Customer Question
I am troubleshooting a...

I am troubleshooting a 25 amp, A.C. 3000 watt base board heater. with a type 24A05A-1 White Rodgers controller. The original controller stopped opening and closing. I purchased a new 24A05A-1 from my local supplier and installed it. Before applying a load I tested the output voltage from the transformer , with a Klein 117 multi-meter, The voltage read 31.9 volts, the transformer started to vibrate and then voltage output dropped to 0.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About seven days.

Contractor's Assistant: Do you plan on doing the work yourself?

This work is being done by my neighbor, he is a licenced electrician.

Contractor's Assistant: Anything else we should know to help you best?

It is cold here and I would like to get my heat back.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

There are no filters as it is a baseboard heater. The installation instructions say I should have no more than .2 amps of thermostat power, before the transformer quite I had 31.9 amps!

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 3 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 3 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 2 hours by:
12/26/2017
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,315
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, those 24A05A-1 White Rodgers controllers are line voltage (230 or 120V) there is no transformer involved with that circuit at all in virtually all cases, tell me exactly where you found the 24vac transformer, we can go from there.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Good Morning Phil
I am in error when I mentioned that we received 31.9 amps from the transformer. It was volts, not amps. My misunderstanding. Also, we seem to be discussing two different pieces of equipment.In a sticker on the front side of this unit, a 24A05-1, it produces a current of .21 amp @ 18 V.A.C voltage for the low voltage thermostat. Am I reading this wrong?I look forward to your reply.Sincerely,Jim Dillon
HVAC Technician: Phil, Mechanical Engineer replied 3 months ago

Hello,

Boy did I screw this up, I assumed you had a line voltage thermostat there, as most baseboard heaters have... but instead you have a 24volt time delay **relay... controlled by a 24 volt thermostat somewhere, that sends 24vac to the time delay circuit on your white rodgers *relay. Click here

The term **controller most often refers to a thermostat that controls the temperature.

Amperage is the actual number of electrons passing a certain point per second, a few hundred thousand per secon as I recall... volts is the pressure that the utility company puts on the power lines into your house... that pressure is what forces the electrons (amperage) back and forth in the wire 60 times a second.

No item such as the base board heater in your house *produces and current... (current is Volts x Amps... or Watts)... the draw (or use) current The 24vac transformer that converts 120vac to 24vac however converts the 120v to 24v and that 24 v is used to operate the time delay relay.

If you say that transformer burned it, first check for a dead short in the wiring and then replace the transformer with the same voltage and VA (volt amp rating) generally 120 volts on the primary side and 24volts on the secondary side, and rated for 40VA... not less.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,315
9,315 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,315 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The whole screen on my -Rodgers thermostat is blinking. I
The whole screen on my White-Rodgers thermostat is blinking. I replaced the batteries, nothing happened. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
I am replacing an old -rodgers thermostat with 3 wires with
I am replacing an old white-rodgers thermostat with 3 wires with a Honeywell digital thermostat. When I removed the old plate the only labeling on the old was "Y or 6" with y white wire, grey wire con… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a white Rodgers heat only thermostat, mod.1e78-140.
I have a white Rodgers heat only thermostat, mod.1e78-140. it is not working, does it run on batt. or is the power wired from home. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a White-Rodgers 1 F81-261 Programmable thermostat.I
I have a White-Rodgers 1 F81-261 Programmable thermostat.I want to operate it manually. Please help. It has reset at 62 degrees. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a White-Rodgers thermostat with the flap that opens
Hi, I have a White-Rodgers thermostat with the flap that opens to the menu. All of a sudden the temp of the room that the display shows on the left is not showing the temperature in Fahrenheit, but it… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My white rodgers 1f78 non-prgm thermostat won't work. The
My white rodgers 1f78 non-prgm thermostat won't work. … read more
Phil
Phil
Mechanical Engineer
9,315 satisfied customers
I have a White Rodgers !F-95-1291 Touch screen thermostat
I have a White Rodgers !F-95-1291 Touch screen thermostat with remote outdoor sensor. The out door reading is off by 10 degr F, too low. What's the prob? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an f8024 white rodgers, i am renting right now but
I have an f8024 white rodgers, i am renting right now but the unit worked last summer, i just replaced the batteries, but when i press the temp down button, nothing happens. … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
49 satisfied customers
I have a white/rodgers 8A05A -101 relay that I want to use
I have a white/rodgers 8A05A -101 relay that I want to use for a hot water circulating pump. The thermostat wiring is straight forward but the wiring for the 120 v is not. I have the following wires. … read more
Phil
Phil
Mechanical Engineer
9,315 satisfied customers
White Rodgers Thermostat 1f78-1151 is hooked up but not
I have a white Rodgers Thermostat 1f78-1151, I've hooked it up and it isn't working. I don't know if I wired it wrong. When I just connect the wires together the baseboards come on.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old White/Rodgers thermostat that I'm upgrading to
I have an old White/Rodgers thermostat that I'm upgrading to a wifi Honeywell. All wires are labeled, but there is one labeled W that has no corresponding slot in the new thermostat. Is this W equal C… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a 15-20 yr old white-Rodgers thermostat wired to an
We have a 15-20 yr old white-Rodgers thermostat wired to an attic furnace; a pain to get to. We have to keep getting up in there to reset it. This time it's not coming on? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
White Rodgers thermostat not heating even after changing battery.
I have a 1F81-51 White Rodgers thermostat. It's been flashing low battery for a while. This morning, the house felt very cold and the heat was not functioning. Set on 69, but house was 61. I replaced … read more
Phil
Phil
Mechanical Engineer
9,315 satisfied customers
My white-Rodgers thermostat keeps failing. Sometimes it works.
The white-Rodgers thermostat keeps failing. Sometimes it works sometimes it doesn't. A company came to check and when they were here, it was working then it failed again. They check the HVAC in the at… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Changed batteries on White Rodgers Thermostat. It stopped working
I have a White Rodgers thermostat control model #1F78. Today the thermostat said batteries were low so I changed them. Now nothing works. I tried other batteries and nothing. I put the old ones back i… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
White Rodgers thermostat does not display the set temperature.
I've got a Goodman furnace and a White Rodgers thermostat. The thermostat in heat mode will not display a heat set temp. Just blank, though the screen does display the ambient temp. The A/C works, but… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I would like a manual for our White Rodgers thermostat
I would like a manual for our White Rodgers thermostat IF85-277. Can you send me one? We have just misplaced ours. It is working fine. I just need a manual so that I know how to set the unit for speci… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am looking for a low voltage thermostat for a gas furnace
I am looking for a low voltage thermostat for a gas furnace that is non-programmable, heat only, requires only two low voltage wires, and has at least a two degree temperature differential, Any sugges… read more
Webb-Guy
Webb-Guy
Maitenance Supervisor
Associate Degree
2,768 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x