodman GMT090-4A furnace that will not fire up. I
I have a Goodman GMT090-4A furnace that will not fire up. I see 3 blinking lights on main board. I checked ignitor ok at 80 ohms but thought to replace so did that. Unit is eleven years old replaced f… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Blower is blowing no heat .the switch is reading ohms. Ive
Blower is blowing no heat .the switch is reading ohms. I've pressed 3 times to reset. My termistate is correct. Thought maybe the gas line had a bubble so I bleed it. Nope still no flame… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am getting a 33 code and furnace will not light. I have
I am getting a 33 code and furnace will not light. I have checked voltage at roll-out and limit switches while it is running it's 4 minute test and I get 27 vac at all terminals to ground. If I leave … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have an American Standard freedom 90 model #TX061C5HPB2 manufactured
I have an American Standard freedom 90 model #TX061C5HPB2 manufactured in 97. I just had gas hooked up to the house last week for the first time. The unit has been used for AC for the past 3 years and… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
intermittent Carrier Weathermaker 9200 displays a continuous
intermittent Carrier Weathermaker 9200 displays a continuous red led light. What does this mean? How do I know if it is red light 1 or red light 2? Thanks!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Coldest night of the year and my Payne gas furnace (no pilot
Coldest night of the year and my Payne gas furnace (no pilot light kind) is blowing cold air only. Did the recycle thing. When power applied, blower comes on immediately, but no burners that I can tel… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
I have a Payne PG8UAA060135ABJA furnace where the big blower
I have a Payne PG8UAA060135ABJA furnace where the big blower fan comes on instead of the litter exhaust fan that generally comes on just before ignition. What should I do to trouble shoot?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Bryant 395 cav upflow furnace. (10 yrs old) It showed
I have a Bryant 395 cav upflow furnace. (10 yrs old) It showed a code 33, I had a service tech out and he told me that the circuit board needed to be replaced, after troubleshooting the pressure senso… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, My furnace is not ignightinh. It is a G1D93AU high
Hi, My furnace is not ignightinh. It is a G1D93AU high efficiency 90+ Condensing Gas unit. It has been functioning well until today. I've read over the manual, and checked the LED code. It told me tha… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have Bryant 340MAV (90+ condensing) with a recurring problem
I have Bryant 340MAV (90+ condensing) with a recurring problem that is getting worse. It would start normally - induction motor start for 20-30 seconds then glow plug start, then gas valve opens and b… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My new Carrier 58STA 155K BTUs fires up fine then flame shuts
My new Carrier 58STA 155K BTUs fires up fine then flame shuts off after few minutes and air blows until cool, then starts up again. It is heating the house but the on off sequence makes me think their… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier 58MXA060-12 gas furnace. I had the heat exchangers
I have a Carrier 58MXA060-12 gas furnace. I had the heat exchangers changed out on the class action law suit 1 year ago. Now the furnace has been cutting out leaving the blower motor running. Error co… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x