HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

Furnace will not turn on goes thru sequence inducer,

Customer Question
Furnace will not turn...

Furnace will not turn on goes thru sequence inducer, ignitor, but the gas valve will not open gas. Replace a new one still will not. But in new board, nothing

Contractor's Assistant: Did you check the furnace's filters?

Its clean

Contractor's Assistant: Do you plan on doing the work yourself?

Yes i have a license but this is killing me

Contractor's Assistant: Anything else we should know to help you best?

Flsme sendor is new slso

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 16 minutes by:
12/26/2017
HVAC Technician: airheatman, HVAC Technician replied 7 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,368
Experience: Furnace, A/C and heat pump specialist.
Verified

Do you have a manometer to check inlet gas pressure? And are you getting 24v to the valve?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Ruud 80 Plus ( UGDE 12ERAJS ) is not igniting. Ignitor glows,
Ruud 80 Plus ( UGDE 12ERAJS ) is not igniting. Ignitor glows, flame rod is clean and looks good. Gas solenoid does not open. Inducer blower motor sometimes does not turn, and, sometimes motor will jus… read more
R G
R G
44 satisfied customers
Payne Model PG8MAA036070ABJA with code 34 followed by 14.
Payne Model PG8MAA036070ABJA with code 34 followed by 14. "Professional" replaced ignitor 5 months ago which fixed it for a week. I then cleaned the flame sensor which fixed it until now. I order a ne… read more
R G
R G
44 satisfied customers
Good afternoon, Goodman GMPN060 -3 Rev B led blinks 3 times on
Good afternoon, Goodman GMPN060 -3 Rev B led blinks 3 times on call for heat, fan starts, gas flows, ignitor does not glow. Replace ignitor, as I have done almost every 2 years? If you agree, please c… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Plus 90i furnace that will not fire, the code is a
I have a Plus 90i furnace that will not fire, the code is a number 34 (3 yellow, 4 green) Looks be the gas valve can you confirm? For diagnostic purposes can you clarify the sequence of events, does t… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I am getting a reading of three flashes on my diagnostic light
I am getting a reading of three flashes on my diagnostic light , we tested the air switch from normally open and blew into it and the contacts sounded like they closed so we verified that it closed wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an american standard Freedom 90, when I turn the heat
I have an american standard Freedom 90, when I turn the heat on nothing happens.......if thermostat is set to auto, blower will run if its set to on. There is no flame, an it makes no noise. It flashe… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Rheem Model RRKA8036JK08E (so the paperwork says).
I have a Rheem Model RRKA8036JK08E (so the paperwork says). It cools fine, but will not heat. I had a service tech (read that replacement artist) look at the furnace. First he said it was the gas valv… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Model# RGPH-10EBRJR Serial#DH5D307F339601010, wont
I have a Model# RGPH-10EBRJR Serial#DH5D307F339601010, wont light, I followed intructions to the letter to relight & my gas is on! Any suggestions? Thanks, Carl… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
have a gas furnace high Eff. goes thru proper sequences. draft
have a gas furnace high Eff. goes thru proper sequences. draft fan,hsi glow, but sometimes doesnt ignite gas then when it does start, shuts off before room is satisfied. got any ideas? already changed… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
No heat. Fan turns on only in on position still no heat. Thermo
No heat. Fan turns on only in on position still no heat. Thermo coupling clean. Ignitor turns on sometimes. Is this the mother board? Furnace is 4 years old.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
1992-93 bryant furnace 3 burner mid-eff runs sweet for about
1992-93 bryant furnace 3 burner mid-eff runs sweet for about 2 hours(kicks on kicks off) then does nothing. temp falls below temp diff set on thermastat(makes for a very cold morning)so i either turn … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I HAVE ARUUD MODEL URGG07E24JKR. I TURNED ON THE HEAT AND
I HAVE ARUUD MODEL URGG07E24JKR. I TURNED ON THE HEAT AND NOTHING HAPPENED. IS THERE A CHECK LIST OR OTHER GUIDE TO FOLLOW TO CHECK MY UNIT OUT?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
My Ducane furnace inducer keeps running without giving heat.
Draft inducer keeps running but heat will not come on, unless I turn it off, then back on. wWhat could be the problem?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
i have a trane xe80 furnace with hot surface ign. gas will
i have a trane xe80 furnace with hot surface ign. gas will not go on , induce motor runs ignitor gets red hot gas valve clicks ignitor goes off… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
My central heater is blowing cold air instead of heat I
My central heater is blowing cold air instead of heat? I have a corsaire RCBA-3765AS21 And I had the same problem and the HVAC guy came over and replaced the igniter. It worked good for a day and now … read more
Roger (Mr. Fixit)
Roger (Mr. Fixit)
Service and Sales Manager
Bachelor's Degree
16 satisfied customers
Have a mid 80s Amana air command 80 that is acting up. Fan
Have a mid 80's Amana air command 80 that is acting up. Fan cuts on, 15 sec later hear a click. Replaced the igniter and still not burning. By passed the vacuum switch for testing and still not igniti… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a gas furnace model XL 80. when turn on the burners
I have a gas furnace model XL 80. when turn on the burners don't go on. so no heat is coming out, the pump works and the lighter turn on but the burners no. can you help me this problem please.… read more
Josh
Josh
Service Technician
High School or GED
30 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x