Furnace will not engage pressure switch (rated -1.11) on the…

Customer Question
Furnace will not engage...

Furnace will not engage pressure switch (rated -1.11) on the port of the draft inducer it reads -2.1) 3 pressure switches have been tried and new hoses. Amps on motor are .72. Flue is open, draft inducer is clean heat exchanger is clean, all drains are open and working

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

T-stat is turned all the way up, filters are clean

Contractor's Assistant: Do you plan on doing the work yourself?

I’m a contractor and Rheem technical support is closed

Contractor's Assistant: Anything else we should know to help you best?

Gas valve, burner tubes and board have been replaced

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 20 minutes by:
12/26/2017
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you

Is it proane or nat gas

Things to check

  1. Obstructed intake or exaust pipe, use a shopvac outside where pipes ends.
  2. You may have a blocked secondary hear exchanger
Ask Your Own HVAC Question
Customer reply replied 7 months ago
Propane...
exhaust and supply air are open sometimes (once a day) the burner tubes don’t fully light then the second time it will. I get a -2.1 at the port on the draft inducer housing. But once the hose is installed I only get a .97 or so. Tried different hoses and same deal.
Customer reply replied 7 months ago
Air are open. Sometimes
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

How old is unit

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

You need to do a gas pressure test

  1. Inlet of gas valve should be approx 10.5 to 11wc
  2. outlet when gas valve opens 10- 10.5 wc

If pressure was off for a long period of time bad combustion may have obstructed secondary heat exchanger.

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago
I noticed question is still opened and unrated please dont forget the 5 star rating if we are done Sincerely
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
937 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Weil-Mclain HE-4 gas water boiler, with induced draft, shuts
Weil-Mclain HE-4 gas water boiler, with induced draft, shuts offs by Fuse Thermo rollout switch. What is wrong with it? Boiler got new control unit, vacuum switch, new blower motor. Works good for sev… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hello, Furnace: 5 year old Tempstar model#N9MP2100F14C2,
Hello, Furnace: 5 year old Tempstar model#N9MP2100F14C2, SN#A073359765, built in 2007 Problem: Approx 50% of the time, the ignighter does not glow to light the natural gas. Replaced: I replaced the ig… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My coleman lp furnace will most of the time just run the inducer
My coleman lp furnace will most of the time just run the inducer motor which i replaced and wont ignite but when i take the hose off the pressure switch the hose that goes to the burner and blow throu… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Gas furnace pressure switch stuck open. How to fix?
The gas furnace is not working. The red light is flashing three times indicating pressure switch stuck open. What should I do to fix it?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
20 yo Lennox with faulty air pressure sensor - replaced but
20 yo Lennox with faulty air pressure sensor - replaced but still not working apparently. I have been able to tap it to get it to work, but not today.… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a Rheem RGDD-08NE-GR Gas furnace that the heat exchangers
I have a Rheem RGDD-08NE-GR Gas furnace that the heat exchangers will fire but stay on for different periods of time, same thing happens with the blower. Sometimes the heat exchangers will fire and th… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hello. I have a Ruud 90 Plus furnace, installed in about 1995.
Hello. I have a Ruud 90 Plus furnace, installed in about 1995. Series URGA-10EZAJS, Serial #DF50707 F0495 2396. I just replaced the Induced Draft Blower (the squrial cage desinegrated), and now when I… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Heil gas hot air furnace, about 5 years old. The furnace
I have a Heil gas hot air furnace, about 5 years old. The furnace would start and light the burners, then after about 30 seconds the burner would go out, and the process would continue again, light th… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a rudd ugph-10ebrjr. When the exhaust to the outside
I have a rudd ugph-10ebrjr. When the exhaust to the outside comes on the small exhaust fan on the unit starts to turn slowly in one direction. This is all it will do. I take the hose off the pressure … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Coleman Evcon DGU10014UB - I am getting 6 blinks
I have a Coleman Evcon DGU10014UB - I am getting 6 blinks (lockout - pressure switch, ). It resets, then does it again after a hour or so. What part is failing If any) ? The pressure switch?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I replaced my inducer assembly. It runs but the furnace wont
I replaced my draft inducer assembly. It runs but the furnace won't start heating. carrier model 58msa. error light blinks 1 3. Inducer runs for several mimutes then shuts off. Never Mind, I got it ru… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
hello, on this cold night my furnace stopped coming on. The
hello, on this cold night my furnace stopped coming on. The error code is two short and three long. I have a carrier furnace. 23 PRESSURE SWITCH DID NOT OPEN Check for: - Obstructed pressure tubing. -… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Rheem 80 Plus furnace. When turned on with the thermostat,
I have a Rheem 80 Plus furnace. When turned on with the thermostat, the induced draft fan comes on, but the burner will not light.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My Rheem furnace keeps cycling. The igniter lights and then
My Rheem furnace keeps cycling. The igniter lights and then the gas burners light but after about 5-10 seconds the gas burners shut off. The fan continues to run suring this time. After 30-60 seconds … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
hello, my furnace has stopped heating at some point last night
hello, my furnace (Payne PG8M) has stopped heating at some point last night - when I reset the breaker, the blower starts fine for a few minutes, but no heat/flame comes on, and then the blower stops … read more
BigD in NoCal
BigD in NoCal
Stationary Engineer
Vocational, Technical or Trade Scho
4 satisfied customers
If we installed furnace in wrong direction, will the furnace not work?
My furnace won't stay running to heat to the set tempurature. If we installed the furnace filter the wrong directions could this be the problem?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Rheem (Model# XXXXX) furnace starts, runs for a few seconds
Rheem (Model# XXXXX) furnace starts, runs for a few seconds but does not ignite. the the blower comes on for a few seconds then suts off and the cycle starts again. Blower also runs intermitently with… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Rheem Criterion II gas furnace main burner will not stay lit
My Rheem Criterion II gas furnace main burner will not remain lit. What should I check first?… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x